VT#, V#, and C# match the Torus convention.
Wesley
> On Dec 2, 2016, at 10:32 AM, Renuka Rajput-Ghoshal <renuka at jlab.org> wrote:
> 
> Hello Pablo,
> The description and calculations looks good to me, but the PLC tag for comparators (C1, C2 etc.) are confusing! Normally C is used for coil, but these are not the coils!
> Could you suggest some other name (may be COMP1 etc.).
> 
> Thanks
> Renuka
> 
> 
> ----- Original Message -----
> From: "Pablo Campero" <campero at jlab.org>
> To: "dsg-hallb magnets" <dsg-hallb_magnets at jlab.org>
> Sent: Thursday, December 1, 2016 5:00:46 PM
> Subject: [Dsg-hallb_magnets] Solenoid- PLC software comparators
> 
> Hello Wesley, 
> 
> Attached table with the PLC tag name for the Solenoid software comparators and voltages. 
> You can also find this spreadsheet in the M Drive, the path is M:\hallb_eng\CLAS12\Magnets\Solenoid\Controls and Wiring Solenoid PLC Software Comparators 
> 
> Renuka, 
> 
> Let me know if you have any correction in the attached table, I assigned the voltage (V1 to V15 ) and comparators (C1 to C10) based on your "Hall-B Solenoid Quench Detector Channel Assigment and Voltage Limits QD and Software" spread sheet. 
> 
> Thanks 
> Pablo Campero 
> Detector Support Group. 
> 
> 
> 
> _______________________________________________
> Dsg-hallb_magnets mailing list
> Dsg-hallb_magnets at jlab.org
> https://mailman.jlab.org/mailman/listinfo/dsg-hallb_magnets
> _______________________________________________
> Dsg-hallb_magnets mailing list
> Dsg-hallb_magnets at jlab.org
> https://mailman.jlab.org/mailman/listinfo/dsg-hallb_magnets
    
    
More information about the Dsg-hallb_magnets
mailing list