Hi,

It appears that your expectation is not correct.
I stopped reviewing the code when I found the following.

Issues found:

Rung 0
The MPS_WA_Value will always be greater than ADC_Readback_MPS

The WA value is the PSU set value 0 to 100% or 0 to 999999
The readback value is always a factor of 10 less.

Rung 2
I_MOL is the current set value 0 to 3000 amps., it will never match the ADC readback.

Unknown, possible runaway, condition when there is an interlock, the PSU ramps down, operator resets the interlock, and restarts.

Cheers,
Mike




----- Original Message -----
From: "Amanda Hoebel" <amandah at jlab.org>
To: "dsg-hallc controls" <dsg-hallc_controls at jlab.org>
Sent: Monday, July 30, 2018 4:49:35 PM
Subject: [Dsg-hallc_controls] Current regulation loop

Hello Steve and Mike,

Updated versions of the HMS and SHMS programs to include the current regulation loop are in the M: drive, "M:\dsg-hallc_controls\HMS_Controls_V20_current_loop.ACD" and "M:\dsg-hallc_controls\SHMS_V_20_current_loop.ACD". The program was tested using the DSG test PLC and a serial program to simulate the danfysik power supply. The program ran as expected and allowed the user to change setpoints mid-ramp without issue. 