[Dsg-rich] [Rich] FPGA temp alarm

Chris Cuevas cuevas at jlab.org
Tue Oct 16 15:56:57 EDT 2018


Hi,

Software can stop for a variety of reasons, but good to know that there 
is a default watchdog timer on the cRIO. How much time elapses before 
software stoppage is detected and the relay opens?

I am not concerned about  a power off sequence because I know the CAEN 
mainframe and modules will latch OFF until new commands are issued.

Thanks,

-Chris

~~~~~~~~~~~~~~~~~


On 10/16/2018 3:11 PM, Tyler Lemon wrote:
> If the software stops running, the relay goes into its default open 
> state, disabling the CAEN.
>
> The most likely cause of the cRIO's software stopping is a power 
> outage.  In the event of a power outage, there will be a sequence of 
> events (compressor losing power, airflow/tank pressure dropping, 
> interlock tripping) that will disable the CAEN. All components of the 
> hardware interlock system are on UPS, so the hardware interlock 
> components will stay alive long enough after the power outage to 
> disable the CAEN. When the power is restored, the cRIO is set up to 
> automatically run the interlock program on boot. On power restore, the 
> CAEN will remain disabled until all normal operating conditions 
> (airflow, buffer tank pressure, temperatures) are restored and the 
> CAEN's interlocks are cleared.
>
> --Tyler
> ------------------------------------------------------------------------
> *From: *"Chris Cuevas" <cuevas at jlab.org>
> *To: *"Tyler Lemon" <tlemon at jlab.org>
> *Cc: *"Valery Kubarovsky" <vpk at jlab.org>, "Mirazita Marco" 
> <Marco.Mirazita at lnf.infn.it>, rich at jlab.org, "dsg-rich" 
> <dsg-rich at jlab.org>
> *Sent: *Tuesday, October 16, 2018 2:53:02 PM
> *Subject: *Re: [Rich] [Dsg-rich] FPGA temp alarm
>
> Hi Tyler,
>
> So the cRIO software must always be running to detect out of limit 
> signals from the front end sensors? What happens if the software stops 
> running? Is there a default timeout[watchdog] setting that will open 
> the final relay contact?
>
> Thanks for the feedback,
>
> -Chris
>
> ~~~~~~~~~~~
>
>
> On 10/16/2018 1:52 PM, Tyler Lemon wrote:
>
>     Chris,
>
>     For the hardware interlocks, if any of the cRIO-based system's
>     sensors (RTDs, humidity, airflow, air pressure, N2 flow; sensors
>     not dependent on FPGA DAQ readout) go out of limit, the cRIO
>     disables HV and LV by opening a relay contact to the Interlock
>     port on the CAEN mainframe.
>
>     This disables HV and LV and will only allow HV and LV to be
>     re-enabled if the interlock is clear and a user has reset the
>     interlock.
>
>     Regards,
>     Tyler
>
>
>
>
>     ------------------------------------------------------------------------
>     *From: *"Chris Cuevas" <cuevas at jlab.org>
>     *To: *"Valery Kubarovsky" <vpk at jlab.org>, "Mirazita Marco"
>     <Marco.Mirazita at lnf.infn.it>
>     *Cc: *rich at jlab.org, "dsg-rich" <dsg-rich at jlab.org>
>     *Sent: *Tuesday, October 16, 2018 1:38:14 PM
>     *Subject: *Re: [Rich] [Dsg-rich] FPGA temp alarm
>
>     Hi All,
>
>     The FPGAs have a firmware set point for the die temperature. Ben
>     can verify this set point, but it sure sounds like the 'interlock'
>     systems rely on software code. Are there watchdog timers set up in
>     case the code stops running?
>
>     For a true hardware interlock, one that does not depend on
>     software, there should be temperature probes coupled directly to a
>     comparator circuit which latches off the Low_Voltage outputs to
>     the FPGA boards. From these email threads, it sounds like all the
>     temperature devices are monitored with software, and if a software
>     set point threshold is violated, then the Low_Voltage is turned
>     OFF. If the monitored temperature devices go below the software
>     set point threshold, is the Low_Voltage power reapplied automatically?
>
>     Thanks,
>
>     -Chris
>
>     ~~~~~~~~~~~~~~~~~
>
>
>     On 10/16/2018 9:40 AM, Valery Kubarovsky wrote:
>
>         The detector (actually LV in this particular case, because the
>         HV was off at that moment)
>         was shut down by software interlock that monitors the FPGS
>         temperature.
>
>         ------------------------------------------------------------------------
>
>             *From: *"Marco Mirazita" <Marco.Mirazita at lnf.infn.it>
>             *To: *"Tyler Lemon" <tlemon at jlab.org>
>             *Cc: *"Valery Kubarovsky" <vpk at jlab.org>, rich at jlab.org,
>             "dsg-rich" <dsg-rich at jlab.org>
>             *Sent: *Tuesday, October 16, 2018 9:37:41 AM
>             *Subject: *Re: [Rich] [Dsg-rich] FPGA temp alarm
>
>             But we have a soft interlock shutting down the system if fpga
>             temperature goes above 75 deg.
>
>
>             Il 2018-10-16 14:24 Tyler Lemon ha scritto:
>             > Hello Marco,
>             >
>             > The hardware interlock system does not monitor FPGA
>             temperatures. It
>             > monitors the RTDs installed in the EP.
>             >
>             > The hardware interlock system did not trip off the
>             electronics because
>             > the strange temperature readings were only seen on the FPGA
>             > temperature readouts.
>             >
>             > Best regards,
>             > Tyler
>             >
>             > -------------------------
>             >
>             > FROM: "Mirazita Marco" <Marco.Mirazita at lnf.infn.it>
>             > TO: "Valery Kubarovsky" <vpk at jlab.org>
>             > CC: rich at jlab.org, "dsg-rich" <dsg-rich at jlab.org>
>             > SENT: Tuesday, October 16, 2018 8:16:06 AM
>             > SUBJECT: Re: [Rich] [Dsg-rich] FPGA temp alarm
>             >
>             > Hi Valery,
>             > thank you, in fact my main worry was that the interlock
>             didn't shut
>             > down
>             > the electronics.
>             > It would be anyway good to understand why we had this event.
>             > I saw from the strip charts that also the LV currents
>             and voltages
>             > have
>             > frequent random spikes.
>             > Marco
>             >
>             > Il 2018-10-16 13:55 Valery Kubarovsky ha scritto:
>             >> Marco,
>             >> If you take a more careful look you will find out that
>             the LV was
>             > shut
>             >> down.
>             >> The HV was off. We investigate the reason. It is the
>             first time we
>             > had
>             >> such an event.
>             >> Probably it was connected with the software update that
>             was done
>             >> approximately at the same time.
>             >> Regards,
>             >> Valery
>             >>
>             >> -------------------------
>             >>
>             >>> FROM: "Marco Mirazita" <Marco.Mirazita at lnf.infn.it>
>             >>> TO: dsg-rich at jlab.org, rich at jlab.org
>             >>> SENT: Tuesday, October 16, 2018 4:03:24 AM
>             >>> SUBJECT: [Dsg-rich] FPGA temp alarm
>             >>
>             >>> Hi all,
>             >>> yesterday at about 4:20 pm jlab time I received
>             several alarm
>             >>> messages
>             >>> saying that the FPGA temperatures reached values
>             around 115 deg.
>             >>> Since it looked like a readout error, I checked the
>             strip chart,
>             >>> where
>             >>> there is actually a spike in the readout at that time,
>             but to
>             > values
>             >>> of
>             >>> the order of -10^5. See the attached plot.
>             >>> So, it is clear that it was a readout error, but it is
>             strange that
>             >>> the
>             >>> alarm message and epics report different values.
>             >>> Also, according to the logbook, the electronics was
>             not shut down
>             > by
>             >>> the
>             >>> interlocks, as should have happened if the temperature
>             really went
>             >>> above
>             >>> 100 deg.
>             >>> So, perhaps the values reported in the alarm messages
>             are not the
>             >>> correct ones?
>             >>> Marco
>             >>>
>             >>> _______________________________________________
>             >>> Dsg-rich mailing list
>             >>> Dsg-rich at jlab.org
>             >>> https://mailman.jlab.org/mailman/listinfo/dsg-rich
>             >>
>             >> _______________________________________________
>             >> Dsg-rich mailing list
>             >> Dsg-rich at jlab.org
>             >> https://mailman.jlab.org/mailman/listinfo/dsg-rich
>             > _______________________________________________
>             > Rich mailing list
>             > Rich at jlab.org
>             > https://mailman.jlab.org/mailman/listinfo/rich
>
>
>
>         _______________________________________________
>         Rich mailing list
>         Rich at jlab.org
>         https://mailman.jlab.org/mailman/listinfo/rich
>
>
>
>     _______________________________________________
>     Rich mailing list
>     Rich at jlab.org
>     https://mailman.jlab.org/mailman/listinfo/rich
>
>
>