Hi All,
If we won’t be getting this info directly from the PLC, I went ahead and added PVs named *WANTGAS.   It has a value of 1 if the last button pressed was START, a value of 0 if the last button pressed was STOP, and a value of 0 if there is READ error with the PLC (e.g. it’s offline).  ** I don’t know if that’s the logic all you guys want.
For this to work, the gas flow must be started and stopped only through EPICS (via the START/STOP buttons).
I tested (without the READ error override), and both BMT and FMT gas iocs are running with this PV.  But it will need to be checked again when PLCs are back online.  Currently it will be 0 for BMT/FMT due to READ error.  I did not mess with FTT ioc since PLC is up, but if it’s restarted it will pickup up this new PV.
-nathan
> On Nov 13, 2017, at 17:21, Nathan Baltzell <baltzell at jlab.org> wrote:
> 
> Sounds like it will be best if Quentin can provide another bit to read whether it’s trying to flow gas or not.  The START/STOP buttons don’t have feedback from the PLC.
> 
> -Nathan
> 
> 
>> On Nov 13, 2017, at 12:42, Brian Eng <beng at jlab.org> wrote:
>> 
>> It's close to what I was looking for, but not quite it.
>> 
>> It sounds like that could go bad if the flows don't match (i.e. there is a leak in the detector), but that's not the same thing as them wanting flow or not.
>> 
>> I was hoping there was something that was on/off indicating we should be sending mixed gas or not.
>> 
>> ----- Original Message -----
>>> From: "Nathan Baltzell" <baltzell at jlab.org>
>>> To: "BERTRAND Quentin" <Quentin.BERTRAND at cea.fr>
>>> Cc: "Brian Eng" <beng at jlab.org>, "mdefurne" <mdefurne at jlab.org>, "Guillaume Christiaens" <guillaum at jlab.org>,
>>> dsg-mvt at jlab.org
>>> Sent: Monday, November 13, 2017 12:42:34 PM
>>> Subject: Re: [Dsg-mvt] MVT with premix in hall B
>> 
>>> Thanks Quentin,
>>> 
>>> I think that might be what Brian wants.  Combined with testing the .STAT field
>>> for READ error (value = 3).
>>> 
>>> -Nathan
>>> 
>>> 
>>>> On Nov 13, 2017, at 12:36, BERTRAND Quentin <Quentin.BERTRAND at cea.fr> wrote:
>>>> 
>>>> Hi Nathan,
>>>> 
>>>> FLOW_STAT means that IN_FLOW and OUT_FLOW corresponds to the SETPOINT when it is
>>>> 1.
>>>> 
>>>> Quentin
>>>> ________________________________________
>>>> De : Nathan Baltzell [baltzell at jlab.org]
>>>> Envoyé : lundi 13 novembre 2017 18:02
>>>> À : Brian Eng
>>>> Cc : mdefurne; Guillaume Christiaens; BERTRAND Quentin; dsg-mvt at jlab.org
>>>> Objet : Re: [Dsg-mvt] MVT with premix in hall B
>>>> 
>>>> Quentin,
>>>> 
>>>> What exactly does FLOW_STAT mean?   Looks like it’s at word 32, 11th bit.
>>>> 
>>>> -Nathan
>>>> 
>>>> {P,              R,             PORT,   OFFSET, MASK,       ZNAM,   ONAM,   ZSV,
>>>> OSV,        SCAN}
>>>> {B_DET_BMT_GAS_, FLOWDIFF_FLT,  R505,   32,     1,          Ok,     Fault,
>>>> NO_ALARM,   MAJOR,      "I/O Intr"}
>>>> {B_DET_BMT_GAS_, INFLOW_FLT,    R505,   32,     2,          Ok,     Fault,
>>>> NO_ALARM,   MAJOR,      "I/O Intr"}
>>>> {B_DET_BMT_GAS_, OVRFLOW_FLT,   R505,   32,     4,          Ok,     Fault,
>>>> NO_ALARM,   MAJOR,      "I/O Intr"}
>>>> # FLOW_START    8
>>>> # FLOW_STOP     16
>>>> # <empty>       32
>>>> # <empty>       64
>>>> # <empty>       128
>>>> {B_DET_BMT_GAS_, GEN_WRN,       R505,   32,     256,        Ok,     Fault,
>>>> NO_ALARM,   MAJOR,      "I/O Intr"}
>>>> {B_DET_BMT_GAS_, GEN_FLT,       R505,   32,     512,        Ok,     Fault,
>>>> NO_ALARM,   MAJOR,      "I/O Intr"}
>>>> {B_DET_BMT_GAS_, FLOW_STAT,     R505,   32,     1024,       Fault,  Ok,
>>>> MAJOR,      NO_ALARM,   "I/O Intr"}
>>>> {B_DET_BMT_GAS_, PRES_WRN,      R505,   32,     2048,       Ok,     Fault,
>>>> NO_ALARM,   MAJOR,      "I/O Intr"}
>>>> {B_DET_BMT_GAS_, INFLOW_WRN,    R505,   32,     4096,       Ok,     Fault,
>>>> NO_ALARM,   MAJOR,      "I/O Intr"}
>>>> {B_DET_BMT_GAS_, OVRFLOW_WRN,   R505,   32,     8192,       Ok,     Fault,
>>>> NO_ALARM,   MAJOR,      "I/O Intr"}
>>>> {B_DET_BMT_GAS_, FLOWDIFF_WRN,  R505,   32,     16384,      Ok,     Fault,
>>>> NO_ALARM,   MAJOR,      "I/O Intr"}
>>>> {B_DET_BMT_GAS_, PRES_FLT,      R505,   32,     32768,      Ok,     Fault,
>>>> NO_ALARM,   MAJOR,      "I/O Intr”}
>>>> 
>>>> 
>>>> 
>>>>> On Nov 13, 2017, at 08:58, Brian Eng <beng at jlab.org> wrote:
>>>>> 
>>>>> Yes, a normally off/false boolean(s) that indicates if any of the MVT detectors
>>>>> need gas would be what I'm looking for.
>>>>> 
>>>>> The *_INFLOW_SET PVs will work just fine for calculating the mixing flow.
>>>>> 
>>>>> Basically I'm trying to see if there is something that will handle the failure
>>>>> case right now, the PLC is offline, but the PVs still have numbers in them. So
>>>>> right now if we had gas it would be trying to flow it despite the gas not
>>>>> actually being required.
>>>>> 
>>>>>> On Nov 10, 2017, at 7:36 PM, Nathan Baltzell <baltzell at jlab.org> wrote:
>>>>>> 
>>>>>> Hello All,
>>>>>> 
>>>>>> These EPICS pvs suffixed by SET are the setpoints used by the PLC when it is
>>>>>> actually flowing gas.  And the START/STOP ones are control outputs from EPICS
>>>>>> to the PLC.  I doubt any of those should be used for trying to understand the
>>>>>> live status of the gas flow.
>>>>>> 
>>>>>> The pvs suffixed by INFLOW/OUTFLOW are readbacks on measured flows.  But I
>>>>>> suspect Brian wants a boolean status for gas flow?  The FLT (fault) column on
>>>>>> that screen may also be useful (see attached screenshot).  Depends on what
>>>>>> logic you want here.  Also, it’s on my todo list to add a summary PV (on ‘OR’
>>>>>> of all faults) and add it to the overview screen for shift workers and alarms.
>>>>>> If that will be useful here, I’ll do it ASAP.  Or let’s define what exactly
>>>>>> you want from EPICS for this and we’ll make it happen.
>>>>>> 
>>>>>> Quentin is the PLC expert on all this and defined the PLC-EPICS communications
>>>>>> that Wesley wrote.
>>>>>> 
>>>>>> Ok, that is my understanding of things.
>>>>>> 
>>>>>> Cheers,
>>>>>> Nathan
>>>>>> 
>>>>>> 
>>>>>> P.S.  PLC appears to be offline currently, but:
>>>>>> https://hallbopi.jlab.org/webopi3.3/w?opi=CLAS12_Menu-web.opi
>>>>>> click CVT->BMTGas for live readings
> 
    
    