[Dsg-rich] Third cable and connector on RICH LV boards' service connector
Amrit Yegneswaran
yeg at jlab.org
Wed Aug 9 20:08:53 EDT 2017
does anybody have a clue of what they want?
when it was first suggested that there is no need for sequencing the shutdown of HV and LV , sequencing was insisted upon.
and now pronto presto , simplificazione!.
we'll wait for confirmation from marco mirizita/contalbrigo.
reading these e-mails i think that there are much more than the interlock signals that are slow.
there's never enough time to do it right the first time, but always enough time to do it over, howso?
From: "Valery Kubarovsky" <vpk at jlab.org>
To: "Tyler Lemon" <tlemon at jlab.org>
Cc: "dsg-rich" <dsg-rich at jlab.org>, "Benjamin Raydo" <braydo at jlab.org>, "Chris Cuevas" <cuevas at jlab.org>
Sent: Wednesday, August 9, 2017 6:03:22 PM
Subject: Re: [Dsg-rich] Third cable and connector on RICH LV boards' service connector
Hi All,
To simplify the interlock system I suggest to use the CAEN mainframe interlock input.
The sequence of shutting off HV and LV that we discussed before is not mandatory.
regards,
Valery
From: "Tyler Lemon" <tlemon at jlab.org>
To: "Chris Cuevas" <cuevas at jlab.org>
Cc: "dsg-rich" <dsg-rich at jlab.org>, "Benjamin Raydo" <braydo at jlab.org>
Sent: Wednesday, August 9, 2017 4:10:46 PM
Subject: Re: [Dsg-rich] Third cable and connector on RICH LV boards' service connector
BQ_BEGIN
Hello Chris,
My reply is inline below in blue.
Hi,
If the 'hardware interlock system' produces an interlock relay closure, and this closure is the logical OR of several signals, then the closure should be connected to the CAEN mainframe interlock input(CPU). Is this the case?
For the LV boards, the hardware interlock system will open a relay to break the short circuits required at the service connector to enable a group's output. This is described in on page 7 of the attached manual for the A2518 boards.
We are not using the interlock input on the CAEN mainframe because when asked, Valery said HV should be turned off before LV. Using the interlock input on the mainframe will shutoff both HV and LV at the same time.
The interlock signals on the A2518 boards control two groups of 4 low voltage outputs. Each output channel has over-voltage and over-current trip points,
We are not monitoring any current or voltage output of HV or LV. The hardware interlock system will only disable HV/LV in the event that one of the hardware interlock system sensors (temperature, humidity, N2 flow, cooling airflow, cooling tank pressure) goes out of the determined limits.
and I do not see the need to interface to each group of LV interlocks if there is a global interlock signal that will latch a disable condition.
We have programed the hardware interlock system in a way that disables all LV groups at once and all HV channels at once. The hardware interlock system does not disable/enable each individual group.
Is it really necessary to sequence the shutoff of HV and LV?
If not, we can change the hardware interlock system code to use the CAEN mainframe interlock input.
Best regards,
Tyler
_______________________________________________
Dsg-rich mailing list
Dsg-rich at jlab.org
https://mailman.jlab.org/mailman/listinfo/dsg-rich
BQ_END
_______________________________________________
Dsg-rich mailing list
Dsg-rich at jlab.org
https://mailman.jlab.org/mailman/listinfo/dsg-rich
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <https://mailman.jlab.org/pipermail/dsg-hallb_rich/attachments/20170809/a0981af2/attachment-0002.html>
More information about the Dsg-rich
mailing list