do you mean  to insert a "chiller"?
That would be a good thing, but one must carefully study it in order to 
avoid any condensation of water vapor in the piping inside the 
Electronic Panel.

Il 2019-09-27 20:25 Tyler Lemon ha scritto:
> Hi Sandro,
> 
>  In addition to what George mentioned, DSG is also looking into the
> concept of an externally-cooled compressor system that would be able
> to provide cooled air to RICH, increasing the current compressors'
> cooling capabilities. Depending on what we find, such a system may
> allow us to cool two RICH sectors with one compressor.
> 
>  Once we have any other information on how this could be done, we will
> distribute the info to the RICH collaboration.
> 
>  Best regards,
>  Tyler
> 
> -------------------------
> 
> FROM: Dsg-rich <dsg-rich-bounces at jlab.org> on behalf of George Jacobs
> <jacobsg at jlab.org>
>  SENT: Friday, September 27, 2019 1:37 PM
>  TO: Tomassini Sandro <sandro.tomassini at lnf.infn.it>;
> dsg-rich at jlab.org <dsg-rich at jlab.org>
>  SUBJECT: Re: [Dsg-rich] [EXTERNAL] RICH electronics
> 
>  Hi Sandro,
> 
>  If I remember correctly, each line is currenly supplied by it's own
> rotameter. So, if you want to do this, you must contact the Hall B
> Engineer. He is the system owner. He is in charge of the system. You
> may or may not need a TOSP for this, but that is up to Hall B.
> 
>  There are other things you can do to improve cooling efficiency. For
> example, cable routing inside the e-panel should be improved in the
> next RICH sector. Another, would be exploring the use of finned
> plastic heat sinks on the components to increase the surface area to
> be cooled.
> 
>  Cheers,
>  George
> 
> --
>  George Jacobs
>  Jefferson Lab (TJNAF)
>  STE 12
>  12000 Jefferson Ave.
>  Newport News, VA 23606
>  (office) 757-269-7021
>  (email) jacobsg at jlab.org
> 
> -------------------------
> 
> FROM: Dsg-rich <dsg-rich-bounces at jlab.org> on behalf of Tomassini
> Sandro <sandro.tomassini at lnf.infn.it>
>  SENT: Friday, September 27, 2019 5:03 AM
>  TO: dsg-rich at jlab.org <dsg-rich at jlab.org>
>  SUBJECT: Re: [Dsg-rich] [EXTERNAL] RICH electronics
> 
> Hi All,
> inside the rich e-panel there are two air manifolds but I do not
> remember if we have the possibility to adjust the flow separately.
> What might be interesting to test is to change the flow in the two
> manifolds separately in order to find the best setup that minimizes
> the flow towards the detector keeping a good safety margin on the max
> temperatures on the electronic boards.
> May be I am dreaming...
> George is this possible in your opinion?
> Hope to see you soon
> 
> Many thanks
> 
> Sandro
> 
> Il 24/09/2019 14:23, Tyler Lemon ha scritto:
> 
>> Hello,
>> 
>> From Ben and Mateo's reply, it seems the goal of the test should be
>> to keep the same temperatures in RICH as previous running periods.
>> 
>> Ideally, the test would involve finding what airflow settings are
>> required to maintain ~65 C in RICH FPGAs. It may be that 900 slm is
>> actually required to keep temperatures in the appropriate range.
>> 
>> At a bare minimum, the tests should involve adjusting compressor
>> settings with the goal of maintaining 900 slm total flow. For this,
>> RICH electronics can be left off since the airflow measurements
>> would be the indicator of test results.
>> 
>> It is as Marco said, we never tried to optimize the cooling system.
>> These tests would be the only way to see what is actually needed to
>> cool RICH and to see whether the current cooling system could even
>> provide enough flow for two RICH sectors.
>> 
>> - Tyler
>> 
>> -------------------------
>> 
>> FROM: Marco Mirazita <Marco.Mirazita at lnf.infn.it>
>> SENT: Tuesday, September 24, 2019 4:18 AM
>> TO: Amrit Yegneswaran <yeg at jlab.org>
>> CC: Benjamin Raydo <braydo at jlab.org>; Tyler Lemon
>> <tlemon at jlab.org>; dsg-rich <dsg-rich at jlab.org>
>> SUBJECT: Re: [Dsg-rich] [EXTERNAL] RICH electronics
>> 
>> Hi all,
>> let me make a couple of remarks.
>> 
>> 1) The temperature limits were set to ensure a safe operation of
>> the
>> whole system, which, as Ben said, includes not just the FPGA, but
>> cables, MAROC, external temperature close to TOF, etc. I don't want
>> to
>> change these limits unless strictly necessary and only if with no
>> risk
>> for the detectors.
>> However, we know that the current running conditions are mostly
>> driven
>> by one FPGA which is producing more heat (its temperature is about
>> 2 or
>> 3 degrees higher than the neighbors) and by chance it is also in
>> the
>> hottest spot of the panel.
>> 
>> 2) The cooling system was originally designed to be able to feed
>> two
>> RICH modules with one compressor, in case of failure of the other
>> one.
>> We are now far from this situation. We run one RICH with 900 slm
>> with a
>> maximum of 1200 slm per compressor. But we never attempted a real
>> optimization of the air flow. For example, the lower line is
>> flowing
>> less air than the upper one, while I would expect the opposite.
>> 
>> For these reasons, I think there could be room to optimize the
>> running
>> conditions and get closer to the original design.
>> But let me stress again that this optimization must ensure to stay
>> within the safety limits.
>> 
>> Best regards,
>> Marco
>> 
>> Il 2019-09-24 04:12 Amrit Yegneswaran ha scritto:
>>> given ben's last sentence
>>> 
>>> (highlighted; i guess "it" in the sentence refers to "the
>>> temperature" as does "that".
>>> from which we have it = that => i = hat or i =tha, aah the
>> pronouns
>>> they are precious!)
>>> 
>>> anyway i'm now very confused about the planned test and the
>> intent
>>> thereof?
>>> 
>>> are we thinking reducing the airflow from ~950 slm will reduce
>> the
>>> temperature below 65c?
>>> pardon my obtuseness.
>>> 
>>> so what mods are you conjuring up tyler?
>>> 
>>> -------------------------
>>> 
>>> FROM: Benjamin Raydo <braydo at jlab.org>
>>> SENT: Monday, September 23, 2019 5:33 PM
>>> TO: Tyler Lemon <tlemon at jlab.org>; Amrit Yegneswaran
>> <yeg at jlab.org>;
>>> Marco Mirazita <Marco.Mirazita at lnf.infn.it>
>>> CC: dsg-rich <dsg-rich at jlab.org>
>>> SUBJECT: Re: [Dsg-rich] [EXTERNAL] RICH electronics
>>> 
>>> Hi Tyler,
>>> 
>>> Matteo is correct about the temperature limit of 85C to respect
>> the
>>> FPGA timing constraints, but we also have fiber cables running
>> close
>>> to those parts that are rated for 80C (I'd expect some
>> deformation
>>> possible if we go above this for a long period).
>>> 
>>> Can we set a safe limit of 75C for any reported FPGA temperature
>> for
>>> your tests (short term limit: <1hr)? If your tests need to run in
>> such
>>> a way that you want a higher limit, let us discuss again if you
>> don't
>>> mind. For long term it would be great to keep it as low as
>> possible
>>> and for the moment I believe we've been running with the hottest
>> FPGA
>>> temp to be around 65C so don't want to see that increase
>> significantly
>>> if there are any changes to the cooling.
>>> 
>>> Hope that helps.
>>> 
>>> Thanks,
>>> Ben
>>> 
>>> -------------------------
>>> 
>>> FROM: Tyler Lemon <tlemon at jlab.org>
>>> SENT: Monday, September 23, 2019 4:59 PM
>>> TO: Amrit Yegneswaran <yeg at jlab.org>; Marco Mirazita
>>> <Marco.Mirazita at lnf.infn.it>; Benjamin Raydo <braydo at jlab.org>
>>> CC: dsg-rich <dsg-rich at jlab.org>
>>> SUBJECT: Re: [Dsg-rich] [EXTERNAL] RICH electronics
>>> 
>>> Hi Ben,
>>> 
>>> In October, we're planning on doing some testing to optimize
>> RICH's
>>> cooling system and see what would needed to modify the system to
>> cool
>>> two RICH sectors.
>>> 
>>> With respect to the RICH readout electronics, FPGAs, and their
>>> timing, are there any temperature limits we should take into
>>> consideration when testing the cooling system?
>>> 
>>> Thanks,
>>> Tyler
>>> 
>>> -------------------------
>>> 
>>> FROM: Amrit Yegneswaran <yeg at jlab.org>
>>> SENT: Monday, September 23, 2019 4:48 PM
>>> TO: Tyler Lemon <tlemon at jlab.org>; Marco Mirazita
>>> <Marco.Mirazita at lnf.infn.it>
>>> CC: dsg-rich <dsg-rich at jlab.org>
>>> SUBJECT: Re: [Dsg-rich] [EXTERNAL] RICH electronics
>>> 
>>> tyler
>>> address fpga temp issue with ben.
>>> i believe 60c is right at the edge of timing issues, not sure.
>>> -------------------------
>>> 
>>> FROM: Dsg-rich <dsg-rich-bounces at jlab.org> on behalf of Tyler
>> Lemon
>>> <tlemon at jlab.org>
>>> SENT: Monday, September 23, 2019 3:11 PM
>>> TO: Marco Mirazita <Marco.Mirazita at lnf.infn.it>
>>> CC: dsg-rich <dsg-rich at jlab.org>
>>> SUBJECT: Re: [Dsg-rich] [EXTERNAL] RICH electronics
>>> 
>>> Hi Marco,
>>> 
>>> Looking back at EP temperatures during steady operations (I
>> picked
>>> 3/10/2019 to 3/31/2019), Hardware Interlock RTDs were ~40 deg C
>> and
>>> FPGA temperatures were ~60 deg C.
>>> 
>>> Is there a temperature increase that would be considered
>> acceptable?
>>> For example if the FPGA temperatures were ~70 deg C rather than
>> ~60
>>> deg C?
>>> 
>>> The first test should be determining what flow rate is actually
>>> needed to maintain EP temperatures in that acceptable range with
>> all
>>> RICH electronics on.
>>> 
>>> -Tyler
>>> 
>>> -------------------------
>>> 
>>> FROM: Marco Mirazita <Marco.Mirazita at lnf.infn.it>
>>> SENT: Monday, September 23, 2019 9:01 AM
>>> TO: Tyler Lemon <tlemon at jlab.org>
>>> CC: dsg-rich <dsg-rich at jlab.org>
>>> SUBJECT: Re: [Dsg-rich] [EXTERNAL] RICH electronics
>>> 
>>> Hi Tyler,
>>> sorry, I had in mind that the replacement of the PT was scheduled
>> for
>>> 
>>> last Wednesday.
>>> 
>>> The tests we have in mind to optimize the cooling system is
>> basically
>>> 
>>> what you said. But we still have to make a plan of the specific
>>> measurements we need. We will do this plan in the next weeks.
>>> Any suggestion from you and the DSG is welcome.
>>> 
>>> Best regards,
>>> Marco
>>> 
>>> Il 2019-09-20 20:46 Tyler Lemon ha scritto:
>>> > Hi Marco,
>>> >
>>> > The PT replacement has not been completed. It is scheduled for
>> next
>>> > Wednesday September 25.
>>> >
>>> > As for the visit to optimize RICH running conditions, I will
>> not be
>>> > at work for at least part of the week of October 21 to October
>> 25,
>>> > however there should be other people from DSG that would be
>> able to
>>> > help.
>>> >
>>> > What tests are being planned for the visit? Would it
>> essentially be
>>> > varying the settings of the cooling system (flow rate, buffer
>> tank
>>> > pressure, compressor output pressure) and seeing how the
>>> temperature
>>> > within RICH is affected?
>>> >
>>> > Best regards,
>>> > Tyler
>>> >
>>> > -------------------------
>>> >
>>> > FROM: Marco Mirazita <Marco.Mirazita at lnf.infn.it>
>>> > SENT: Friday, September 20, 2019 12:21 PM
>>> > TO: Tyler Lemon <tlemon at jlab.org>
>>> > CC: dsg-rich <dsg-rich at jlab.org>; Valery Kubarovsky
>> <vpk at jlab.org>;
>>> > marco contalbrigo <mcontalb at fe.infn.it>
>>> > SUBJECT: Re: [EXTERNAL] RICH electronics
>>> >
>>> > Hi Tyler,
>>> > do you know if Bob has completed the replacement of the FT?
>>> > If so, the compressor could be restarted on Monday morning,
>> once we
>>> > are
>>> > sure everything is working properly I can turn on the RICH
>>> > electronics
>>> > and keep it on for the night and then make the tests on Tuesday
>>> > morning.
>>> >
>>> > As you know, we didn't have much time to optimize the working
>> point
>>> > of
>>> > the cooling system after the RICH installation, we simply
>> choose
>>> > running
>>> > conditions that ensure a safe operation of the detector.
>>> > But these running conditions might be problematic with two RICH
>>> > modules
>>> > and definitely not sustainable in case of failure of one of the
>> two
>>> > compressors.
>>> > Therefore, also in preparation of the upcoming CLAS12 data
>> taking,
>>> > I'm
>>> > planning a visit to JLab for Dario and Sandro to try to
>> optimize
>>> the
>>> > running conditions, and to be effective this work must be
>>> coordinated
>>> >
>>> > with you and the DSG.
>>> > The proposed dates are from October 21 to October 31. Is this
>> plan
>>> ok
>>> >
>>> > for you?
>>> > Thank you,
>>> > Marco
>>> >
>>> > Il 2019-09-18 14:12 Tyler Lemon ha scritto:
>>> > > Hi Marco,
>>> > >
>>> > > Bob Miller has scheduled the replacement of the faulty
>> pressure
>>> > > transducer (PT) on the air-cooling buffer tank for next
>>> Wednesday,
>>> > > September 25.
>>> > >
>>> > > Could the tests be scheduled to start Thursday September 26?
>>> > >
>>> > > Best regards,
>>> > > Tyler
>>> > >
>>> > > -------------------------
>>> > >
>>> > > FROM: Marco Mirazita <Marco.Mirazita at lnf.infn.it>
>>> > > SENT: Wednesday, September 18, 2019 4:08 AM
>>> > > TO: Tyler Lemon <tlemon at jlab.org>
>>> > > CC: dsg-rich <dsg-rich at jlab.org>; Valery Kubarovsky
>>> <vpk at jlab.org>;
>>> > > marco contalbrigo <mcontalb at fe.infn.it>
>>> > > SUBJECT: [EXTERNAL] RICH electronics
>>> > >
>>> > > Hi Tyler,
>>> > > the RICH electronics is off since quite a lot of time and in
>>> > > preparation
>>> > > of the upcoming CLAS12 running I would like to turn it on to
>>> verify
>>> > > that
>>> > > everything is still working and eventually to take new scaler
>>> > > calibration data.
>>> > > I could plan this work for the beginning of the next week.
>>> > > In preparation for that, we should coordinate to have all the
>>> > systems
>>> > >
>>> > > ready. Would you be available to start the compressor for the
>>> test?
>>> > > Thank you,
>>> > > Marco
>>> >
>>> > _______________________________________________
>>> > Dsg-rich mailing list
>>> > Dsg-rich at jlab.org
>>> > https://mailman.jlab.org/mailman/listinfo/dsg-rich [1] [1]
>>> 
>>> 
>>> Links:
>>> ------
>>> [1] https://mailman.jlab.org/mailman/listinfo/dsg-rich [1]
>> 
>> _______________________________________________
>> Dsg-rich mailing list
>> Dsg-rich at jlab.org
>> https://mailman.jlab.org/mailman/listinfo/dsg-rich [1]
> 
> --
> -----------------------------------------
> Dr. Eng. Sandro Tomassini
> Istituto Nazionale di Fisica Nucleare
> Laboratori Nazionali di Frascati
> ---Research Division---
> P.O.Box 13 00044 Frascati (RM) Italy
> Tel. office: +39 06 9403 2919/8089
> Fax: +39 06 94032256
> e-mail: sandro.tomassini at lnf.infn.it
> https://urldefense.proofpoint.com/v2/url?u=http-3A__www.lnf.infn.it_&d=DwICAg&c=CJqEzB1piLOyyvZjb8YUQw&r=sLmN_kLNB8f_QBCYTgZaO1cK1zcpXSUHz0BQf_04bYk&m=FYoZuKxMGYYuG3IPrj9aJCaZXOVGlmjcK_ELUvTQ3Ls&s=hB5tTkKv7HHYhusEfsdhJO3_S19e2kSvXldaAjSzTg4&e=  [2]
> -----------------------------------------
> --
> 
> 
> Links:
> ------
> [1] https://mailman.jlab.org/mailman/listinfo/dsg-rich
> [2]
> https://urldefense.proofpoint.com/v2/url?u=http-3A__www.lnf.infn.it_&d=DwMD-g&c=CJqEzB1piLOyyvZjb8YUQw&r=sLmN_kLNB8f_QBCYTgZaO1cK1zcpXSUHz0BQf_04bYk&m=Ks_koQB8zfdhAZpqWi1ulFQVWFGW3EuWLeBlPjTyTDs&s=sUK8i5XKeQizqnO1zVv4v1N6p7Mr7ouujo4N8w-3gRQ&e=
> 
> _______________________________________________
> Dsg-rich mailing list
> Dsg-rich at jlab.org
> https://mailman.jlab.org/mailman/listinfo/dsg-rich




More information about the Dsg-rich mailing list