[Dsg-hallb_magnets] [Dsg-internal] Solenoid work log
    Amrit Yegneswaran 
    yeg at jlab.org
       
    Thu Sep 14 22:17:22 EDT 2017
    
    
  
pablo, 
thanks for the excellent work log. 
so i guess we reached 1000A. 
any way more tomorrow. 
goodnight and godbless 
From: "Pablo Campero" <campero at jlab.org> 
To: "Amrit Yegneswaran" <yeg at jlab.org> 
Cc: "dsg-hallb magnets" <dsg-hallb_magnets at jlab.org> 
Sent: Thursday, September 14, 2017 10:02:32 PM 
Subject: Re: [Dsg-hallb_magnets] [Dsg-internal] Solenoid work log 
Hello Amrit, 
The following is log work for 9/14/17: 
7:00 AM - Reset (Power cycle) Solenoid PLC and FastDAQ cRIO to recover all solenoid control systems. 
8:00 AM - Investigated all controls systems and instrumentation affected by the power outage on Solenoid/DBX UPS. 
8:30 AM - Noticed that Torus PLC Point I/O system and Torus FastDAQ cRIO were affected. PLC point I/O system returned to normal operations, not the same case for the Torus FastDAQ cRIO. 
9:00 AM - Stared to debugged Sol - FastDAQ cRIO and noticed that it did not recover after power cycle and put the system on Safe mode. 
10:00 AM - Began debugging to recover communications with Solenoid FastDAQ via direct Ethernet and RS232 connections. 
11:00 AM - Swapped Solenoid FastDAQ cRIO by spare available (the one that was recover after the 2nd outage power issue back on 06/28/17) 
11:50 AM - Deployed FastDAQ LabVIEW program on the cRIO. 
14:00 PM - Attended Solenoid Plan Forward and Responsibilities (Find attached minutes meeting) 
14:30 PM - Re-deployed FastDAQ LabVIEW program on the cRIO, Run cRIO full functions to readout all voltage taps on the magnet. 
15:30: PM - Stared Power up solenoid to 1000 A. After the solenoid cooldown recover, we monitored and wait VCL temperatures go from 12 to 10 K. 
16:30 PM - Monitored main cryo signals, VTs , MPS current voltage and 
17:30 PM - Noticed unstable supply cooldown helium to cooldown the solenoid, controlled ramp down initiated due to LL he and raise on temperatures in VCL.(problems not present when Torus was on line). 
18:10 pm - Stopped ramp up of the magnet. 
Plan to continue the power -up to 1250 A tomorrow at 8:00 AM. 
Best Regards, 
Pablo 
From: "Amrit Yegneswaran" <yeg at jlab.org> 
To: "dsg-hallb magnets" <dsg-hallb_magnets at jlab.org> 
Sent: Thursday, September 14, 2017 4:58:39 PM 
Subject: Re: [Dsg-hallb_magnets] [Dsg-internal] Solenoid work log 
thanks for the update pablo. 
you owe me work log from yesterday and the meeting minutes. 
From: "Pablo Campero" <campero at jlab.org> 
To: "dsg-internal" <dsg-internal at jlab.org> 
Sent: Thursday, September 14, 2017 3:29:44 PM 
Subject: [Dsg-internal] Solenoid work log 
Hello Amrit, Meeting to plan the activities and roles finished at 2:40 pm. Brian and I were debugging the solenoid fastDaq cRIO. We re-deployed the labview program with the FPGA filter version. We are monitoring temperatures in the coils (~5 K), Cooldown has been recovered, but we are still waiting to get low temperatures in te vcl, they are about 12K. It has been planed to start power up the solenoid in a few minutes.( about15:30) Regards, Pablo 
_______________________________________________ 
Dsg-internal mailing list 
Dsg-internal at jlab.org 
https://mailman.jlab.org/mailman/listinfo/dsg-internal 
_______________________________________________ 
Dsg-hallb_magnets mailing list 
Dsg-hallb_magnets at jlab.org 
https://mailman.jlab.org/mailman/listinfo/dsg-hallb_magnets 
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <https://mailman.jlab.org/pipermail/dsg-hallb_magnets/attachments/20170914/b6c49d56/attachment.html>
    
    
More information about the Dsg-hallb_magnets
mailing list