[Dsg-mvt] [New Logentry] Follow-up Re: issue with flowmeter reading
beng at jlab.org
beng at jlab.org
Fri Jan 12 10:25:02 EST 2018
Logentry Text:
--
Per discussions with Maxime the logic for the MVT system has been changed to match the DC mixing setup.
Namely it uses a state machine to either have the flow increasing or decreasing based on two pressure setpoints. It still has a max pressure limit (set to 20 psig) where the flow will be set to 0, otherwise if the logic is as follows:
Increasing mode: if pressure >= PHigh go to decreasing mode, otherwise stay in increasing mode
Decreasing mode: if pressure <= PLow go to increase mode, otherwise stay in decreasing mode
Currently, PHigh = 16 psig & PLow = 8 psig
Since the buffer tank has an unknown quality mixture due to the previous fluctuations it probably should be vented and purged with Ar before starting again.
---