Hello Tyler,
I got it, thanks,
Valery
> From: "Tyler Lemon" <tlemon at jlab.org>
> To: "dsg-rich" <dsg-rich at jlab.org>
> Sent: Thursday, August 9, 2018 8:22:31 AM
> Subject: [Dsg-rich] error in EP cRIO interlock program found, need to deploy
> corrected code
> Hello Valery,
> Yesterday while causing interlocks to test RICH alarms, I noticed an error on
> EPICS where the EP humidity interlock summaries incorrectly indicate an error
> when EP Temperature 16 interlocks trip.
> This does not prevent the interlock system from operating correctly since it was
> caused by an indexing error in the data sent to EPICS. Everything on the cRIO
> that takes action in the event of an interlock works as it should.
> This morning since RICH is still powered off, we will deploy the corrected
> program that fixes the error in the EPICS interface.
> Best regards,
> Tyler