[Dsg-hallb_magnets] Readout of the status of the guard vacuum pump
George Biallas
biallas at jlab.org
Wed Apr 19 11:58:08 EDT 2017
Pablo,
Thank you very much for the follow-up.
With regard to Item 3, I thought that I was just not knowledgeable enough to read the literature - that you instrument folks would know right away. I was wrong.
So, indeed the MOOG Controller folk just don't compose good product descriptions. Yes, please contact them.
| From: "Pablo Campero" <campero at jlab.org>
| To: "Ruben Fair" <rfair at jlab.org>, "dsg-hallb magnets"
| <dsg-hallb_magnets at jlab.org>
| Cc: "George Biallas" <biallas at jlab.org>, "Joseph Matalevich" <josephm at jlab.org>
| Sent: Wednesday, April 19, 2017 11:42:15 AM
| Subject: Re: Readout of the status of the guard vacuum pump
| Hello Ruben,
| See my answers in blue:
| 1. I understand from Renuka that PT8677 is already being monitored by the PLC -
| is this correct?
| Yes, the readout signal for the PT8677 (Guard Vacuum) pressure is already
| monitored by the PLC and also appears in the Solenoid wiring drawing
| B00000-900-0626.
| 2. Which screen is PT8677 presently being displayed on? We will need it
| displayed on the Cryo screen.
| The PT8677 is currently displayed on the EPICS Helium-SST screen.
| 3. We will also need an 'indicator' located next to the PT8677 to provide 'pump
| motor status'
| I shall look through the information George has sent round to determine what
| form this status will take and will let you know.
| Is there a spare PLC channel to allow inclusion of this status?
| I already looked into the information sent by George Biallas and I cannot found
| any useful information to determinate the type of the output signals of the
| guard vacuum pump controller (MOOG- BDO-Q2-50-40). To my understanding
| typically these outputs signals: S1 (Hall Switch #1) and GND (GND for hall
| sensors #9) used to be aware of the status of the guard pump; gives pulse train
| signals (Discrete Signals), but there is nothing in the manual to confirm that.
| So maybe I can contact to the vendor of the controller and confirm this aspect,
| and then I can determinate if we have any spare available in the PLC input
| modules to be used to monitor this signal.
| Best Regard
| Pablo
| From: "Ruben Fair" <rfair at jlab.org>
| To: "George Biallas" <biallas at jlab.org>
| Cc: "Scot Spiegel" <spiegel at jlab.org>, "Renuka Rajput-Ghoshal"
| <renuka at jlab.org>, "Pablo Campero Rojas" <campero at jlab.org>, "Joseph
| Matalevich" <josephm at jlab.org>, "Wesley Moore" <wmoore at jlab.org>
| Sent: Wednesday, April 19, 2017 10:44:25 AM
| Subject: Re: Readout of the status of the guard vacuum pump
| Pablo,
| Can you give me the following information:
| 1. I understand from Renuka that PT8677 is already being monitored by the PLC -
| is this correct?
| 2. Which screen is PT8677 presently being displayed on? We will need it
| displayed on the Cryo screen.
| 3. We will also need an 'indicator' located next to the PT8677 to provide 'pump
| motor status'
| I shall look through the information George has sent round to determine what
| form this status will take and will let you know.
| Is there a spare PLC channel to allow inclusion of this status?
| Regards
| Ruben
| From: "Ruben Fair" <rfair at jlab.org>
| To: "George Biallas" <biallas at jlab.org>
| Cc: "Scot Spiegel" <spiegel at jlab.org>, "Renuka Rajput-Ghoshal"
| <renuka at jlab.org>, "Pablo Campero Rojas" <campero at jlab.org>, "Joseph
| Matalevich" <josephm at jlab.org>, lester at jlab.org, "Ernest Stallworth"
| <stallwor at jlab.org>, "wmoore" <wmoore at jlab.org>
| Sent: Tuesday, April 18, 2017 6:57:07 PM
| Subject: Re: Readout of the status of the guard vacuum pump
| Scot
| Could you please work with Mark to get the relevant cables made?
| Pablo
| Can you implement this in the PLC and work with Wesley to get the EPICS screen
| updated? Also remember to update the relevant spreadsheets and then work with
| Renuka to get the docs updated.
| Also speak to Joe Matalevich to see what alarms and/or controls he needs setting
| up.
| Regards
| Ruben
| > On Apr 18, 2017, at 4:56 PM, George Biallas <biallas at jlab.org> wrote:
| > Folks,
|> Joseph Matalevich asks for a new readout. He requests the status of the guard
|> vacuum pump as given by the MOOG motor controller signal contacts +#5 and -#1
|> on page 3 and on 9 of the Data Sheet I enclose on the Air Squared Pump and its
| > controller.
| > Is there a spare module on the PLC for this?
|> He is also not aware of where the Guard Vacuum pressure (vacuum) signal is
| > displayed in the control system.
|> He requests that both the pressure and the pump status be displayed on the Cryo
| > Page.
|> We need a new shielded pair to be added from PLC to the vacuum shelf area for
| > this signal.
| > Let's add it to the vacuum signal festoon.
| > --
| > George H. Biallas P.E.
| > Suite 402
| > Jefferson Lab
| > 12050 Jefferson Ave.
| > Newport News VA 23606
| > Work: 757 269 7535,
| > Page: 757 584 7535
| > Cell: 757 813 1179
| > Home: 757 877 1267
| > <Air Squared v12h020a-bldc-c Scroll Vacuum Pump Dat Sheet .pdf>
--
George
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <https://mailman.jlab.org/pipermail/dsg-hallb_magnets/attachments/20170419/62db6b8b/attachment-0001.html>
More information about the Dsg-hallb_magnets
mailing list