[Dsg-hallb_magnets] Solenoid - Sequence of pre-power up I and C	checks
    Ruben Fair 
    rfair at jlab.org
       
    Tue Aug 22 20:23:55 EDT 2017
    
    
  
Thank you very much Pablo and team
Regards
Ruben
> On Aug 22, 2017, at 7:54 PM, Pablo Campero <campero at jlab.org> wrote:
> 
> Hi Ruben,
> 
> Here is an updated of the Pre-Power up interlock checks completed today:
> 
> Fast Dump interlocks 
> 
> 1. Test Hard-wire Interlock Voltage Tap cable.
> 2. Splices over temperature
> 3.Vapor Cooled lead over temperature
> 
> Controlled Ramp Down
> 
> 4. PLC Fast Dump Button (MPS EPICS screen)
> 5. PLC hard coded current limit.
> 6. UPS_ Battery low signal.
> 7..Vapor Cooled lead over temperature.
> 8.Water Cooled lead over temperature.
> 
> Checks will continue tomorrow.
> 
> Regards,
> Pablo 
> 
> 
> From: "Ruben Fair" <rfair at jlab.org>
> To: "Pablo Campero" <campero at jlab.org>
> Cc: "dsg-hallb magnets" <dsg-hallb_magnets at jlab.org>
> Sent: Monday, August 21, 2017 6:15:29 PM
> Subject: Re: [Dsg-hallb_magnets] Solenoid - Sequence of pre-power up I and C checks
> 
> Thank you very much for the update Pablo.
> 
> Have a good evening
> 
> Regards
> 
> Ruben
> 
> On Aug 21, 2017, at 5:59 PM, Pablo Campero <campero at jlab.org> wrote:
> 
> Hello Ruben,
> 
> This afternoon was completed three interlock checks:
> 
> 1. Watchdog fail (Hardware)
> 2. Supply Current lead water flow  
> 3. Return Current lead water flow 
> 
> So far all of them are worked without any problem.
> 
> 
> To proceed with the full test and clear all the fault/interlocks trips was required:
> 
> 1. Add a jumper for the Quench Detection #1 (channel 1 and 2 tripped at this time). Wire jumper connected at the SOE relay terminal block. 
> 2. Disable relay outputs for  in cryocon 1 and cryocon 2. (Actual configured thresholds  are: 8.5 and 10 K )
> 3. Turn on current lead water flows (Return and supply). 
> 4. Turn on liquid levels hardware controllers for Lead and Magnet reservoir.
> 5. Verify wiring connection for the PSU (connected only Control power 110 V external power supply).
> 
> 
> After completed with the mentioned checkouts the PSU was turned off (pushed E-bottom), liquid levels hardware controllers was turned off, and also the supply water valve for the current leads was closed.
> It will be need to turn on and enable all of them tomorrow to clear out all faults and continue with the test.
> 
> 
> Pablo
>  
> 
> 
> 
> From: "Ruben Fair" <rfair at jlab.org>
> To: "Pablo Campero Rojas" <campero at jlab.org>
> Cc: "dsg-hallb magnets" <dsg-hallb_magnets at jlab.org>, "Mark Todd" <mtodd at jlab.org>, "Sarin Philip" <philip at jlab.org>, "Onish Kumar" <okumar at jlab.org>
> Sent: Monday, August 21, 2017 2:40:03 PM
> Subject: Re: [Dsg-hallb_magnets] Solenoid - Sequence of pre-power up I and C checks
> 
> Thank you.
> 
> As discussed previously, you will have to 'jumper out' the interlocks which we cannot use right now - liquid levels for example.
> 
> Regards
> 
> Ruben
> 
> 
> From: "Pablo Campero Rojas" <campero at jlab.org>
> To: "dsg-hallb magnets" <dsg-hallb_magnets at jlab.org>
> Cc: "Mark Todd" <mtodd at jlab.org>, "Sarin Philip" <philip at jlab.org>, "Onish Kumar" <okumar at jlab.org>
> Sent: Monday, August 21, 2017 2:28:45 PM
> Subject: Re: [Dsg-hallb_magnets] Solenoid - Sequence of pre-power up I and C checks
> 
> Ruben,
> 
> We will start the checks this afternoon.
> With regards to Onish's email, first action is check and make sure that all interlocks faults are clear, that includes the hardware interlocks (liquid levels, cryocon units, lead water flow), this hardware interlocks also affects the Quench Det. status on the PS control module (status in remote control board) and the MPS Dump switch engages.
> I verified PLC side and it seems to be fine, there is no 'PLC Fast Dump interlocks' at this time.  PLC relay outputs associate with the 'Fast dump interlocks' are clear.
> 
> Best Regards,
> Pablo 
>  
> 
> From: "Ruben Fair" <rfair at jlab.org>
> To: "Onish Kumar" <okumar at jlab.org>
> Cc: "Brian Eng" <beng at jlab.org>, "Pablo Campero Rojas" <campero at jlab.org>, "Probir Ghoshal" <ghoshal at jlab.org>, "Sarin Philip" <philip at jlab.org>, "Mark Todd" <mtodd at jlab.org>
> Sent: Monday, August 21, 2017 11:44:43 AM
> Subject: Re: [Dsg-hallb_magnets] Solenoid - Sequence of pre-power up I and C checks
> 
> Thank you Onish and Mark.
> 
> Pablo, Brian,
> 
> Can you check all this out this afternoon - see Onish's note below.
> 
> Regards
> 
> Ruben
> 
> 
> From: "Onish Kumar" <okumar at jlab.org>
> To: "Ruben Fair" <rfair at jlab.org>
> Cc: "Brian Eng" <beng at jlab.org>, "Pablo Campero Rojas" <campero at jlab.org>, "Probir Ghoshal" <ghoshal at jlab.org>, "Sarin Philip" <philip at jlab.org>, "Mark Todd" <mtodd at jlab.org>
> Sent: Monday, August 21, 2017 11:41:07 AM
> Subject: Re: [Dsg-hallb_magnets] Solenoid - Sequence of pre-power up I and C checks
> 
> Hi Ruben,
> 
> We have finished our checklist today (see attachment). While working on our checklist we found that QD PLC inputs are not making contact. I think Pablo and Brian should check on their side if QD PLC relay's are good (Below is the list of interlock to check, PLC side). To make sure something is not wrong on our side we check the wiring and did continuity tests, and the test passed, hence I suspect issue on the PLC side. We did all of our test by taking connector X15 off and putting jumpers between pins A & H, and between pins J & K.
> 
> List of interlock to check:
> 1. Quench Det. Fast Ramp Down
> 2. Fast Dischange
> 3. Energy Dump Status
> 4. Control PLC status.
> 
> Please note all the interlocks mentioned above are in series, so if any one of them is not making contact then they will show-up as Quench Det. (on the PS control module) and the Dump switch engages. Let us know if you have any questions or concerns.
> 
> Thanks,
> Onish
> 
> --
> Onish Kumar
> DC Power Systems Engineer
> Jefferson Lab, EES-DCP
> Email: okumar at jlab.org
> Phone: (757) 269-7852
> 
> From: "Ruben Fair" <rfair at jlab.org>
> To: "Brian Eng" <beng at jlab.org>
> Cc: "Pablo Campero" <campero at jlab.org>, "Onish Kumar" <okumar at jlab.org>, "Probir Ghoshal" <ghoshal at jlab.org>, "Sarin Philip" <philip at jlab.org>
> Sent: Thursday, August 17, 2017 12:06:40 PM
> Subject: Re: [Dsg-hallb_magnets] Solenoid - Sequence of pre-power up I and C checks
> 
> Ok
> 
> Onish - we have to wait till you complete your work
> 
> Ruben
> 
> > On Aug 17, 2017, at 11:15 AM, Brian Eng <beng at jlab.org> wrote:
> > 
> > Ruben,
> > 
> > Pablo and I just went through the interlock checkout and I don't think there's any we can start early with.
> > 
> > We either need the MPS to be operational (in order to have some current or to close the fast dump contactor) or to have all the interlocks cleared as the first step.
> > 
> > Unless we change the procedure to not require all the interlocks to be cleared at the very least we'll have to wait for DC power to finish their MPS work before starting.
> > 
> >> On Aug 17, 2017, at 9:34 AM, Pablo Campero <campero at jlab.org> wrote:
> >> 
> >> Hello Ruben,
> >> 
> >> Brian and I will start with the  Pre-Power Up checks today.
> >> To complete with the full test for most of the 'Fast Dump- Hardware Interlock' checkouts is required to turn on the PSU to verified correct function of the dump switch and remote resets on the PSU.
> >> Will someone will be available to turn on the PSU after the replacement of the connector in the remote crate and re-tune of the QD units? 
> >> 
> >> Best Regards,
> >> Pablo  
> >> 
> >> From: "Ruben Fair" <rfair at jlab.org>
> >> To: "Onish Kumar" <okumar at jlab.org>, "Probir Ghoshal" <ghoshal at jlab.org>, "Pablo Campero Rojas" <campero at jlab.org>, "Brian Eng" <beng at jlab.org>, "Nicholas Sandoval" <sandoval at jlab.org>
> >> Cc: "George Biallas" <biallas at jlab.org>, "Scot Spiegel" <spiegel at jlab.org>
> >> Sent: Thursday, August 17, 2017 7:40:46 AM
> >> Subject: Solenoid - Sequence of pre-power up I and C checks
> >> 
> >> Gentlemen,
> >> 
> >> Some of the I and C checks for pre-power up will have to be carried out in sequence (e.g. anything to do with the QD units):
> >> 
> >> 1. Replace connector on PSU remote control crate + complete both PSU check sheets - Onish (to be completed by Friday 18th Aug)
> >> 2. Re-tune QD units - Probir (by Thursday 24th Aug) - as Probir is out Mon-Wed next week)
> >> 3. Checks (including interlock checks) on QD units (by Friday 25th Aug) - Pablo/Brian/Nick - though of course you can make a start on the other checks
> >> 
> >> As our cooling rate has increased (we are presently cooling at about 10 K/day), we won't have as much time as we initially thought so we should start as soon as possible.
> >> 
> >> Regards
> >> 
> >> Ruben
> 
> 
> _______________________________________________
> Dsg-hallb_magnets mailing list
> Dsg-hallb_magnets at jlab.org
> https://mailman.jlab.org/mailman/listinfo/dsg-hallb_magnets
> 
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <https://mailman.jlab.org/pipermail/dsg-hallb_magnets/attachments/20170822/5d9cb8df/attachment-0001.html>
    
    
More information about the Dsg-hallb_magnets
mailing list