[Dsg-hallb_magnets] Solenoid Controls_Final_Wiring check-out
    Wesley Moore 
    wmoore at jlab.org
       
    Fri Jun 16 17:21:29 EDT 2017
    
    
  
Pablo,
They aren’t working because the tag names don’t match.  Why were they changed from:
CryoCon_Reset_PB
CryoCon_WatchDog
Since they are coming from the Solenoid PLC, they shouldn’t need “Sol_”, right?
Wesley
> On Jun 16, 2017, at 5:02 PM, Ruben Fair <rfair at jlab.org> wrote:
> 
> Thank you all
> 
> Wesley
> 
> Let us know when these issues are resolved.
> 
> Regards
> 
> Ruben
> 
> On Jun 16, 2017, at 4:54 PM, Pablo Campero <campero at jlab.org <mailto:campero at jlab.org>> wrote:
> 
>> Hello Ruben,
>> 
>> Tyler, Amanda and I tested the following instrumentation:
>>  
>> 1. PT-100  temperature sensor TP8675 (Vaporizer)
>> 2. PT-100 temperature sensor TP8680 (Relief Valve)
>> 3. Cryocon Units 2 and 3.    
>> 4. Solenoid valve SV8622 (Vent valve)   
>> 
>> Controls for the temperature sensors and solenoid valve are working as expected, and also readouts of these instrumentation was checked.
>> Detailed information of the results for this test can be find in the TEST PLC- EPICS PLAN_v7_June 16th 2017 spreadsheet. Find it on M:\hallb_eng\CLAS12\Magnets\Solenoid\Controls and Wiring.
>> 
>> 
>> Wesley,
>> During the test, the 'Solenoid Cryocon Status' EPICS screen was checked too, and we noticed the following:
>> 1. 'Solenoid Watchdog'  indicator is not updating  for Solenoid and DBX. (pink color in the Solenoid-Watchdog readout box)
>> 2. 'Reset Button' is not connecting with the associate tag in the Solenoid PLC code.
>> 
>> Here is the tag names used in the Solenoid PLC code that are related with these signals mentioned above.
>> 
>> PLC TAG	Data Type 
>> Sol_CryoCon_Reset_PB	BOOL
>> Sol_CryoCon_Watchdog	INT
>> 
>> If you have a chance, please check and let me know any comments.
>> 
>> 
>> Best Regards,
>> Pablo 
>> 
>> From: "Ruben Fair" <rfair at jlab.org <mailto:rfair at jlab.org>>
>> To: "Pablo Campero Rojas" <campero at jlab.org <mailto:campero at jlab.org>>
>> Cc: "dsg-hallb magnets" <dsg-hallb_magnets at jlab.org <mailto:dsg-hallb_magnets at jlab.org>>
>> Sent: Tuesday, June 13, 2017 8:58:13 AM
>> Subject: Re: Solenoid Controls_Final_Wiring check-out
>> 
>> Thank you very much Pablo - appreciate it.
>> 
>> Let me know if you need help.
>> 
>> Cheers
>> 
>> Ruben
>> 
>> 
>> From: "Pablo Campero Rojas" <campero at jlab.org <mailto:campero at jlab.org>>
>> To: "Ruben Fair" <rfair at jlab.org <mailto:rfair at jlab.org>>
>> Cc: "dsg-hallb magnets" <dsg-hallb_magnets at jlab.org <mailto:dsg-hallb_magnets at jlab.org>>
>> Sent: Tuesday, June 13, 2017 8:56:19 AM
>> Subject: Re: Solenoid Controls_Final_Wiring check-out
>> 
>> Hello Ruben,
>> 
>> The Instrumentation  TEST PLC- EPICS PLAN_v6_June 13th 2017 spreadsheet was update with the new instrumentation that needs to be tested. You can find it on the link : M:\hallb_eng\CLAS12\Magnets\Solenoid\Controls and Wiring.
>> 
>> The test for the instrumentation, that was required by Scot for the PTS (Temperature Sensors), Cryocon units and solenoid vales will be complete by the end of this week, I will let you know once I complete the tasks.
>> 
>> Best Regards,
>> Pablo 
>> From: "Ruben Fair" <rfair at jlab.org <mailto:rfair at jlab.org>>
>> To: "Pablo Campero Rojas" <campero at jlab.org <mailto:campero at jlab.org>>
>> Sent: Tuesday, June 13, 2017 7:51:22 AM
>> Subject: Fwd: Solenoid Controls_Final_Wiring check-out
>> 
>> Pablo,
>> 
>> Please confirm that these additional tests have been added to your I and C test spreadsheet.
>> 
>> When are you planning to complete the tests?
>> 
>> If you need help from Nick, Scot or myself let us know.
>> 
>> Regards
>> 
>> Ruben
>> 
>> From: "Ruben Fair" <rfair at jlab.org <mailto:rfair at jlab.org>>
>> To: "Scot Spiegel" <spiegel at jlab.org <mailto:spiegel at jlab.org>>
>> Cc: "Probir Ghoshal" <ghoshal at jlab.org <mailto:ghoshal at jlab.org>>, "Renuka Rajput-Ghoshal" <renuka at jlab.org <mailto:renuka at jlab.org>>, "Pablo Campero Rojas" <campero at jlab.org <mailto:campero at jlab.org>>, "Nicholas Sandoval" <sandoval at jlab.org <mailto:sandoval at jlab.org>>
>> Sent: Friday, June 9, 2017 4:12:09 PM
>> Subject: Re: Solenoid Controls_Final_Wiring check-out
>> 
>> Thank you Scot.
>> 
>> Pablo,
>> 
>> Can you add these tests to your overall I and C test spreadsheet and then plan to get them completed within the next 2 weeks?
>> 
>> Regards
>> 
>> Ruben
>> 
>> 
>> From: "Scot Spiegel" <spiegel at jlab.org <mailto:spiegel at jlab.org>>
>> To: "Ruben Fair" <rfair at jlab.org <mailto:rfair at jlab.org>>
>> Cc: "Probir Ghoshal" <ghoshal at jlab.org <mailto:ghoshal at jlab.org>>, "Renuka Rajput-Ghoshal" <renuka at jlab.org <mailto:renuka at jlab.org>>, "Pablo Campero Rojas" <campero at jlab.org <mailto:campero at jlab.org>>, "Nicholas Sandoval" <sandoval at jlab.org <mailto:sandoval at jlab.org>>
>> Sent: Friday, June 9, 2017 3:13:30 PM
>> Subject: Solenoid Controls_Final_Wiring check-out
>> 
>> All,
>> 
>> Mark Lester and I have completed the last few cable terminations in the Solenoid Racks.
>> 
>> The remaining devices will need to verified before the Solenoid arrives.
>> 
>> Test requirement for -  Valve solenoids (vaporizer) 24VDC (X) 3, PT's (X) 2 & CRYOCON #2, Channel D for Vaporizer temperature.
>> 
>> Best regards,
>> 
>> Scot Spiegel
>> Sr. Technologist / Designer
>> Physics / Hall D
>> JSA Jefferson Lab
>> 12000 Jefferson Ave.
>> Bldg. 55 Rm. 1546-24
>> Newport News, VA. 23606
>> Ph. 757-536-5900
>> Wk. 757-269-5900
>> 
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <https://mailman.jlab.org/pipermail/dsg-hallb_magnets/attachments/20170616/663c177c/attachment.html>
    
    
More information about the Dsg-hallb_magnets
mailing list