[Dsg-hallc_controls] Current regulation loop
Mike Fowler
fowler at jlab.org
Wed Aug 1 10:29:53 EDT 2018
Hi,
We need a copy of your code and only the changes you propose to make.
The ADC file you modified is old and if loaded into the PLC it would cause operational problems.
We need to be able to copy and paste your code into the running system, not replace the running system.
Cheers,
Mike
----- Original Message -----
From: "Mike Fowler" <fowler at jlab.org>
To: "Amanda Hoebel" <amandah at jlab.org>
Cc: "dsg-hallc controls" <dsg-hallc_controls at jlab.org>
Sent: Wednesday, August 1, 2018 9:02:16 AM
Subject: Re: [Dsg-hallc_controls] Current regulation loop
Hi,
It appears that your expectation is not correct.
I stopped reviewing the code when I found the following.
Issues found:
Rung 0
The MPS_WA_Value will always be greater than ADC_Readback_MPS
The WA value is the PSU set value 0 to 100% or 0 to 999999
The readback value is always a factor of 10 less.
Rung 2
I_MOL is the current set value 0 to 3000 amps., it will never match the ADC readback.
Unknown, possible runaway, condition when there is an interlock, the PSU ramps down, operator resets the interlock, and restarts.
Cheers,
Mike
----- Original Message -----
From: "Amanda Hoebel" <amandah at jlab.org>
To: "dsg-hallc controls" <dsg-hallc_controls at jlab.org>
Sent: Monday, July 30, 2018 4:49:35 PM
Subject: [Dsg-hallc_controls] Current regulation loop
Hello Steve and Mike,
Updated versions of the HMS and SHMS programs to include the current regulation loop are in the M: drive, "M:\dsg-hallc_controls\HMS_Controls_V20_current_loop.ACD" and "M:\dsg-hallc_controls\SHMS_V_20_current_loop.ACD". The program was tested using the DSG test PLC and a serial program to simulate the danfysik power supply. The program ran as expected and allowed the user to change setpoints mid-ramp without issue.
Regards,
Amanda
_______________________________________________
Dsg-hallc_controls mailing list