[Dsg-hallb_magnets] Can you give me an update on your check outs?

Ruben Fair rfair at jlab.org
Tue Aug 8 07:34:45 EDT 2017


Thank you Pablo. 

We can review all the check sheets - as completed thus far, later today. I shall set up a meeting. 

Ruben 


From: "Pablo Campero Rojas" <campero at jlab.org> 
To: "dsg-hallb magnets" <dsg-hallb_magnets at jlab.org> 
Sent: Monday, August 7, 2017 5:14:09 PM 
Subject: Re: [Dsg-hallb_magnets] Can you give me an update on your check outs? 

Hello Ruben, 

Here some updates on the Solenoid I&C. 

For the P010- Pre-Cooldown Valve Checkout Procedure: 
SV8675BY - was completed tested . 120 V AC and air supply line were connected this morning. No issues in controls and EPICS monitoring for the valve. 


Additionally, test for heaters on Lead A and Lead B. 
Tested heaters in a temperature range of 292 to 310 K. They reacted as expected. hardware wiring, PLC logic and EPICS indicators works properly. 
Values in the PLC code will be changed to keep a temperature range between 301 and 303 K. Same as Torus thresholds.That means at temp <301 K heaters will be turned on, and at temp >303 K heaters will be disable. 


Best Regards, 
Pablo 


From: "Probir Ghoshal" <ghoshal at jlab.org> 
To: "Ruben Fair" <rfair at jlab.org> 
Cc: "Nicholas Sandoval" <sandoval at jlab.org>, "Pablo Campero Rojas" <campero at jlab.org>, "Brian Eng" <beng at jlab.org>, "Wesley Moore" <wmoore at jlab.org> 
Sent: Monday, August 7, 2017 10:50:58 AM 
Subject: Re: Can you give me an update on your check outs? 

Please find the data/information that is needed for the check list all saved as required in the Check list. 
all saved at the following location - 
M:\hallb_eng\CLAS12\Magnets\Solenoid\Solenoid test in HALL B 
Regards 

Probir 

----- Original Message ----- 
From: "Ruben Fair" <rfair at jlab.org> 
To: "Nicholas Sandoval" <sandoval at jlab.org> 
Cc: "Pablo Campero Rojas" <campero at jlab.org>, "Brian Eng" <beng at jlab.org>, "Probir Ghoshal" <ghoshal at jlab.org>, wmoore at jlab.org 
Sent: Monday, August 7, 2017 9:23:42 AM 
Subject: Re: Can you give me an update on your check outs? 

Many thanks Nick. 

I think for now, copy the relevant sheets from the previous P006 and attach to your current sheets. 

I hope to have the load cells connected later this morning 

Cheers 

Ruben 

> On Aug 7, 2017, at 9:20 AM, Nicholas Sandoval <sandoval at jlab.org> wrote: 
> 
> Hi Ruben, 
> 
> 
> My summary so far: 
> -P010 (Valve checkout) I skipped DBX/TST valves as they are in use. All solenoid valves checked out OK less VCL flow controllers(need helium) and SV8675BY (need 120VAC). No show stoppers here 
> 
> -P013 (instrument checkout) Looks good through Page 8, with exception of pressure transducers and Liquid level transmitters. Pablo has the last few pages of this checkout as we split it. 
> 
> -P006 looks like it is for all magnet cryogenic systems not just Solenoid. Since we are using the TST, DBX, Dewar, etc should we print out the previous checkout for those systems and affix it to this one? Or do we need to stop the torus cooling and perform a real checkout again? 
> 
> Best Regards, 
> 
> Nick 
> 
> 
> 
> ----- Original Message ----- 
> From: "Ruben Fair" <rfair at jlab.org> 
> To: "Pablo Campero Rojas" <campero at jlab.org>, "Brian Eng" <beng at jlab.org>, "Nicholas Sandoval" <sandoval at jlab.org>, "Probir Ghoshal" <ghoshal at jlab.org>, wmoore at jlab.org 
> Sent: Monday, August 7, 2017 8:03:40 AM 
> Subject: Can you give me an update on your check outs? 

_______________________________________________ 
Dsg-hallb_magnets mailing list 
Dsg-hallb_magnets at jlab.org 
https://mailman.jlab.org/mailman/listinfo/dsg-hallb_magnets 
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <https://mailman.jlab.org/pipermail/dsg-hallb_magnets/attachments/20170808/4a06a752/attachment.html>


More information about the Dsg-hallb_magnets mailing list