[Dsg-rtpc] Questions about the gas systems
George Jacobs
jacobsg at jlab.org
Wed Jun 27 11:15:59 EDT 2018
Hi All,
The 25 psi relief valve setpoint is too low. The MFC require 30 psi to operate. The 25 psi relief was chosen for use when the system used a rotometer. This was an earlier design.
Please consider the 75 psi setpoint relief valve to be a place holder with a reasonable setpoint. You can choose any relief valve you prefer.
The orifice selected is a standard precise orifice, O'Keefe Controls, we use these in many gas cylinder supply setups of this type. You can also consider it, a place holder and choose one of your own preference.
There is a short write up I did on this system a couple weeks ago located on the jlab O: drive. I am out of the office today, perhaps Brian or Mark can send you a copy of it.
George
From: "William Crahen" <wcrahen at jlab.org>
To: "Brian Eng" <beng at jlab.org>, dsg-rtpc at jlab.org
Cc: "Bob Miller" <rmiller at jlab.org>
Sent: Tuesday, June 26, 2018 5:24:43 PM
Subject: Re: [Dsg-rtpc] Questions about the gas systems
So this valve has a minimum crack pressure of 25 psig, which would be
okay, it just means that all piping going from the gas shed to the mass
flow controller must be per ASME B31.3, or perhaps B31.9 (We used 31.9
for the hall D FDC, and Tim Whitlatch is on the pressure system
committee, so I don't see a reason we can't use for the CO2/Helium
stuff). I see what appears to be an orifice disc on the high pressure
side of the supply regulator-do we have the cut sheet on that? that is
typically the design limiter for un-controlled flow- you assume the
regulator fails at full gas bottle pressure (3500 psi?) and calculate
what flow can occur- that sizes your relief valve.
On 6/26/2018 4:47 PM, Brian Eng wrote:
> Not sure if it's on hand or not, but here's some information on that ASME relief valve from their site: http://www.cdivalve.com/products/valves/air-compressor-valves/asme-code-safety-valves
>
> Specs: http://www.cdivalve.com/images/uploads/ST.png
> Drawing: http://www.cdivalve.com/files/upload/23/st25.pdf
> Flow Chart: http://www.cdivalve.com/files/upload/23/flow_charts_st.pdf
>
> Hope that helps.
>
>> On Jun 26, 2018, at 4:34 PM, Carlos Ayerbe <gayoso at jlab.org> wrote:
>>
>> FYI
>>
>> Goerge already has it.
>>
>> -Carlos
>>
>> ----- Forwarded Message -----
>> From: "William Crahen" <wcrahen at jlab.org>
>> To: "George Jacobs" <jacobsg at jlab.org>, "Carlos Ayerbe Gayoso" <gayoso at jlab.org>
>> Cc: "Bob Miller" <rmiller at jlab.org>
>> Sent: Tuesday, June 26, 2018 4:30:48 PM
>> Subject: Questions about the gas systems
>>
>> Hi guys- Carlos provided me with some documentation on the parts you are
>> planning to use- I see a parts list showing a relief valve RV1 = STLMO
>> model ST25-1/4", set to crack at 75 psi, presumably accommodating 74
>> scfm at some higher pressure. Do you plan to use this? If so, I need to
>> see a cut sheet on it with flow curves, etc. Alternately, is this
>> replaced by the CONRADER valve I find elsewhere in this documentation?
_______________________________________________
Dsg-rtpc mailing list
Dsg-rtpc at jlab.org
https://mailman.jlab.org/mailman/listinfo/dsg-rtpc
--
George Jacobs
Physics Detector Support Group
Jefferson Lab
12000 Jefferson Ave.
STE 12
Newport News, VA 23606
(office) 757-269-7115
(cell) 757-876-0480
(email) jacobsg at jlab.org