[Dsg-hallb_magnets] Solenoid Controls_Final_Wiring check-out
Ruben Fair
rfair at jlab.org
Fri Jun 16 17:02:04 EDT 2017
Thank you all
Wesley
Let us know when these issues are resolved.
Regards
Ruben
> On Jun 16, 2017, at 4:54 PM, Pablo Campero <campero at jlab.org> wrote:
>
> Hello Ruben,
>
> Tyler, Amanda and I tested the following instrumentation:
>
> 1. PT-100 temperature sensor TP8675 (Vaporizer)
> 2. PT-100 temperature sensor TP8680 (Relief Valve)
> 3. Cryocon Units 2 and 3.
> 4. Solenoid valve SV8622 (Vent valve)
>
> Controls for the temperature sensors and solenoid valve are working as expected, and also readouts of these instrumentation was checked.
> Detailed information of the results for this test can be find in the TEST PLC- EPICS PLAN_v7_June 16th 2017 spreadsheet. Find it on M:\hallb_eng\CLAS12\Magnets\Solenoid\Controls and Wiring.
>
>
> Wesley,
> During the test, the 'Solenoid Cryocon Status' EPICS screen was checked too, and we noticed the following:
> 1. 'Solenoid Watchdog' indicator is not updating for Solenoid and DBX. (pink color in the Solenoid-Watchdog readout box)
> 2. 'Reset Button' is not connecting with the associate tag in the Solenoid PLC code.
>
> Here is the tag names used in the Solenoid PLC code that are related with these signals mentioned above.
>
> PLC TAG Data Type
> Sol_CryoCon_Reset_PB BOOL
> Sol_CryoCon_Watchdog INT
>
> If you have a chance, please check and let me know any comments.
>
>
> Best Regards,
> Pablo
>
> From: "Ruben Fair" <rfair at jlab.org>
> To: "Pablo Campero Rojas" <campero at jlab.org>
> Cc: "dsg-hallb magnets" <dsg-hallb_magnets at jlab.org>
> Sent: Tuesday, June 13, 2017 8:58:13 AM
> Subject: Re: Solenoid Controls_Final_Wiring check-out
>
> Thank you very much Pablo - appreciate it.
>
> Let me know if you need help.
>
> Cheers
>
> Ruben
>
>
> From: "Pablo Campero Rojas" <campero at jlab.org>
> To: "Ruben Fair" <rfair at jlab.org>
> Cc: "dsg-hallb magnets" <dsg-hallb_magnets at jlab.org>
> Sent: Tuesday, June 13, 2017 8:56:19 AM
> Subject: Re: Solenoid Controls_Final_Wiring check-out
>
> Hello Ruben,
>
> The Instrumentation TEST PLC- EPICS PLAN_v6_June 13th 2017 spreadsheet was update with the new instrumentation that needs to be tested. You can find it on the link : M:\hallb_eng\CLAS12\Magnets\Solenoid\Controls and Wiring.
>
> The test for the instrumentation, that was required by Scot for the PTS (Temperature Sensors), Cryocon units and solenoid vales will be complete by the end of this week, I will let you know once I complete the tasks.
>
> Best Regards,
> Pablo
> From: "Ruben Fair" <rfair at jlab.org>
> To: "Pablo Campero Rojas" <campero at jlab.org>
> Sent: Tuesday, June 13, 2017 7:51:22 AM
> Subject: Fwd: Solenoid Controls_Final_Wiring check-out
>
> Pablo,
>
> Please confirm that these additional tests have been added to your I and C test spreadsheet.
>
> When are you planning to complete the tests?
>
> If you need help from Nick, Scot or myself let us know.
>
> Regards
>
> Ruben
>
> From: "Ruben Fair" <rfair at jlab.org>
> To: "Scot Spiegel" <spiegel at jlab.org>
> Cc: "Probir Ghoshal" <ghoshal at jlab.org>, "Renuka Rajput-Ghoshal" <renuka at jlab.org>, "Pablo Campero Rojas" <campero at jlab.org>, "Nicholas Sandoval" <sandoval at jlab.org>
> Sent: Friday, June 9, 2017 4:12:09 PM
> Subject: Re: Solenoid Controls_Final_Wiring check-out
>
> Thank you Scot.
>
> Pablo,
>
> Can you add these tests to your overall I and C test spreadsheet and then plan to get them completed within the next 2 weeks?
>
> Regards
>
> Ruben
>
>
> From: "Scot Spiegel" <spiegel at jlab.org>
> To: "Ruben Fair" <rfair at jlab.org>
> Cc: "Probir Ghoshal" <ghoshal at jlab.org>, "Renuka Rajput-Ghoshal" <renuka at jlab.org>, "Pablo Campero Rojas" <campero at jlab.org>, "Nicholas Sandoval" <sandoval at jlab.org>
> Sent: Friday, June 9, 2017 3:13:30 PM
> Subject: Solenoid Controls_Final_Wiring check-out
>
> All,
>
> Mark Lester and I have completed the last few cable terminations in the Solenoid Racks.
>
> The remaining devices will need to verified before the Solenoid arrives.
>
> Test requirement for - Valve solenoids (vaporizer) 24VDC (X) 3, PT's (X) 2 & CRYOCON #2, Channel D for Vaporizer temperature.
>
> Best regards,
>
> Scot Spiegel
> Sr. Technologist / Designer
> Physics / Hall D
> JSA Jefferson Lab
> 12000 Jefferson Ave.
> Bldg. 55 Rm. 1546-24
> Newport News, VA. 23606
> Ph. 757-536-5900
> Wk. 757-269-5900
>