Hi Marco,
Is there a set schedule for the tests where the compressor is needed? We can plan to have the compressor turned back on in time for that if there is.
Looking at the archived compressor data since it has been turned on and running steadily, we can see that the compressor is not doing its typical "saw-tooth" pattern that we saw this past April. All other cooling parameters are similar to previous experimental runs.
Attached are plots of archived data: one from the past ~24 hours, and one from about one year ago in September 2018. The one from September 2018 shows the typical "saw-tooth" pattern we expect, but the one from the past 24 hours does not.
The only difference between the two plots is the ambient pressure is higher (411 inches-H2O vs 408 inches-H2O) in the one from September 2018, but I am unsure if this is a big enough difference to cause the saw-tooth pattern to not occur.
Best regards,
Tyler
________________________________
From: Marco Mirazita <Marco.Mirazita at lnf.infn.it>
Sent: Tuesday, October 8, 2019 12:04 PM
To: Tyler Lemon <tlemon at jlab.org>
Cc: dsg-rich at jlab.org <dsg-rich at jlab.org>
Subject: [EXTERNAL] Re: [Dsg-rich] [New Logentry] RICH compressor ON after maintenance
Hi Tyler,
I completed this first test on the RICH (elog
https://logbooks.jlab.org/entry/3733786) and the detector is now off.
I would ask you to turn the compressor also off, unless you need to make
some further test.
The compressor on and electronics off is a condition we want to avoid,
because it generates an increase of the humidity inside the RICH.
Thank you,
Marco
Il 2019-10-07 20:20 tlemon at jlab.org ha scritto:
> RICH COMPRESSOR ON AFTER MAINTENANCE [1]
>
> * Edit [2]
> * Delete [3]
>
> Lognumber 3733741 [1]. Submitted by tlemon [4] on Mon, 10/07/2019 -
> 14:16 [5].
>
> LOGBOOKS:
> RICH [6]
>
> ENTRY MAKERS:
> ambrown, campero, mealer
>
> The compressor in the RICH air-cooling system has been turned on after
> maintenance on and replacement of the buffer tank PT.
>
> All compressor settings are the same as during the spring physics run:
> Compressor internal on-off settings: on at 104 psi; off at 113 psi
> (highest output range allowable on compressor)
> Airflow 1: 500 slm
> Airflow 2: 400 slm
>
> The new PT installed on the buffer tank appears to match the pressure
> indicated by the buffer tank's local pressure gauge. Because of this,
> the PT reading may be a little different than before.
>
> Since the cooling system is back online, RICH electronics can now be
> powered.
>
>
> Links:
> ------
> [1] https://logbooks.jlab.org/entry/3733741
> [2] https://logbooks.jlab.org/entry/3733741/edit?destination=email/send
> [3]
> https://logbooks.jlab.org/entry/3733741/delete?destination=email/send
> [4] https://logbooks.jlab.org/user/tlemon
> [5]
> https://logbooks.jlab.org/entries?start_date=1570468581&end_date=1570475781&book=RICH
> [6] https://logbooks.jlab.org/book/rich
>
> _______________________________________________
> Dsg-rich mailing list
> Dsg-rich at jlab.org
> https://mailman.jlab.org/mailman/listinfo/dsg-rich
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <https://mailman.jlab.org/pipermail/dsg-hallb_rich/attachments/20191008/0fb0cd21/attachment-0002.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: RICH_cooling_2019-10-08.PNG
Type: image/png
Size: 113519 bytes
Desc: RICH_cooling_2019-10-08.PNG
URL: <https://mailman.jlab.org/pipermail/dsg-hallb_rich/attachments/20191008/0fb0cd21/attachment-0004.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: RICH_cooling_2018-09-03.PNG
Type: image/png
Size: 154309 bytes
Desc: RICH_cooling_2018-09-03.PNG
URL: <https://mailman.jlab.org/pipermail/dsg-hallb_rich/attachments/20191008/0fb0cd21/attachment-0005.png>
More information about the Dsg-rich
mailing list