[Dsg-rich] [Revised Logentry] Backup N2 pressure transducers wired to cRIO
tlemon at jlab.org
tlemon at jlab.org
Mon Feb 4 11:50:03 EST 2019
Logentry Text:
--
RICH N2 backup manifold PTs have been wired to cRIO. The cRIO is powered back on.
The EPICS PVs for the PTs are:
B_DET_RICH_INTLK_N2_BACKUP_PT2
B_DET_RICH_INTLK_N2_BACKUP_PT3
The PTs are Dwyer 0-50 psia pressure transducers (model 626-02-GH-P1-E1-S1). They are absolute pressure transducers so their output signal is 1 atm (~14 psi) higher than expected gauge pressure. The conversion from absolute to gauge pressure has been added to the cRIO's LabVIEW program by subtracting 14.6959 from the absolute pressure.
---