Walt,
The current setup is a 208 100A panel. This will not provide adequate power to run both compressors at the same time. The options to remedy this are as follows.
Option 1: If both need to run at the same time, upgrade the existing 30kVA transformer to a 75kVA unit, and replace the existing 100A panel with a 225A panel.
Option 2: If both need to run at the same time, install new 30kVA transformer and new 100A panel (will need additional floor space)
Option 3: If only 1 needs to run at a time, install a new DPDT switch by the compressors and utilize the existing 70A feed to run either compressor. This switch runs about $950.
Jason Willoughby
FM&L Electrical Engineer
Thomas Jefferson National Accelerator Facility
628 Hofstadter Road STE 1
Newport News, VA 23606
(757)-269-5372
From: "Walt Akers" <akers at jlab.org>
To: "Brian Eng" <beng at jlab.org>, "Jason Willoughby" <jasonw at jlab.org>
Cc: "Bob Miller" <rmiller at jlab.org>, "dsg-rich" <dsg-rich at jlab.org>
Sent: Wednesday, January 10, 2018 10:57:43 AM
Subject: Re: RICH Compressor in EEL
I'll let Jason weigh in on this, but, I believe that, if the Bertha
is disconnected, this is no longer a hot system and you should
be able to remove the cables - if you know how to do that work.
Walt
Brian Eng wrote:
> Hi Walt,
>
> The current schedule calls for taking the air compressor that is currently located in EEL/125 to Hall B tomorrow morning.
>
> I've already unplugged the Bertha from the wall, but I wasn't sure if we needed plant services to disconnect the Bertha from the compressor.
>
> Thanks
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <https://mailman.jlab.org/pipermail/dsg-hallb_rich/attachments/20180111/6affd7ae/attachment-0002.html>
More information about the Dsg-rich
mailing list