[Dsg-hallc_controls] Hall C HMI screens
Jack Segal
segal at jlab.org
Tue Aug 28 18:06:35 EDT 2018
Ideally we would have been able to spend time on controls GUIs before we started running.
I did a little poking around at one point. Queries on the EPICS Archiver gave me the attached
results. I did not have time to do anything further with the information.
I think that for general use in the halls we would like to develop some GUIs and have the
displays pushed out in the
https://epicsweb.jlab.org/wmenu/
webserver (login is your CUE account). Similar to what has been done for Hall A and others.
For example:
https://epicsweb.jlab.org/wedm/screen?edl=/cs/opshome/edm/HALLA/tools/tmpwrkDisplay.edl
https://epicsweb.jlab.org/wedm/screen?edl=/cs/opshome/edm/cryo/CRYO_O_totalmenu.edl
https://epicsweb.jlab.org/wedm/screen?edl=hacryo/right72/HACRYO_O_right_D1test1.edl
In the end this will be easier for the users and techs than dealing with the PLC oddities
when just looking for status and information. It is also readily accessible from offsite.
On 8/28/2018 4:10 PM, Brian Eng wrote:
> Hi Steve,
>
> Is there a general Hall C account that should be used to pull up the EPICS screens? If so, which machine should be used?
>
> Or is there a list of PVs somewhere?
>
>> On Aug 28, 2018, at 4:05 PM, Steve Lassiter <lassiter at jlab.org> wrote:
>>
>> Hello All,
>>
>> Just a reminder not to open an HMI screen (Magnet GUI) while the experiments are ongoing, without first contacting the counting house.
>> DO NOT remote login to cmagnets as this is for the experimenters only now.
>> DO NOT use skylla7 as the is reserved for Mike.
>>
>> Thanks
>> Steven
--
John(Jack) Segal
Halls A and C Spectrometer Support Manager
Thomas Jefferson National Accelerator Facility
12000 Jefferson Avenue
Suite 12
Newport News, VA 23606-4486
Phone: (757) 269-7242
Cell: (757) 320-9977
-------------- next part --------------
CFI6731C: host=opsmya7, active=1, request=1, type=6, size=1, deadband='0.01' {Cryogenics}
CTD673: host=opsmya6, active=1, request=1, type=6, size=1, deadband='0.1' {Cryogenics}
CPI673: host=opsmya6, active=1, request=1, type=6, size=1, deadband='0.05' {Cryogenics}
CTD9541: host=opsmya13, active=1, request=1, type=6, size=1, deadband='0.01' {Cryogenics}
CPI9541: host=opsmya6, active=1, request=1, type=6, size=1, deadband='0.05' {Cryogenics}
CFI60DLP: host=opsmya4, active=1, request=1, type=6, size=1, deadband='0.01' {Cryogenics}
CTD6614: host=opsmya13, active=1, request=1, type=6, size=1, deadband='0.01' {Cryogenics}
CFI6711C: host=opsmya7, active=1, request=1, type=6, size=1, deadband='0.01' {Cryogenics}
CTD671SC: host=opsmya13, active=1, request=1, type=6, size=1, deadband='0.01' {Cryogenics}
CPI671SC: host=opsmya7, active=1, request=1, type=6, size=1, deadband='0.01' {Cryogenics}
CTD672: host=opsmya13, active=1, request=1, type=6, size=1, deadband='0.01' {Cryogenics}
CPI672: host=opsmya6, active=1, request=1, type=6, size=1, deadband='0.01' {Cryogenics}
VWienAngle: host=opsmya0, active=1, request=1, type=6, size=1 {INJTWF}
MWF1I04.BDL: host=opsmya3, active=1, request=1, type=6, size=1 {magnets MyRestore}
IGL1I00OD16_4: host=opsmya5, active=1, request=1, type=3, size=1 {IPOPTO MyRestore}
IGL1I00DAC6: host=opsmya5, active=1, request=1, type=6, size=1 {IGLdac MyRestore}
Phi_FG: host=opsmya0, active=1, request=1, type=6, size=1 {INJTWF}
MFG1I04A.BDL: host=opsmya0, active=1, request=1, type=6, size=1 {magnets MyRestore}
MFG1I04B.BDL: host=opsmya0, active=1, request=1, type=6, size=1 {magnets MyRestore}
HWienAngle: host=opsmya0, active=1, request=1, type=6, size=1 {INJTWF}
MWF0I02.BDL: host=opsmya0, active=1, request=1, type=6, size=1 {magnets MyRestore}
IGL1I00OD16_9: host=opsmya5, active=1, request=1, type=3, size=1 {IPOPTO MyRestore}
IGL1I00DAC5: host=opsmya5, active=1, request=1, type=6, size=1 {IGLdac MyRestore}
psub_aa_pos: host=opsmya0, active=1, request=1, type=6, size=1 {laser}
IGL1I00OD16_16: host=opsmya5, active=1, request=1, type=3, size=1 {IPOPTO MyRestore}
IGL1I00DI24_24M: host=opsmya5, active=1, request=1, type=3, size=1 {IPDIGITAL24}
psub_pl_pos: host=opsmya5, active=1, request=1, type=6, size=1 {helicityControl}
C1068_QDAC07: host=opsmya0, active=1, request=1, type=6, size=1, deadband='1' {QDAC}
C1068_QDAC08: host=opsmya0, active=1, request=1, type=6, size=1, deadband='1' {QDAC}
C1068_QDAC09: host=opsmya0, active=1, request=1, type=6, size=1, deadband='1' {QDAC}
C1068_QDAC10: host=opsmya0, active=1, request=1, type=6, size=1, deadband='1' {QDAC}
C1068_QDAC11: host=opsmya0, active=1, request=1, type=6, size=1, deadband='1' {QDAC}
C1068_QDAC12: host=opsmya0, active=1, request=1, type=6, size=1, deadband='1' {QDAC}
C1068_QDAC13: host=opsmya0, active=1, request=1, type=6, size=1, deadband='1' {QDAC}
C1068_QDAC14: host=opsmya0, active=1, request=1, type=6, size=1, deadband='1' {QDAC}
C1068_QDAC01: host=opsmya0, active=1, request=1, type=6, size=1, deadband='1' {QDAC}
#IGLdac3:ao_5 not archived
#IGLdac3:ao_6 not archived
#IGLdac3:ao_0 not archived
#IGLdac3:ao_1 not archived
pgunFreqDiv:A:frequency: host=opsmya0, active=1, request=1, type=3, size=1 {laser}
pgunFreqDiv:C:frequency: host=opsmya0, active=1, request=1, type=3, size=1 {laser}
IGLdac2:G2Ch3Pos: host=opsmya11, active=1, request=1, type=6, size=1, deadband='0.01' {gunp}
IGLdac2:G2Ch4Neg: host=opsmya11, active=1, request=1, type=6, size=1, deadband='0.01' {gunp}
IGL1I00OD16_8: host=opsmya5, active=1, request=1, type=3, size=1 {IPOPTO MyRestore}
cdipc_xpos: host=opsmya0, active=1, request=1, type=6, size=1, deadband='0.001' {laser}
cdipc_ypos: host=opsmya0, active=1, request=1, type=6, size=1, deadband='0.001' {laser}
psub_cx_pos: host=opsmya0, active=1, request=1, type=6, size=1 {laser}
psub_cy_pos: host=opsmya0, active=1, request=1, type=6, size=1 {laser}
SMRPOSA: host=opsmya5, active=1, request=1, type=6, size=1 {chap}
HELCLOCKs: host=opsmya5, active=1, request=1, type=3, size=1 {helicityControl}
HELDELAYs: host=opsmya5, active=1, request=1, type=3, size=1 {helicityControl}
HELPATTERNs: host=opsmya5, active=1, request=1, type=3, size=1 {helicityControl}
HELCLOCKd: host=opsmya5, active=1, request=1, type=3, size=1 {helicityControl}
HELTSETTLEd: host=opsmya5, active=1, request=1, type=6, size=1 {helicityControl}
HELTSTABLEd: host=opsmya5, active=1, request=1, type=6, size=1 {helicityControl}
HELDELAYd: host=opsmya5, active=1, request=1, type=3, size=1 {helicityControl}
HELPATTERNd: host=opsmya5, active=1, request=1, type=3, size=1 {helicityControl}
HELFREQ: host=opsmya5, active=1, request=1, type=6, size=1 {helicityControl}
SMRPOSB: host=opsmya5, active=1, request=1, type=6, size=1 {chap}
SMRPOSC: host=opsmya5, active=1, request=1, type=6, size=1 {chap}
itov1out: host=opsmya5, active=1, request=1, type=6, size=1, deadband='0.001' {itov}
itov2out: host=opsmya5, active=1, request=1, type=6, size=1, deadband='0.001' {itov}
itov3out: host=opsmya5, active=1, request=1, type=6, size=1, deadband='0.001' {itov}
itov4out: host=opsmya5, active=1, request=1, type=6, size=1, deadband='0.001' {itov}
itov5out: host=opsmya5, active=1, request=1, type=6, size=1, deadband='0.001' {itov}
itov7out: host=opsmya5, active=1, request=1, type=6, size=1, deadband='0.001' {itov}
IFY1I07I not archived
IFY1I07R not archived
IFY0I06I not archived
IFY0I06R not archived
IFY0L03I not archived
IFY0L03R not archived
laser_a_wavelength not archived
laser_b_wavelength not archived
laser_c_wavelength not archived
hac_bcm_average: host=opsmya5, active=1, request=1, type=6, size=1, deadband='0.001' {Hac_BCM}
IBC1H04CRCUR2: host=opsmya8, active=1, request=1, type=6, size=1 {bcmVme}
scaler_calc1: host=opsmya5, active=1, request=1, type=6, size=1, deadband='0.01' {hallb HB_beamline_scalers}
IPM2C24A.IENG: host=opsmya2, active=1, request=1, type=6, size=1, deadband='0.001' {1nABPMS}
IBC3H00CRCUR4: host=opsmya8, active=1, request=1, type=6, size=1 {bcmVme}
R00PGSET: host=opsmya5, active=1, request=1, type=6, size=1 {rf_injmisc MyRestore}
IGL1I00AI27: host=opsmya5, active=1, request=1, type=6, size=1, deadband='0.01' {Xy566}
IGL1I00AI17: host=opsmya5, active=1, request=1, type=6, size=1, deadband='0.01' {Xy566}
WienAngle: host=opsmya5, active=1, request=1, type=6, size=1 {IGLdac}
EHCFR_LIPRC not archived
IGL1I00DAC3: host=opsmya5, active=1, request=1, type=6, size=1, deadband='0.001' {IGLdac}
IGL1I00AI24: host=opsmya5, active=1, request=1, type=6, size=1, deadband='0.01' {Xy566}
hallb_transmission: host=opsmya11, active=1, request=1, type=6, size=1 {gunp}
IGL1I00DAC2: host=opsmya5, active=1, request=1, type=6, size=1, deadband='0.001' {IGLdac}
psub_ab_pos: host=opsmya0, active=1, request=1, type=6, size=1 {laser}
hallc_photocurrent: host=opsmya11, active=1, request=1, type=6, size=1 {gunp}
ISL0I04DT not archived
IGL1I00AI25: host=opsmya5, active=1, request=1, type=6, size=1, deadband='0.01' {Xy566}
IGL1I00AI8: host=opsmya5, active=1, request=1, type=6, size=1, deadband='0.01' {Xy566}
qe_halla: host=opsmya11, active=1, request=1, type=6, size=1 {gunp}
IGL1I00AI23: host=opsmya5, active=1, request=1, type=6, size=1, deadband='0.01' {Xy566}
IGL1I00AI22: host=opsmya5, active=1, request=1, type=6, size=1, deadband='0.01' {Xy566}
qe_hallb: host=opsmya11, active=1, request=1, type=6, size=1 {gunp}
IGL1I00AI26: host=opsmya5, active=1, request=1, type=6, size=1, deadband='0.01' {Xy566}
psub_ac_pos: host=opsmya0, active=1, request=1, type=6, size=1 {laser}
IGL1I00AI7: host=opsmya5, active=1, request=1, type=6, size=1, deadband='0.01' {Xy566}
qe_hallc: host=opsmya11, active=1, request=1, type=6, size=1 {gunp}
halla_photocurrent: host=opsmya11, active=1, request=1, type=6, size=1 {gunp}
IGL1I00PStrans: host=opsmya5, active=1, request=1, type=6, size=1, deadband='0.001' {psMMeter}
halla_transmission: host=opsmya11, active=1, request=1, type=6, size=1 {gunp}
ibcm1: host=opsmya5, active=1, request=1, type=6, size=1, deadband='0.01' {hallc}
ibcm2: host=opsmya5, active=1, request=1, type=6, size=1, deadband='0.01' {hallc}
ibcm17: host=opsmya2, active=1, request=1, type=6, size=1, deadband='0.01' {HallC_bcm}
iunser: host=opsmya2, active=1, request=1, type=6, size=1, deadband='0.01' {HallC_bcm}
ibcm4a not archived
ibcm4b not archived
#HC:bcm_select not archived
EHCFR_LIXWidth: host=opsmya5, active=1, request=1, type=6, size=1 {raster}
EHCFR_LIYWidth: host=opsmya5, active=1, request=1, type=6, size=1 {raster}
EHCFR_ENERGY not archived
HALLC:p: host=opsmya5, active=1, request=1, type=6, size=1 {bem}
HALLA:p: host=opsmya5, active=1, request=1, type=6, size=1 {bem}
EHCFR_INITENERGY: host=opsmya5, active=1, request=1, type=6, size=1 {raster}
EHCFR_A_IXPEAK: host=opsmya12, active=1, request=1, type=6, size=1 {raster}
EHCFR_B_IXPEAK: host=opsmya12, active=1, request=1, type=6, size=1 {raster}
EHCFR_A_IYPEAK: host=opsmya12, active=1, request=1, type=6, size=1 {raster}
EHCFR_B_IYPEAK: host=opsmya12, active=1, request=1, type=6, size=1 {raster}
HCCO:HMS:POSRB: host=opsmya0, active=1, request=1, type=6, size=1, deadband='100' {hallc}
HCCO:SHMS:POSRB: host=opsmya0, active=1, request=1, type=6, size=1, deadband='100' {hallc}
IPM3C00.XPOS: host=opsmya3, active=1, request=1, type=2, size=1, deadband='0.005' {bpm}
IPM3C00.YPOS: host=opsmya3, active=1, request=1, type=2, size=1, deadband='0.005' {bpm}
IPM3C01.XPOS: host=opsmya3, active=1, request=1, type=2, size=1, deadband='0.005' {bpm}
IPM3C01.YPOS: host=opsmya3, active=1, request=1, type=2, size=1, deadband='0.005' {bpm}
IPM3C02.XPOS: host=opsmya3, active=1, request=1, type=2, size=1, deadband='0.005' {bpm}
IPM3C02.YPOS: host=opsmya3, active=1, request=1, type=2, size=1, deadband='0.005' {bpm}
IPM3C03.XPOS: host=opsmya3, active=1, request=1, type=2, size=1, deadband='0.005' {bpm}
IPM3C03.YPOS: host=opsmya3, active=1, request=1, type=2, size=1, deadband='0.005' {bpm}
IPM3C04.XPOS: host=opsmya3, active=1, request=1, type=2, size=1, deadband='0.005' {bpm}
IPM3C04.YPOS: host=opsmya3, active=1, request=1, type=2, size=1, deadband='0.005' {bpm}
IPM3C05.XPOS: host=opsmya3, active=1, request=1, type=2, size=1, deadband='0.005' {bpm}
IPM3C05.YPOS: host=opsmya3, active=1, request=1, type=2, size=1, deadband='0.005' {bpm}
IPM3C06.XPOS: host=opsmya3, active=1, request=1, type=2, size=1, deadband='0.005' {bpm}
IPM3C06.YPOS: host=opsmya3, active=1, request=1, type=2, size=1, deadband='0.005' {bpm}
IPM3C07.XPOS: host=opsmya3, active=1, request=1, type=2, size=1, deadband='0.005' {bpm}
IPM3C07.YPOS: host=opsmya3, active=1, request=1, type=2, size=1, deadband='0.005' {bpm}
IPM3C07A.XPOS: host=opsmya3, active=1, request=1, type=2, size=1, deadband='0.005' {bpm}
IPM3C07A.YPOS: host=opsmya3, active=1, request=1, type=2, size=1, deadband='0.005' {bpm}
IPM3C08.XPOS: host=opsmya3, active=1, request=1, type=2, size=1, deadband='0.005' {bpm}
IPM3C08.YPOS: host=opsmya3, active=1, request=1, type=2, size=1, deadband='0.005' {bpm}
IPM3C10.XPOS: host=opsmya3, active=1, request=1, type=2, size=1, deadband='0.005' {bpm}
IPM3C10.YPOS: host=opsmya3, active=1, request=1, type=2, size=1, deadband='0.005' {bpm}
IPM3C11.XPOS: host=opsmya3, active=1, request=1, type=2, size=1, deadband='0.005' {bpm}
IPM3C11.YPOS: host=opsmya3, active=1, request=1, type=2, size=1, deadband='0.005' {bpm}
IPM3C12.XPOS: host=opsmya3, active=1, request=1, type=2, size=1, deadband='0.005' {bpm}
IPM3C12.YPOS: host=opsmya3, active=1, request=1, type=2, size=1, deadband='0.005' {bpm}
IPM3C14.XPOS: host=opsmya3, active=1, request=1, type=2, size=1, deadband='0.005' {bpm}
IPM3C14.YPOS: host=opsmya3, active=1, request=1, type=2, size=1, deadband='0.005' {bpm}
IPM3C16.XPOS: host=opsmya3, active=1, request=1, type=2, size=1, deadband='0.005' {bpm}
IPM3C16.YPOS: host=opsmya3, active=1, request=1, type=2, size=1, deadband='0.005' {bpm}
IPM3C17.XPOS: host=opsmya3, active=1, request=1, type=2, size=1, deadband='0.005' {bpm}
IPM3C17.YPOS: host=opsmya3, active=1, request=1, type=2, size=1, deadband='0.005' {bpm}
IPM3C18.XPOS: host=opsmya3, active=1, request=1, type=2, size=1, deadband='0.005' {bpm}
IPM3C18.YPOS: host=opsmya3, active=1, request=1, type=2, size=1, deadband='0.005' {bpm}
IPM3C19.XPOS: host=opsmya3, active=1, request=1, type=2, size=1, deadband='0.005' {bpm}
IPM3C19.YPOS: host=opsmya3, active=1, request=1, type=2, size=1, deadband='0.005' {bpm}
IPM3P01.XPOS not archived
IPM3P01.YPOS not archived
IPM3P02A.XPOS: host=opsmya3, active=1, request=1, type=2, size=1, deadband='0.005' {bpm}
IPM3P02A.YPOS: host=opsmya3, active=1, request=1, type=2, size=1, deadband='0.005' {bpm}
IPM3P02B.XPOS: host=opsmya3, active=1, request=1, type=2, size=1, deadband='0.005' {bpm}
IPM3P02B.YPOS: host=opsmya3, active=1, request=1, type=2, size=1, deadband='0.005' {bpm}
IPM3P03.XPOS not archived
IPM3P03.YPOS not archived
IPM3C20.XPOS: host=opsmya1, active=1, request=1, type=2, size=1, deadband='0.005' {bpm}
IPM3C20.YPOS: host=opsmya1, active=1, request=1, type=2, size=1, deadband='0.005' {bpm}
IPM3C21.XPOS: host=opsmya3, active=1, request=1, type=2, size=1, deadband='0.005' {bpm}
IPM3C21.YPOS: host=opsmya3, active=1, request=1, type=2, size=1, deadband='0.005' {bpm}
IPM3H02.XPOS: host=opsmya3, active=1, request=1, type=2, size=1, deadband='0.005' {bpm}
IPM3H02.YPOS: host=opsmya3, active=1, request=1, type=2, size=1, deadband='0.005' {bpm}
IPM3H04.XPOS: host=opsmya3, active=1, request=1, type=2, size=1, deadband='0.005' {bpm}
IPM3H04.YPOS: host=opsmya3, active=1, request=1, type=2, size=1, deadband='0.005' {bpm}
IPM3H07A.XPOS: host=opsmya3, active=1, request=1, type=2, size=1, deadband='0.005' {bpm}
IPM3H07A.YPOS: host=opsmya3, active=1, request=1, type=2, size=1, deadband='0.005' {bpm}
IPM3H07B.XPOS: host=opsmya3, active=1, request=1, type=2, size=1, deadband='0.005' {bpm}
IPM3H07B.YPOS: host=opsmya3, active=1, request=1, type=2, size=1, deadband='0.005' {bpm}
IPM3H07C.XPOS: host=opsmya3, active=1, request=1, type=2, size=1, deadband='0.005' {bpm}
IPM3H07C.YPOS: host=opsmya3, active=1, request=1, type=2, size=1, deadband='0.005' {bpm}
IPM3H07A.FSUM not archived
IPM3H07A.TSUM not archived
IPM3H07B.FSUM not archived
IPM3H07B.TSUM not archived
IPM3H07C.FSUM not archived
IPM3H07C.TSUM not archived
IPM3H07A.SSUM not archived
IPM3H07A.RSUM not archived
IPM3H07B.SSUM not archived
IPM3H07B.RSUM not archived
IPM3H07C.SSUM not archived
IPM3H07C.RSUM not archived
IPM3H08.FSUM: host=opsmyasb0, active=1, request=1, type=6, size=1, deadband='1', clip=604800; {cjs.2018-05-01}
IPM3H08.TSUM: host=opsmyasb0, active=1, request=1, type=6, size=1, deadband='1', clip=604800; {cjs.2018-05-01}
IPM3H09.FSUM: host=opsmyasb0, active=1, request=1, type=6, size=1, deadband='1', clip=604800; {cjs.2018-05-01}
IPM3H09.TSUM: host=opsmyasb0, active=1, request=1, type=6, size=1, deadband='1', clip=604800; {cjs.2018-05-01}
IPM3H08.SSUM: host=opsmyasb0, active=1, request=1, type=6, size=1, deadband='1', clip=604800; {cjs.2018-05-01}
IPM3H08.RSUM: host=opsmyasb0, active=1, request=1, type=6, size=1, deadband='1', clip=604800; {cjs.2018-05-01}
IPM3H09.SSUM: host=opsmyasb0, active=1, request=1, type=6, size=1, deadband='1', clip=604800; {cjs.2018-05-01}
IPM3H09.RSUM: host=opsmyasb0, active=1, request=1, type=6, size=1, deadband='1', clip=604800; {cjs.2018-05-01}
IPM3H08.XROT: host=opsmyasb0, active=1, request=1, type=2, size=1, deadband='0.05', clip=604800; {cjs.2018-05-03}
IPM3H08.YROT: host=opsmyasb0, active=1, request=1, type=2, size=1, deadband='0.05', clip=604800; {cjs.2018-05-03}
IPM3H09.XROT: host=opsmyasb0, active=1, request=1, type=2, size=1, deadband='0.05', clip=604800; {cjs.2018-05-03}
IPM3H09.YROT: host=opsmyasb0, active=1, request=1, type=2, size=1, deadband='0.05', clip=604800; {cjs.2018-05-03}
IPM3H08.XPOS: host=opsmya3, active=1, request=1, type=2, size=1, deadband='0.005' {bpm}
IPM3H08.YPOS: host=opsmya3, active=1, request=1, type=2, size=1, deadband='0.005' {bpm}
IPM3H09.XPOS: host=opsmya3, active=1, request=1, type=2, size=1, deadband='0.005' {bpm}
IPM3H09.YPOS: host=opsmya3, active=1, request=1, type=2, size=1, deadband='0.005' {bpm}
IPM3C17.XIFG not archived
IPM3C17.YIFG not archived
IPM3C18.XIFG not archived
IPM3C18.YIFG not archived
IPM3C19.XIFG not archived
IPM3C19.YIFG not archived
IPM3P02A.XIFG not archived
IPM3P02A.YIFG not archived
IPM3P03.XIFG not archived
IPM3P03.YIFG not archived
IPM3P02B.XIFG not archived
IPM3P02B.YIFG not archived
IPM3C20.XIFG not archived
IPM3C20.YIFG not archived
IPM3C21.XIFG not archived
IPM3C21.YIFG not archived
IPM3H02.XIFG not archived
IPM3H02.YIFG not archived
IPM3H04.XIFG not archived
IPM3H04.YIFG not archived
IPM3H07A.XIFG not archived
IPM3H07A.YIFG not archived
IPM3H07B.XIFG not archived
IPM3H07B.YIFG not archived
IPM3H07C.XIFG not archived
IPM3H07C.YIFG not archived
IPM3H09.XIFG not archived
IPM3H09.YIFG not archived
#IPM3H09B.XIFG not archived
#IPM3H09B.YIFG not archived
IPM3C17.XSOF: host=opsmya7, active=1, request=1, type=2, size=1 {bpm MyRestore}
IPM3C17.YSOF: host=opsmya7, active=1, request=1, type=2, size=1 {bpm MyRestore}
IPM3C18.XSOF: host=opsmya7, active=1, request=1, type=2, size=1 {bpm MyRestore}
IPM3C18.YSOF: host=opsmya7, active=1, request=1, type=2, size=1 {bpm MyRestore}
IPM3C19.XSOF: host=opsmya7, active=1, request=1, type=2, size=1 {bpm MyRestore}
IPM3C19.YSOF: host=opsmya7, active=1, request=1, type=2, size=1 {bpm MyRestore}
IPM3P02A.XSOF: host=opsmya3, active=1, request=1, type=2, size=1 {bpm MyRestore}
IPM3P02A.YSOF: host=opsmya3, active=1, request=1, type=2, size=1 {bpm MyRestore}
IPM3P03.XSOF not archived
IPM3P03.YSOF not archived
IPM3P02B.XSOF: host=opsmya3, active=1, request=1, type=2, size=1 {bpm MyRestore}
IPM3P02B.YSOF: host=opsmya3, active=1, request=1, type=2, size=1 {bpm MyRestore}
IPM3C20.XSOF: host=opsmya3, active=1, request=1, type=2, size=1 {bpm MyRestore}
IPM3C20.YSOF: host=opsmya3, active=1, request=1, type=2, size=1 {bpm MyRestore}
IPM3C21.XSOF: host=opsmya3, active=1, request=1, type=2, size=1 {bpm MyRestore}
IPM3C21.YSOF: host=opsmya3, active=1, request=1, type=2, size=1 {bpm MyRestore}
IPM3H02.XSOF: host=opsmya3, active=1, request=1, type=2, size=1 {bpm MyRestore}
IPM3H02.YSOF: host=opsmya3, active=1, request=1, type=2, size=1 {bpm MyRestore}
IPM3H04.XSOF: host=opsmya3, active=1, request=1, type=2, size=1 {bpm MyRestore}
IPM3H04.YSOF: host=opsmya3, active=1, request=1, type=2, size=1 {bpm MyRestore}
IPM3H07A.XSOF: host=opsmya3, active=1, request=1, type=2, size=1 {bpm MyRestore}
IPM3H07A.YSOF: host=opsmya3, active=1, request=1, type=2, size=1 {bpm MyRestore}
IPM3H07B.XSOF: host=opsmya3, active=1, request=1, type=2, size=1 {bpm MyRestore}
IPM3H07B.YSOF: host=opsmya3, active=1, request=1, type=2, size=1 {bpm MyRestore}
IPM3H07C.XSOF: host=opsmya3, active=1, request=1, type=2, size=1 {bpm MyRestore}
IPM3H07C.YSOF: host=opsmya3, active=1, request=1, type=2, size=1 {bpm MyRestore}
IPM3H09.XSOF: host=opsmya3, active=1, request=1, type=2, size=1 {bpm MyRestore}
IPM3H09.YSOF: host=opsmya3, active=1, request=1, type=2, size=1 {bpm MyRestore}
IPM3H08.XSOF: host=opsmya3, active=1, request=1, type=2, size=1 {bpm MyRestore}
IPM3H08.YSOF: host=opsmya3, active=1, request=1, type=2, size=1 {bpm MyRestore}
IPM3H07A.XPOF: host=opsmya3, active=1, request=1, type=2, size=1 {bpm MyRestore}
IPM3H07A.YPOF: host=opsmya3, active=1, request=1, type=2, size=1 {bpm MyRestore}
IPM3H07B.XPOF: host=opsmya3, active=1, request=1, type=2, size=1 {bpm MyRestore}
IPM3H07B.YPOF: host=opsmya3, active=1, request=1, type=2, size=1 {bpm MyRestore}
IPM3H07C.XPOF: host=opsmya3, active=1, request=1, type=2, size=1 {bpm MyRestore}
IPM3H07C.YPOF: host=opsmya3, active=1, request=1, type=2, size=1 {bpm MyRestore}
IPM3H08.XPOF: host=opsmya3, active=1, request=1, type=2, size=1 {bpm MyRestore}
IPM3H08.YPOF: host=opsmya3, active=1, request=1, type=2, size=1 {bpm MyRestore}
IPM3H09.XPOF: host=opsmya3, active=1, request=1, type=2, size=1 {bpm MyRestore}
IPM3H09.YPOF: host=opsmya3, active=1, request=1, type=2, size=1 {bpm MyRestore}
IPM3H07A.XRAW: host=opsmya3, active=1, request=1, type=2, size=1 {bpm}
IPM3H07A.YRAW: host=opsmya3, active=1, request=1, type=2, size=1 {bpm}
IPM3H07B.XRAW: host=opsmya3, active=1, request=1, type=2, size=1 {bpm}
IPM3H07B.YRAW: host=opsmya3, active=1, request=1, type=2, size=1 {bpm}
IPM3H07C.XRAW: host=opsmya3, active=1, request=1, type=2, size=1 {bpm}
IPM3H07C.YRAW: host=opsmya3, active=1, request=1, type=2, size=1 {bpm}
IPM3H08.XRAW not archived
IPM3H08.YRAW not archived
IPM3H09.XRAW: host=opsmya3, active=1, request=1, type=2, size=1 {bpm}
IPM3H09.YRAW: host=opsmya3, active=1, request=1, type=2, size=1 {bpm}
FB_A:FB_On: host=opsmya5, active=1, request=1, type=3, size=1 {fastfb}
FB_C:FB_On: host=opsmya5, active=1, request=1, type=3, size=1 {fastfb}
FB_C:status:mbbi2.B7: host=opsmya5, active=1, request=1, type=4, size=1 {fastfb}
FB_C:use_RF: host=opsmya5, active=1, request=1, type=3, size=1 {fastfb MyRestore}
FB_A:use_RF: host=opsmya10, active=1, request=1, type=3, size=1 {fastfb MyRestore}
FB_A:status:mbbi2.B7: host=opsmya5, active=1, request=1, type=4, size=1 {fastfb}
OXSS_RDF: host=opsmya5, active=1, request=1, type=6, size=1, deadband='0.01' {hallc}
OXSS_MGFD: host=opsmya5, active=1, request=1, type=6, size=1, deadband='0.01', clip=1209600; {hallc}
TARGPOS: host=opsmya12, active=1, request=1, type=6, size=1 {hallc}
COLPOS1: host=opsmya12, active=1, request=1, type=6, size=1 {hallc}
COLPOS2: host=opsmya12, active=1, request=1, type=6, size=1 {hallc}
COLPOS3: host=opsmya12, active=1, request=1, type=6, size=1 {hallc}
COLPOS4: host=opsmya12, active=1, request=1, type=6, size=1 {hallc}
COLPOS5: host=opsmya12, active=1, request=1, type=6, size=1 {hallc}
COLPOS6: host=opsmya12, active=1, request=1, type=6, size=1 {hallc}
COLPOS7: host=opsmya12, active=1, request=1, type=6, size=1 {hallc}
FB_C:CORR:C1_value.B: host=opsmya5, active=1, request=1, type=6, size=1 {fastfb}
FB_C:CORR:C2_value.B: host=opsmya5, active=1, request=1, type=6, size=1 {fastfb}
FB_C:CORR:C3_value.B: host=opsmya5, active=1, request=1, type=6, size=1 {fastfb}
FB_C:CORR:C4_value.B: host=opsmya5, active=1, request=1, type=6, size=1 {fastfb}
IOCSE14:SEEGainMod;r not archived
IOCSE14:SEEProcMod;r: host=opsmya5, active=1, request=1, type=3, size=1 {fastfb}
IOCSE14:PassSel;r not archived
IOCSE17:SEEGainMod;r not archived
IOCSE17:SEEProcMod;r not archived
IOCSE17:PassSel;r not archived
IOCSE18:SEEGainMod;r not archived
IOCSE18:SEEProcMod;r not archived
IOCSE18:PassSel;r not archived
IOCSE20:SEEGainMod;r not archived
IOCSE20:SEEProcMod;r not archived
IOCSE20:PassSel;r not archived
IHA3H07AIR: host=opsmya0, active=1, request=1, type=6, size=1 {hallc_g0}
IHA3H07BIR: host=opsmya0, active=1, request=1, type=6, size=1 {hallc_g0}
IGL1I00DIOHWTB.B2: host=opsmya5, active=1, request=1, type=4, size=1 {IPOPTO}
IGL1I00DIOFLRD not archived
hel_even_1: host=opsmya2, active=1, request=1, type=6, size=1, deadband='1' {HelicityMagnets}
hel_odd_1: host=opsmya2, active=1, request=1, type=6, size=1, deadband='1' {HelicityMagnets}
hel_even_2: host=opsmya2, active=1, request=1, type=6, size=1, deadband='1' {HelicityMagnets}
hel_odd_2: host=opsmya2, active=1, request=1, type=6, size=1, deadband='1' {HelicityMagnets}
hel_even_3: host=opsmya2, active=1, request=1, type=6, size=1, deadband='1' {HelicityMagnets}
hel_odd_3: host=opsmya2, active=1, request=1, type=6, size=1, deadband='1' {HelicityMagnets}
hel_even_4: host=opsmya2, active=1, request=1, type=6, size=1, deadband='1' {HelicityMagnets}
hel_odd_4: host=opsmya2, active=1, request=1, type=6, size=1, deadband='1' {HelicityMagnets}
hel_mag_status.D: host=opsmya2, active=1, request=1, type=6, size=1, deadband='1' {HelicityMagnets}
hcBDSSELECT not archived
hcL1_Fan_Freq_R: host=opsmya3, active=1, request=1, type=6, size=1, deadband='.1' {HallC_Cryotarget}
hcL2_Fan_Freq_R: host=opsmya3, active=1, request=1, type=6, size=1, deadband='.1' {HallC_Cryotarget}
hcL3_Fan_Freq_R: host=opsmya3, active=1, request=1, type=6, size=1, deadband='.1' {HallC_Cryotarget}
hcBDSPOS: host=opsmya3, active=1, request=1, type=6, size=1, deadband='1' {HallC_Cryotarget}
hcBDSPOS: host=opsmya3, active=1, request=1, type=6, size=1, deadband='1' {HallC_Cryotarget}
hcLS218_1_T5: host=opsmya3, active=1, request=1, type=6, size=1, deadband='0.02' {HallC_Cryotarget}
hcLS218_1_T6: host=opsmya3, active=1, request=1, type=6, size=1, deadband='0.02' {HallC_Cryotarget}
hcLS218_1_T7: host=opsmya3, active=1, request=1, type=6, size=1, deadband='0.02' {HallC_Cryotarget}
hcL1_TI_HX_In_R not archived
hcLS218_2_T5: host=opsmya3, active=1, request=1, type=6, size=1, deadband='0.02' {HallC_Cryotarget}
hcLS218_2_T6: host=opsmya3, active=1, request=1, type=6, size=1, deadband='0.02' {HallC_Cryotarget}
hcLS218_2_T7: host=opsmya3, active=1, request=1, type=6, size=1, deadband='0.02' {HallC_Cryotarget}
hcL2_TI_HX_In_R not archived
hcLS218_3_T5: host=opsmya3, active=1, request=1, type=6, size=1, deadband='0.02' {HallC_Cryotarget}
hcLS218_3_T6: host=opsmya3, active=1, request=1, type=6, size=1, deadband='0.02' {HallC_Cryotarget}
hcLS218_3_T7: host=opsmya3, active=1, request=1, type=6, size=1, deadband='0.02' {HallC_Cryotarget}
hcL3_TI_HX_In_R not archived
hcH2_P_Fill_Target_R: host=opsmya3, active=1, request=1, type=6, size=1, deadband='.1' {HallC_Cryotarget}
hcH2_P_Exhaust_R: host=opsmya3, active=1, request=1, type=6, size=1, deadband='.1' {HallC_Cryotarget}
hcD2_P_Fill_Target_R: host=opsmya3, active=1, request=1, type=6, size=1, deadband='.1' {HallC_Cryotarget}
hcD2_P_Exhaust_R: host=opsmya3, active=1, request=1, type=6, size=1, deadband='.1' {HallC_Cryotarget}
hcL1_hp_power_R: host=opsmya3, active=1, request=1, type=6, size=1, deadband='.1' {HallC_Cryotarget}
hcL2_hp_power_R: host=opsmya3, active=1, request=1, type=6, size=1, deadband='.1' {HallC_Cryotarget}
hcL3_hp_power_R: host=opsmya3, active=1, request=1, type=6, size=1, deadband='.1' {HallC_Cryotarget}
hcScatt_Chamber_Vac_R: host=opsmya3, active=1, request=1, type=6, size=1 {HallC_Cryotarget}
SHMS_Momentum not archived
ecSHMS_Angle: host=opsmya5, active=1, request=1, type=6, size=1, deadband='0.01' {hallc}
ecSP_SHMS not archived
ecSHB_Set_Current not archived
ecSQ1_Set_Current not archived
ecSQ2_Set_Current not archived
ecSQ3_Set_Current not archived
ecSDI_Set_Current not archived
ecSHB_I_coarse: host=opsmya12, active=1, request=1, type=6, size=1 {hallc}
ecSQ1_I_coarse: host=opsmya12, active=1, request=1, type=6, size=1 {hallc}
ecSQ2_I_coarse: host=opsmya12, active=1, request=1, type=6, size=1 {hallc}
ecSQ3_I_coarse: host=opsmya12, active=1, request=1, type=6, size=1 {hallc}
ecSDI_I_coarse: host=opsmya12, active=1, request=1, type=6, size=1 {hallc}
ecSHB_I_True: host=opsmya6, active=1, request=1, type=6, size=1, deadband='1%' {Cryogenics}
ecSQ1_I_True: host=opsmya6, active=1, request=1, type=6, size=1, deadband='1%' {Cryogenics}
ecSQ2_I_True: host=opsmya6, active=1, request=1, type=6, size=1, deadband='1%' {Cryogenics}
ecSQ3_I_True: host=opsmya6, active=1, request=1, type=6, size=1, deadband='1%' {Cryogenics}
ecSDI_I_True: host=opsmya6, active=1, request=1, type=6, size=1, deadband='1%' {Cryogenics}
ecSHB_HallP not archived
ecSQ1_HallP not archived
ecSQ2_HallP not archived
ecSQ3_HallP not archived
ecSHB_HP not archived
ecSQ1_HP not archived
ecSQ2_HP not archived
ecSQ3_HP not archived
ecSDI_HP not archived
ecSDI_B_Set_NMR not archived
ecSDI_B_True_NMR not archived
HMS_Momentum not archived
ecHMS_Angle: host=opsmya5, active=1, request=1, type=6, size=1, deadband='0.01' {hallc}
ecP_HMS not archived
ecQ1_Set_Current not archived
ecQ2_Set_Current not archived
ecQ3_Set_Current not archived
ecDI_Set_Current not archived
ecQ1_I_coarse: host=opsmya12, active=1, request=1, type=6, size=1 {hallc}
ecQ2_I_coarse: host=opsmya12, active=1, request=1, type=6, size=1 {hallc}
ecQ3_I_coarse: host=opsmya12, active=1, request=1, type=6, size=1 {hallc}
ecDI_I_coarse: host=opsmya12, active=1, request=1, type=6, size=1 {hallc}
ecQ1_I_True: host=opsmya6, active=1, request=1, type=6, size=1, deadband='1%' {Cryogenics}
ecQ2_I_True: host=opsmya6, active=1, request=1, type=6, size=1, deadband='1%' {Cryogenics}
ecQ3_I_True: host=opsmya6, active=1, request=1, type=6, size=1, deadband='1%' {Cryogenics}
ecSDI_I_True: host=opsmya6, active=1, request=1, type=6, size=1, deadband='1%' {Cryogenics}
ecDI_B_Set_NMR not archived
ecDI_B_True_NMR not archived
HCHMS_Q1_LS450:FLD_DATA: host=opsmya0, active=1, request=1, type=6, size=1, deadband='0.001' {HallC_HMS}
HCHMS_Q2_LS450:FLD_DATA: host=opsmya0, active=1, request=1, type=6, size=1, deadband='0.001' {HallC_HMS}
HCHMS_Q3_LS450:FLD_DATA: host=opsmya0, active=1, request=1, type=6, size=1, deadband='0.001' {HallC_HMS}
ecS_Shutter_status not archived
HMSPi:GasCherenkov:Temp: host=opsmya12, active=1, request=1, type=6, size=1, deadband='0.5' {hallc}
HMSPi:GasCherenkov:Pressure: host=opsmya12, active=1, request=1, type=6, size=1, deadband='0.2' {hallc}
MBSY3C: host=opsmya0, active=1, request=1, type=6, size=1 {magnets}
MBSY3CM: host=opsmya0, active=1, request=1, type=6, size=1, deadband='0.02' {magnets}
MBSY3C.BDL: host=opsmya0, active=1, request=1, type=6, size=1 {magnets MyRestore}
MBE3H05 not archived
MBE3H05M: host=opsmya0, active=1, request=1, type=6, size=1, deadband='0.02' {magnets}
MBE3H05.BDL: host=opsmya0, active=1, request=1, type=6, size=1 {magnets MyRestore}
MBE3H07 not archived
MBE3H07M: host=opsmya0, active=1, request=1, type=6, size=1, deadband='0.02' {magnets}
MBE3H07.BDL: host=opsmya0, active=1, request=1, type=6, size=1 {magnets MyRestore}
MQF3M01 not archived
MQF3M01M: host=opsmya0, active=1, request=1, type=6, size=1, deadband='0.02' {magnets}
MQF3M01.BDL: host=opsmya0, active=1, request=1, type=6, size=1 {magnets MyRestore}
MQE3M03 not archived
MQE3M03M: host=opsmya0, active=1, request=1, type=6, size=1, deadband='0.02' {magnets}
MQE3M03.BDL: host=opsmya0, active=1, request=1, type=6, size=1 {magnets MyRestore}
-------------- next part --------------
HallC_bcm: owner=mya, status=active
IBC3C17FLTRKr: host=opsmya10, active=0, request=1, type=6, size=1 {HallC_bcm}
IBC3C17MAGA: host=opsmya10, active=0, request=1, type=6, size=1 {HallC_bcm}
IBC3C17MAGB: host=opsmya10, active=0, request=1, type=6, size=1 {HallC_bcm}
IBC3C17MAGGNr: host=opsmya10, active=0, request=1, type=6, size=1 {HallC_bcm}
IBC3C17TEMP: host=opsmya10, active=0, request=1, type=6, size=1, deadband='0.1' {HallC_bcm}
IBC3C17VGAAr: host=opsmya10, active=0, request=1, type=6, size=1 {HallC_bcm}
IBC3C17VGABr: host=opsmya10, active=0, request=1, type=6, size=1 {HallC_bcm}
IBC3C17VGACr: host=opsmya10, active=0, request=1, type=6, size=1 {HallC_bcm}
IBC3C17VGADr: host=opsmya10, active=0, request=1, type=6, size=1 {HallC_bcm}
IBC3H04AFLTRKr: host=opsmya10, active=1, request=1, type=6, size=1 {HallC_bcm}
IBC3H04AMAGA: host=opsmya10, active=1, request=1, type=6, size=1 {HallC_bcm}
IBC3H04AMAGB: host=opsmya10, active=1, request=1, type=6, size=1 {HallC_bcm}
IBC3H04AMAGGNr: host=opsmya10, active=1, request=1, type=6, size=1 {HallC_bcm}
IBC3H04ATEMP: host=opsmya10, active=1, request=1, type=6, size=1, deadband='0.1' {HallC_bcm}
IBC3H04AVGAAr: host=opsmya10, active=1, request=1, type=6, size=1 {HallC_bcm}
IBC3H04AVGABr: host=opsmya10, active=1, request=1, type=6, size=1 {HallC_bcm}
IBC3H04AVGACr: host=opsmya10, active=1, request=1, type=6, size=1 {HallC_bcm}
IBC3H04AVGADr: host=opsmya10, active=1, request=1, type=6, size=1 {HallC_bcm}
IBC3H04BFLTRKr: host=opsmya10, active=1, request=1, type=6, size=1 {HallC_bcm}
IBC3H04BMAGA: host=opsmya10, active=1, request=1, type=6, size=1 {HallC_bcm}
IBC3H04BMAGB: host=opsmya10, active=1, request=1, type=6, size=1 {HallC_bcm}
IBC3H04BMAGGNr: host=opsmya10, active=1, request=1, type=6, size=1 {HallC_bcm}
IBC3H04BTEMP: host=opsmya10, active=1, request=1, type=6, size=1, deadband='0.1' {HallC_bcm}
IBC3H04BVGAAr: host=opsmya10, active=1, request=1, type=6, size=1 {HallC_bcm}
IBC3H04BVGABr: host=opsmya10, active=1, request=1, type=6, size=1 {HallC_bcm}
IBC3H04BVGACr: host=opsmya10, active=1, request=1, type=6, size=1 {HallC_bcm}
IBC3H04BVGADr: host=opsmya10, active=1, request=1, type=6, size=1 {HallC_bcm}
IBC3H04CFLTRKr: host=opsmya10, active=1, request=1, type=6, size=1 {HallC_bcm}
IBC3H04CMAGA: host=opsmya10, active=1, request=1, type=6, size=1 {HallC_bcm}
IBC3H04CMAGB: host=opsmya10, active=1, request=1, type=6, size=1 {HallC_bcm}
IBC3H04CMAGGNr: host=opsmya10, active=1, request=1, type=6, size=1 {HallC_bcm}
IBC3H04CTEMP: host=opsmya10, active=1, request=1, type=6, size=1, deadband='0.1' {HallC_bcm}
IBC3H04CVGAAr: host=opsmya10, active=1, request=1, type=6, size=1 {HallC_bcm}
IBC3H04CVGABr: host=opsmya10, active=1, request=1, type=6, size=1 {HallC_bcm}
IBC3H04CVGACr: host=opsmya10, active=1, request=1, type=6, size=1 {HallC_bcm}
IBC3H04CVGADr: host=opsmya10, active=1, request=1, type=6, size=1 {HallC_bcm}
IBC3H09FLTRKr: host=opsmya10, active=0, request=1, type=6, size=1 {HallC_bcm}
IBC3H09MAGA: host=opsmya10, active=1, request=1, type=6, size=1 {HallC_bcm}
IBC3H09MAGB: host=opsmya10, active=1, request=1, type=6, size=1 {HallC_bcm}
IBC3H09MAGGNr: host=opsmya10, active=0, request=1, type=6, size=1 {HallC_bcm}
IBC3H09TEMP: host=opsmya10, active=0, request=1, type=6, size=1, deadband='0.1' {HallC_bcm}
IBC3H09VGAAr: host=opsmya10, active=0, request=1, type=6, size=1 {HallC_bcm}
IBC3H09VGABr: host=opsmya10, active=0, request=1, type=6, size=1 {HallC_bcm}
IBC3H09VGACr: host=opsmya10, active=0, request=1, type=6, size=1 {HallC_bcm}
IBC3H09VGADr: host=opsmya10, active=0, request=1, type=6, size=1 {HallC_bcm}
ibcm17: host=opsmya10, active=1, request=1, type=6, size=1, deadband='0.01' {HallC_bcm}
iunser: host=opsmya10, active=1, request=1, type=6, size=1, deadband='0.01' {HallC_bcm}
47 members found
-------------- next part --------------
hallc: owner=mya, status=active
cComptCavityPower: host=opsmya5, active=0, request=1, type=6, size=1, deadband='10' {hallc}
cComptPhotonDetHV: host=opsmya5, active=0, request=1, type=6, size=1 {hallc}
cComptPhotonRate: host=opsmya5, active=0, request=1, type=6, size=1, deadband='10' {hallc}
cComptPhotonRateNorm: host=opsmya5, active=0, request=1, type=6, size=1, deadband='1' {hallc}
cComptScintRateNorm: host=opsmya5, active=0, request=1, type=6, size=1, deadband='0.5' {hallc}
COLPOS1: host=opsmya5, active=1, request=1, type=6, size=1 {hallc}
COLPOS2: host=opsmya5, active=1, request=1, type=6, size=1 {hallc}
COLPOS3: host=opsmya5, active=1, request=1, type=6, size=1 {hallc}
COLPOS4: host=opsmya5, active=1, request=1, type=6, size=1 {hallc}
COLPOS5: host=opsmya5, active=1, request=1, type=6, size=1 {hallc}
COLPOS6: host=opsmya5, active=1, request=1, type=6, size=1 {hallc}
COLPOS7: host=opsmya5, active=1, request=1, type=6, size=1 {hallc}
ecDI_I_coarse: host=opsmya5, active=1, request=1, type=6, size=1 {hallc}
ecHMS_Angle: host=opsmya5, active=1, request=1, type=6, size=1, deadband='0.01' {hallc}
ecQ1_I_coarse: host=opsmya5, active=1, request=1, type=6, size=1 {hallc}
ecQ2_I_coarse: host=opsmya5, active=1, request=1, type=6, size=1 {hallc}
ecQ3_I_coarse: host=opsmya5, active=1, request=1, type=6, size=1 {hallc}
ecSDI_I_coarse: host=opsmya5, active=1, request=1, type=6, size=1 {hallc}
ecSDI_Polarity: host=opsmya5, active=1, request=1, type=6, size=1 {hallc}
ecSHB_I_coarse: host=opsmya5, active=1, request=1, type=6, size=1 {hallc}
ecSHB_Polarity: host=opsmya5, active=1, request=1, type=6, size=1 {hallc}
ecSHMS_Angle: host=opsmya5, active=1, request=1, type=6, size=1, deadband='0.01' {hallc}
ecSQ1_I_coarse: host=opsmya5, active=1, request=1, type=6, size=1 {hallc}
ecSQ1_Polarity: host=opsmya5, active=1, request=1, type=6, size=1 {hallc}
ecSQ2_I_coarse: host=opsmya5, active=1, request=1, type=6, size=1 {hallc}
ecSQ2_Polarity: host=opsmya5, active=1, request=1, type=6, size=1 {hallc}
ecSQ3_I_coarse: host=opsmya5, active=1, request=1, type=6, size=1 {hallc}
ecSQ3_Polarity: host=opsmya5, active=1, request=1, type=6, size=1 {hallc}
EV91001_pos: host=opsmya5, active=1, request=1, type=6, size=1, deadband='0.3' {hallc}
EV91017_readback: host=opsmya5, active=1, request=1, type=6, size=1, deadband='0.3' {hallc}
EV91019_readback: host=opsmya5, active=1, request=1, type=6, size=1, deadband='0.3' {hallc}
FB_A:calibrate: host=opsmya5, active=1, request=1, type=3, size=1 {hallc}
FB_C:calibrate: host=opsmya5, active=1, request=1, type=3, size=1 {hallc}
HallCGasShed:AirHMS: host=opsmya5, active=1, request=1, type=3, size=1 {hallc}
HallCGasShed:BypassMonitor: host=opsmya5, active=1, request=1, type=3, size=1 {hallc}
HallCGasShed:GasHMS: host=opsmya5, active=1, request=1, type=3, size=1 {hallc}
HallCGasShed:GasSHMS: host=opsmya5, active=1, request=1, type=3, size=1 {hallc}
HallCGasShed:LowPSI: host=opsmya5, active=1, request=1, type=3, size=1 {hallc}
HallCGasShed:LowPSIBypass: host=opsmya5, active=1, request=1, type=3, size=1 {hallc}
HallCGasShed:Smoke: host=opsmya5, active=1, request=1, type=3, size=1 {hallc}
HallCGasShed:SolOpen: host=opsmya5, active=1, request=1, type=3, size=1 {hallc}
HCCEDPOS: host=opsmya5, active=1, request=1, type=6, size=1, deadband='.01' {hallc}
HCCO:HMS:POSRB: host=opsmya0, active=1, request=1, type=6, size=1, deadband='100' {hallc}
HCCO:SHMS:POSRB: host=opsmya0, active=1, request=1, type=6, size=1, deadband='100' {hallc}
hcHallC_beam_current: host=opsmya5, active=1, request=1, type=6, size=1, deadband='1%' {hallc}
HMSPi:GasCherenkov:Pressure: host=opsmya5, active=1, request=1, type=6, size=1, deadband='0.2' {hallc}
HMSPi:GasCherenkov:Temp: host=opsmya5, active=1, request=1, type=6, size=1, deadband='0.5' {hallc}
HMS_Angle: host=opsmya5, active=1, request=1, type=6, size=1 {hallc}
ibcm1: host=opsmya5, active=1, request=1, type=6, size=1, deadband='0.01' {hallc}
ibcm2: host=opsmya5, active=1, request=1, type=6, size=1, deadband='0.01' {hallc}
OXSS_MGFD: host=opsmya5, active=1, request=1, type=6, size=1, deadband='0.01', clip=1209600; {hallc}
OXSS_RDF: host=opsmya5, active=1, request=1, type=6, size=1, deadband='0.01' {hallc}
shmsshieldhut:MCP9808_2: host=opsmya5, active=1, request=1, type=6, size=1 {hallc}
shmsshowercounter:MCP9808_1: host=opsmya5, active=0, request=1, type=6, size=1 {hallc}
SHMS_Angle: host=opsmya5, active=1, request=1, type=6, size=1 {hallc}
TARGPOS: host=opsmya5, active=1, request=1, type=6, size=1 {hallc}
56 members found
-------------- next part --------------
HallC_Cryotarget: owner=mya, status=active
hcBDSPOS: host=opsmya3, active=1, request=1, type=6, size=1, deadband='1' {HallC_Cryotarget}
hcCryo_Return_P: host=opsmya3, active=1, request=1, type=6, size=1, deadband='2%' {HallC_Cryotarget}
hcCryo_Return_T: host=opsmya3, active=1, request=1, type=6, size=1, deadband='1%' {HallC_Cryotarget}
hcCryo_Supply_P: host=opsmya3, active=1, request=1, type=6, size=1, deadband='2%' {HallC_Cryotarget}
hcCryo_Supply_T: host=opsmya3, active=1, request=1, type=6, size=1, deadband='1%' {HallC_Cryotarget}
hcD2_Omega_DPG_R: host=opsmya3, active=1, request=1, type=6, size=1, deadband='.1' {HallC_Cryotarget}
hcD2_P_Ballast_R: host=opsmya3, active=1, request=1, type=6, size=1, deadband='.1' {HallC_Cryotarget}
hcD2_P_Exhaust_R: host=opsmya3, active=1, request=1, type=6, size=1, deadband='.1' {HallC_Cryotarget}
hcD2_P_Fill_Bottle_R: host=opsmya3, active=1, request=1, type=6, size=1, deadband='.1' {HallC_Cryotarget}
hcD2_P_Fill_Target_R: host=opsmya3, active=1, request=1, type=6, size=1, deadband='.1' {HallC_Cryotarget}
hcH2_Omega_DPG_R: host=opsmya3, active=1, request=1, type=6, size=1, deadband='.1' {HallC_Cryotarget}
hcH2_P_Ballast_R: host=opsmya3, active=1, request=1, type=6, size=1, deadband='.1' {HallC_Cryotarget}
hcH2_P_Exhaust_R: host=opsmya3, active=1, request=1, type=6, size=1, deadband='.1' {HallC_Cryotarget}
hcH2_P_Fill_Bottle_R: host=opsmya3, active=1, request=1, type=6, size=1, deadband='.1' {HallC_Cryotarget}
hcH2_P_Fill_Target_R: host=opsmya3, active=1, request=1, type=6, size=1, deadband='.1' {HallC_Cryotarget}
hcHallA_beam_current: host=opsmya3, active=0, request=1, type=6, size=1, deadband='0.1' {HallC_Cryotarget}
hcHe3_P_Comp_In_R: host=opsmya3, active=1, request=1, type=6, size=1, deadband='.1' {HallC_Cryotarget}
hcHe3_P_Comp_Out_R: host=opsmya3, active=1, request=1, type=6, size=1, deadband='.1' {HallC_Cryotarget}
hcHe3_P_Fill_Target_R: host=opsmya3, active=1, request=1, type=6, size=1, deadband='.1' {HallC_Cryotarget}
hcHe3_P_Tank_R: host=opsmya3, active=1, request=1, type=6, size=1, deadband='.1' {HallC_Cryotarget}
hcHe_Omega_DPG_R: host=opsmya3, active=1, request=1, type=6, size=1, deadband='.1' {HallC_Cryotarget}
hcHe_P_Purge_R: host=opsmya3, active=1, request=1, type=6, size=1, deadband='.1' {HallC_Cryotarget}
hcL1_Fan_current_R: host=opsmya3, active=1, request=1, type=6, size=1, deadband='.1' {HallC_Cryotarget}
hcL1_Fan_drive_hz_R: host=opsmya3, active=1, request=1, type=6, size=1, deadband='.1' {HallC_Cryotarget}
hcL1_Fan_Freq_R: host=opsmya3, active=1, request=1, type=6, size=1, deadband='.1' {HallC_Cryotarget}
hcL1_Fan_prcnthz_R: host=opsmya3, active=1, request=1, type=6, size=1, deadband='.1' {HallC_Cryotarget}
hcL1_Fan_prcnthz_W: host=opsmya3, active=1, request=1, type=6, size=1, deadband='.1' {HallC_Cryotarget}
hcL1_Fan_voltage_R: host=opsmya3, active=1, request=1, type=6, size=1, deadband='.1' {HallC_Cryotarget}
hcL1_HPH_I_CONV: host=opsmya3, active=1, request=1, type=6, size=1, deadband='.1' {HallC_Cryotarget}
hcL1_HPH_V_CONV: host=opsmya3, active=1, request=1, type=6, size=1, deadband='.1' {HallC_Cryotarget}
hcL1_hp_pid: host=opsmya3, active=1, request=1, type=2, size=1, deadband='.1' {HallC_Cryotarget}
hcL1_hp_pid.CVAL: host=opsmya3, active=1, request=1, type=2, size=1, deadband='.01' {HallC_Cryotarget}
hcL1_hp_pid.OVAL: host=opsmya3, active=1, request=1, type=2, size=1, deadband='.1' {HallC_Cryotarget}
hcL1_hp_power_R: host=opsmya3, active=1, request=1, type=6, size=1, deadband='.1' {HallC_Cryotarget}
hcL1_JTV_Rca: host=opsmya3, active=1, request=1, type=6, size=1, deadband='.1' {HallC_Cryotarget}
hcL1_pbeam: host=opsmya3, active=1, request=1, type=6, size=1, deadband='.1' {HallC_Cryotarget}
hcL1_Temperature: host=opsmya3, active=1, request=1, type=6, size=1, deadband='1%' {HallC_Cryotarget}
hcL1_TI_Cryo_In_R: host=opsmya3, active=1, request=1, type=6, size=1, deadband='1%' {HallC_Cryotarget}
hcL1_TI_Cryo_Out_R: host=opsmya3, active=1, request=1, type=6, size=1, deadband='1%' {HallC_Cryotarget}
hcL2_Fan_current_R: host=opsmya3, active=1, request=1, type=6, size=1, deadband='.1' {HallC_Cryotarget}
hcL2_Fan_drive_hz_R: host=opsmya3, active=1, request=1, type=6, size=1, deadband='.1' {HallC_Cryotarget}
hcL2_Fan_Freq_R: host=opsmya3, active=1, request=1, type=6, size=1, deadband='.1' {HallC_Cryotarget}
hcL2_Fan_prcnthz_R: host=opsmya3, active=1, request=1, type=6, size=1, deadband='.1' {HallC_Cryotarget}
hcL2_Fan_prcnthz_W: host=opsmya3, active=1, request=1, type=6, size=1, deadband='.1' {HallC_Cryotarget}
hcL2_Fan_voltage_R: host=opsmya3, active=1, request=1, type=6, size=1, deadband='.1' {HallC_Cryotarget}
hcL2_HPH_I_CONV: host=opsmya3, active=1, request=1, type=6, size=1, deadband='.1' {HallC_Cryotarget}
hcL2_HPH_V_CONV: host=opsmya3, active=1, request=1, type=6, size=1, deadband='.1' {HallC_Cryotarget}
hcL2_hp_pid: host=opsmya3, active=1, request=1, type=2, size=1, deadband='.1' {HallC_Cryotarget}
hcL2_hp_pid.CVAL: host=opsmya3, active=1, request=1, type=2, size=1, deadband='.01' {HallC_Cryotarget}
hcL2_hp_pid.OVAL: host=opsmya3, active=1, request=1, type=2, size=1, deadband='.1' {HallC_Cryotarget}
hcL2_hp_power_R: host=opsmya3, active=1, request=1, type=6, size=1, deadband='.1' {HallC_Cryotarget}
hcL2_JTV_Rca: host=opsmya3, active=1, request=1, type=6, size=1, deadband='.1' {HallC_Cryotarget}
hcL2_pbeam: host=opsmya3, active=1, request=1, type=6, size=1, deadband='.1' {HallC_Cryotarget}
hcL2_Temperature: host=opsmya3, active=1, request=1, type=6, size=1, deadband='1%' {HallC_Cryotarget}
hcL2_TI_Cryo_In_R: host=opsmya3, active=1, request=1, type=6, size=1, deadband='1%' {HallC_Cryotarget}
hcL2_TI_Cryo_Out_R: host=opsmya3, active=1, request=1, type=6, size=1, deadband='1%' {HallC_Cryotarget}
hcL3_Fan_current_R: host=opsmya3, active=1, request=1, type=6, size=1, deadband='10' {HallC_Cryotarget}
hcL3_Fan_Freq_R: host=opsmya3, active=1, request=1, type=6, size=1, deadband='.1' {HallC_Cryotarget}
hcL3_Fan_voltage_R: host=opsmya3, active=1, request=1, type=6, size=1, deadband='0.1' {HallC_Cryotarget}
hcL3_HPH_I_CONV: host=opsmya3, active=1, request=1, type=6, size=1, deadband='.1' {HallC_Cryotarget}
hcL3_HPH_V_CONV: host=opsmya3, active=1, request=1, type=6, size=1, deadband='.1' {HallC_Cryotarget}
hcL3_hp_pid: host=opsmya3, active=1, request=1, type=2, size=1, deadband='.1' {HallC_Cryotarget}
hcL3_hp_pid.CVAL: host=opsmya3, active=1, request=1, type=2, size=1, deadband='.01' {HallC_Cryotarget}
hcL3_hp_pid.OVAL: host=opsmya3, active=1, request=1, type=2, size=1, deadband='.1' {HallC_Cryotarget}
hcL3_hp_power_R: host=opsmya3, active=1, request=1, type=6, size=1, deadband='.1' {HallC_Cryotarget}
hcL3_JTV_Rca: host=opsmya3, active=1, request=1, type=6, size=1, deadband='.1' {HallC_Cryotarget}
hcL3_pbeam: host=opsmya3, active=1, request=1, type=6, size=1, deadband='.1' {HallC_Cryotarget}
hcL3_Temperature: host=opsmya3, active=1, request=1, type=6, size=1, deadband='1%' {HallC_Cryotarget}
hcL3_TI_Cryo_In_R: host=opsmya3, active=1, request=1, type=6, size=1, deadband='1%' {HallC_Cryotarget}
hcL3_TI_Cryo_Out_R: host=opsmya3, active=1, request=1, type=6, size=1, deadband='1%' {HallC_Cryotarget}
hcLS218_1_T1: host=opsmya3, active=1, request=1, type=6, size=1, deadband='0.02' {HallC_Cryotarget}
hcLS218_1_T2: host=opsmya3, active=1, request=1, type=6, size=1, deadband='0.02' {HallC_Cryotarget}
hcLS218_1_T3: host=opsmya3, active=1, request=1, type=6, size=1, deadband='0.02' {HallC_Cryotarget}
hcLS218_1_T5: host=opsmya3, active=1, request=1, type=6, size=1, deadband='0.02' {HallC_Cryotarget}
hcLS218_1_T6: host=opsmya3, active=1, request=1, type=6, size=1, deadband='0.02' {HallC_Cryotarget}
hcLS218_1_T7: host=opsmya3, active=1, request=1, type=6, size=1, deadband='0.02' {HallC_Cryotarget}
hcLS218_2_T1: host=opsmya3, active=1, request=1, type=6, size=1, deadband='0.02' {HallC_Cryotarget}
hcLS218_2_T2: host=opsmya3, active=1, request=1, type=6, size=1, deadband='0.02' {HallC_Cryotarget}
hcLS218_2_T3: host=opsmya3, active=1, request=1, type=6, size=1, deadband='0.02' {HallC_Cryotarget}
hcLS218_2_T5: host=opsmya3, active=1, request=1, type=6, size=1, deadband='0.02' {HallC_Cryotarget}
hcLS218_2_T6: host=opsmya3, active=1, request=1, type=6, size=1, deadband='0.02' {HallC_Cryotarget}
hcLS218_2_T7: host=opsmya3, active=1, request=1, type=6, size=1, deadband='0.02' {HallC_Cryotarget}
hcLS218_3_T1: host=opsmya3, active=1, request=1, type=6, size=1, deadband='0.02' {HallC_Cryotarget}
hcLS218_3_T2: host=opsmya3, active=1, request=1, type=6, size=1, deadband='0.02' {HallC_Cryotarget}
hcLS218_3_T3: host=opsmya3, active=1, request=1, type=6, size=1, deadband='0.02' {HallC_Cryotarget}
hcLS218_3_T5: host=opsmya3, active=1, request=1, type=6, size=1, deadband='0.02' {HallC_Cryotarget}
hcLS218_3_T6: host=opsmya3, active=1, request=1, type=6, size=1, deadband='0.02' {HallC_Cryotarget}
hcLS218_3_T7: host=opsmya3, active=1, request=1, type=6, size=1, deadband='0.02' {HallC_Cryotarget}
hcLS218_4_T1: host=opsmya3, active=1, request=1, type=6, size=1, deadband='0.02' {HallC_Cryotarget}
hcLS218_4_T2: host=opsmya3, active=1, request=1, type=6, size=1, deadband='0.02' {HallC_Cryotarget}
hcLS218_4_T3: host=opsmya3, active=1, request=1, type=6, size=1, deadband='0.02' {HallC_Cryotarget}
hcLS218_4_T4: host=opsmya3, active=1, request=1, type=6, size=1, deadband='0.02' {HallC_Cryotarget}
hcLS218_4_T5: host=opsmya3, active=1, request=1, type=6, size=1, deadband='0.02' {HallC_Cryotarget}
hcLS218_4_T6: host=opsmya3, active=1, request=1, type=6, size=1, deadband='0.02' {HallC_Cryotarget}
hcLS218_4_T7: host=opsmya3, active=1, request=1, type=6, size=1, deadband='0.02' {HallC_Cryotarget}
hcScatt_Chamber_Vac_R: host=opsmya3, active=1, request=1, type=6, size=1 {HallC_Cryotarget}
hcWR_EV_R: host=opsmya3, active=1, request=1, type=6, size=1, deadband='.1' {HallC_Cryotarget}
97 members found
-------------- next part --------------
hallc_g0: owner=mya, status=active
g0rate1: host=opsmya0, active=0, request=1, type=6, size=1 {hallc_g0}
g0rate10: host=opsmya0, active=0, request=1, type=6, size=1 {hallc_g0}
g0rate11: host=opsmya0, active=0, request=1, type=6, size=1 {hallc_g0}
g0rate12: host=opsmya0, active=0, request=1, type=6, size=1 {hallc_g0}
g0rate13: host=opsmya0, active=0, request=1, type=6, size=1 {hallc_g0}
g0rate14: host=opsmya0, active=0, request=1, type=6, size=1 {hallc_g0}
g0rate15: host=opsmya0, active=0, request=1, type=6, size=1 {hallc_g0}
g0rate16: host=opsmya0, active=0, request=1, type=6, size=1 {hallc_g0}
g0rate2: host=opsmya0, active=0, request=1, type=6, size=1 {hallc_g0}
g0rate3: host=opsmya0, active=0, request=1, type=6, size=1 {hallc_g0}
g0rate4: host=opsmya0, active=0, request=1, type=6, size=1 {hallc_g0}
g0rate5: host=opsmya0, active=0, request=1, type=6, size=1 {hallc_g0}
g0rate6: host=opsmya0, active=0, request=1, type=6, size=1 {hallc_g0}
g0rate7: host=opsmya0, active=0, request=1, type=6, size=1 {hallc_g0}
g0rate8: host=opsmya0, active=0, request=1, type=6, size=1 {hallc_g0}
g0rate9: host=opsmya0, active=0, request=1, type=6, size=1 {hallc_g0}
IHA3H07AIR: host=opsmya0, active=1, request=1, type=6, size=1 {hallc_g0}
IHA3H07BIR: host=opsmya0, active=1, request=1, type=6, size=1 {hallc_g0}
IHA3H09AIR: host=opsmya0, active=0, request=1, type=6, size=1 {hallc_g0}
IHA3H09BIR: host=opsmya0, active=1, request=1, type=6, size=1 {hallc_g0}
20 members found
-------------- next part --------------
HallC_HMS: owner=mya, status=active
ecDI_POLARITY: host=opsmya0, active=1, request=1, type=6, size=1, deadband='0.1' {HallC_HMS}
ecQ1_POLARITY: host=opsmya0, active=1, request=1, type=6, size=1, deadband='0.1' {HallC_HMS}
ecQ2_POLARITY: host=opsmya0, active=1, request=1, type=6, size=1, deadband='0.1' {HallC_HMS}
ecQ3_POLARITY: host=opsmya0, active=1, request=1, type=6, size=1, deadband='0.1' {HallC_HMS}
HCHMS_Q1_LS450:FLD_DATA: host=opsmya0, active=1, request=1, type=6, size=1, deadband='0.001' {HallC_HMS}
HCHMS_Q2_LS450:FLD_DATA: host=opsmya0, active=1, request=1, type=6, size=1, deadband='0.001' {HallC_HMS}
HCHMS_Q3_LS450:FLD_DATA: host=opsmya0, active=1, request=1, type=6, size=1, deadband='0.001' {HallC_HMS}
7 members found
-------------- next part --------------
HallComm: owner=mya, status=active
HallABANU: host=opsmya12, active=1, request=1, type=6, size=1 {HallComm bta}
HallBBANU: host=opsmya12, active=1, request=1, type=6, size=1 {HallComm bta}
HallCBANU: host=opsmya12, active=1, request=1, type=6, size=1 {HallComm bta}
3 members found
-------------- next part --------------
CRTrans1 not archived
CCT10N21: host=opsmya6, active=1, request=1, type=6, size=1, deadband='0.1' {Cryogenics}
CCT60DL: host=opsmya13, active=1, request=1, type=6, size=1, deadband='0.1' {Cryogenics}
CCT60HP: host=opsmya6, active=1, request=1, type=6, size=1, deadband='0.1' {Cryogenics}
CEV6711A.ORBV: host=opsmya13, active=1, request=1, type=2, size=1, deadband='0.4' {Cryogenics}
CEV6711C: host=opsmya6, active=1, request=1, type=2, size=1, deadband='0.01' {Cryogenics}
CEV6711C.ORBV: host=opsmya6, active=1, request=1, type=2, size=1, deadband='0.4' {Cryogenics}
CEV6721A.ORBV: host=opsmya6, active=1, request=1, type=2, size=1, deadband='0.4' {Cryogenics}
CEV6721C.ORBV: host=opsmya6, active=1, request=1, type=2, size=1, deadband='0.4' {Cryogenics}
CEV6761.ORBV: host=opsmya6, active=1, request=1, type=2, size=1, deadband='0.4' {Cryogenics}
CEV71D104.ORBV: host=opsmya6, active=0, request=1, type=2, size=1, deadband='0.4' {Cryogenics}
CEV71Q104.ORBV: host=opsmya6, active=0, request=1, type=2, size=1, deadband='0.4' {Cryogenics}
CEV71Q204.ORBV: host=opsmya6, active=0, request=1, type=2, size=1, deadband='0.4' {Cryogenics}
CEV71Q304.ORBV: host=opsmya6, active=0, request=1, type=2, size=1, deadband='0.01' {Cryogenics}
CEV72D104.ORBV: host=opsmya6, active=0, request=1, type=2, size=1, deadband='0.4' {Cryogenics}
CEV72Q104.ORBV: host=opsmya6, active=0, request=1, type=2, size=1, deadband='0.4' {Cryogenics}
CEV72Q204.ORBV: host=opsmya6, active=0, request=1, type=2, size=1, deadband='0.4' {Cryogenics}
CEV72Q304.ORBV: host=opsmya6, active=0, request=1, type=2, size=1, deadband='0.4' {Cryogenics}
CFI6010: host=opsmya7, active=1, request=1, type=6, size=1, deadband='0.01' {Cryogenics}
CFI6030: host=opsmya7, active=1, request=1, type=6, size=1, deadband='0.01' {Cryogenics}
CFI60DLP: host=opsmya4, active=1, request=1, type=6, size=1, deadband='0.01' {Cryogenics}
CFI6711A: host=opsmya7, active=1, request=1, type=6, size=1, deadband='0.01' {Cryogenics halla_cryo}
CFI6711B: host=opsmya6, active=1, request=1, type=6, size=1, deadband='0.1' {Cryogenics}
CFI6711C: host=opsmya7, active=1, request=1, type=6, size=1, deadband='0.01' {Cryogenics}
CFI6731A: host=opsmya7, active=1, request=1, type=6, size=1, deadband='0.01' {Cryogenics}
CFI6731C: host=opsmya7, active=1, request=1, type=6, size=1, deadband='0.01' {Cryogenics}
CFI6751C: host=opsmya7, active=1, request=1, type=6, size=1, deadband='0.5' {Cryogenics}
CLL671SC: host=opsmya7, active=1, request=1, type=6, size=1, deadband='0.1' {Cryogenics}
CLL675SC: host=opsmya7, active=1, request=1, type=6, size=1, deadband='0.1' {Cryogenics}
CPI6010: host=opsmya6, active=1, request=1, type=6, size=1, deadband='.05' {Cryogenics}
CPI6030: host=opsmya6, active=1, request=1, type=6, size=1, deadband='0.01' {Cryogenics}
CPI603QA: host=opsmya6, active=1, request=1, type=6, size=1, deadband='0.01' {Cryogenics halla_cryo}
CPI603QB: host=opsmya6, active=1, request=1, type=6, size=1, deadband='0.01' {Cryogenics halla_cryo}
CPI603QC: host=opsmya6, active=1, request=1, type=6, size=1, deadband='0.01' {Cryogenics halla_cryo}
CPI60DLP: host=opsmya7, active=1, request=1, type=6, size=1, deadband='0.002' {Cryogenics}
CPI6614: host=opsmya6, active=1, request=1, type=6, size=1, deadband='0.04' {Cryogenics}
CPI671: host=opsmya7, active=1, request=1, type=6, size=1, deadband='0.01' {Cryogenics}
CPI671SC: host=opsmya7, active=1, request=1, type=6, size=1, deadband='0.01' {Cryogenics}
CPI671T: host=opsmya7, active=1, request=1, type=6, size=1, deadband='0.01' {Cryogenics}
CPI672: host=opsmya6, active=1, request=1, type=6, size=1, deadband='0.01' {Cryogenics}
CPI673: host=opsmya6, active=1, request=1, type=6, size=1, deadband='0.05' {Cryogenics}
CPI6751: host=opsmya7, active=1, request=1, type=6, size=1, deadband='0.01' {Cryogenics}
CPI7541: host=opsmya7, active=1, request=1, type=6, size=1, deadband='0.05' {Cryogenics}
CPI9521: host=opsmya6, active=1, request=1, type=6, size=1, deadband='0.01' {Cryogenics}
CPI9541: host=opsmya6, active=1, request=1, type=6, size=1, deadband='0.05' {Cryogenics}
CTD6614: host=opsmya13, active=1, request=1, type=6, size=1, deadband='0.01' {Cryogenics}
CTD671SC: host=opsmya13, active=1, request=1, type=6, size=1, deadband='0.01' {Cryogenics}
CTD671SD: host=opsmya13, active=1, request=1, type=6, size=1, deadband='0.01' {Cryogenics}
CTD671T: host=opsmya6, active=1, request=1, type=6, size=1, deadband='0.01' {Cryogenics}
CTD672: host=opsmya13, active=1, request=1, type=6, size=1, deadband='0.01' {Cryogenics}
CTD673: host=opsmya6, active=1, request=1, type=6, size=1, deadband='0.1' {Cryogenics}
CTD674: host=opsmya13, active=1, request=1, type=6, size=1, deadband='0.01' {Cryogenics}
CTD7541: host=opsmya6, active=1, request=1, type=6, size=1, deadband='0.01' {Cryogenics}
CTD9521: host=opsmya6, active=1, request=1, type=6, size=1, deadband='0.01' {Cryogenics}
CTD9541: host=opsmya13, active=1, request=1, type=6, size=1, deadband='0.01' {Cryogenics}
CTP6751: host=opsmya13, active=1, request=1, type=6, size=1, deadband='0.01' {Cryogenics}
IBC3H00CRCUR4: host=opsmya8, active=1, request=1, type=6, size=1 {bcmVme}
IBC3H04:bcmtctemp_r: host=opsmya8, active=1, request=1, type=6, size=1 {bcmVme}
IBC3H05:bcmtctemp_r: host=opsmya8, active=1, request=1, type=6, size=1, deadband='.14' {bcmVme}
IPM3C01.XPOS: host=opsmya3, active=1, request=1, type=2, size=1, deadband='0.005' {bpm}
IPM3C01.YPOS: host=opsmya3, active=1, request=1, type=2, size=1, deadband='0.005' {bpm}
IPM3C02.XPOS: host=opsmya3, active=1, request=1, type=2, size=1, deadband='0.005' {bpm}
IPM3C02.YPOS: host=opsmya3, active=1, request=1, type=2, size=1, deadband='0.005' {bpm}
IPM3C03.XPOS: host=opsmya3, active=1, request=1, type=2, size=1, deadband='0.005' {bpm}
IPM3C03.YPOS: host=opsmya3, active=1, request=1, type=2, size=1, deadband='0.005' {bpm}
IPM3C04.XPOS: host=opsmya3, active=1, request=1, type=2, size=1, deadband='0.005' {bpm}
IPM3C04.YPOS: host=opsmya3, active=1, request=1, type=2, size=1, deadband='0.005' {bpm}
IPM3C05.XPOS: host=opsmya3, active=1, request=1, type=2, size=1, deadband='0.005' {bpm}
IPM3C05.YPOS: host=opsmya3, active=1, request=1, type=2, size=1, deadband='0.005' {bpm}
IPM3C06.XPOS: host=opsmya3, active=1, request=1, type=2, size=1, deadband='0.005' {bpm}
IPM3C06.YPOS: host=opsmya3, active=1, request=1, type=2, size=1, deadband='0.005' {bpm}
IPM3C07.XPOS: host=opsmya3, active=1, request=1, type=2, size=1, deadband='0.005' {bpm}
IPM3C07.YPOS: host=opsmya3, active=1, request=1, type=2, size=1, deadband='0.005' {bpm}
IPM3C07A.XPOS: host=opsmya3, active=1, request=1, type=2, size=1, deadband='0.005' {bpm}
IPM3C07A.YPOS: host=opsmya3, active=1, request=1, type=2, size=1, deadband='0.005' {bpm}
IPM3C08.XPOS: host=opsmya3, active=1, request=1, type=2, size=1, deadband='0.005' {bpm}
IPM3C08.YPOS: host=opsmya3, active=1, request=1, type=2, size=1, deadband='0.005' {bpm}
IPM3C10.XPOS: host=opsmya3, active=1, request=1, type=2, size=1, deadband='0.005' {bpm}
IPM3C10.YPOS: host=opsmya3, active=1, request=1, type=2, size=1, deadband='0.005' {bpm}
IPM3C11.XPOS: host=opsmya3, active=1, request=1, type=2, size=1, deadband='0.005' {bpm}
IPM3C11.YPOS: host=opsmya3, active=1, request=1, type=2, size=1, deadband='0.005' {bpm}
IPM3C12.XPOS: host=opsmya3, active=1, request=1, type=2, size=1, deadband='0.005' {bpm}
IPM3C12.YPOS: host=opsmya3, active=1, request=1, type=2, size=1, deadband='0.005' {bpm}
IPM3C14.XPOS: host=opsmya3, active=1, request=1, type=2, size=1, deadband='0.005' {bpm}
IPM3C14.YPOS: host=opsmya3, active=1, request=1, type=2, size=1, deadband='0.005' {bpm}
IPM3C16.XPOS: host=opsmya3, active=1, request=1, type=2, size=1, deadband='0.005' {bpm}
IPM3C16.YPOS: host=opsmya3, active=1, request=1, type=2, size=1, deadband='0.005' {bpm}
IPM3C17.XPOS: host=opsmya3, active=1, request=1, type=2, size=1, deadband='0.005' {bpm}
IPM3C17.YPOS: host=opsmya3, active=1, request=1, type=2, size=1, deadband='0.005' {bpm}
IPM3C18.XPOS: host=opsmya3, active=1, request=1, type=2, size=1, deadband='0.005' {bpm}
IPM3C18.YPOS: host=opsmya3, active=1, request=1, type=2, size=1, deadband='0.005' {bpm}
IPM3C19.XPOS: host=opsmya3, active=1, request=1, type=2, size=1, deadband='0.005' {bpm}
IPM3C19.YPOS: host=opsmya3, active=1, request=1, type=2, size=1, deadband='0.005' {bpm}
IPM3C20.YPOS: host=opsmya1, active=1, request=1, type=2, size=1, deadband='0.005' {bpm}
IPM3C21.XPOS: host=opsmya3, active=1, request=1, type=2, size=1, deadband='0.005' {bpm}
IPM3C21.YPOS: host=opsmya3, active=1, request=1, type=2, size=1, deadband='0.005' {bpm}
IPM3H02.XPOS: host=opsmya3, active=1, request=1, type=2, size=1, deadband='0.005' {bpm}
IPM3H02.YPOS: host=opsmya3, active=1, request=1, type=2, size=1, deadband='0.005' {bpm}
IPM3H04.XPOS: host=opsmya3, active=1, request=1, type=2, size=1, deadband='0.005' {bpm}
IPM3H04.YPOS: host=opsmya3, active=1, request=1, type=2, size=1, deadband='0.005' {bpm}
IPM3H07A.XPOF: host=opsmya3, active=1, request=1, type=2, size=1 {bpm MyRestore}
IPM3H07A.XPOS: host=opsmya3, active=1, request=1, type=2, size=1, deadband='0.005' {bpm}
IPM3H07A.XRAW: host=opsmya3, active=1, request=1, type=2, size=1 {bpm}
IPM3H07A.XSOF: host=opsmya3, active=1, request=1, type=2, size=1 {bpm MyRestore}
IPM3H07A.YPOF: host=opsmya3, active=1, request=1, type=2, size=1 {bpm MyRestore}
IPM3H07A.YPOS: host=opsmya3, active=1, request=1, type=2, size=1, deadband='0.005' {bpm}
IPM3H07A.YRAW: host=opsmya3, active=1, request=1, type=2, size=1 {bpm}
IPM3H07A.YSOF: host=opsmya3, active=1, request=1, type=2, size=1 {bpm MyRestore}
IPM3H07B.XPOF: host=opsmya3, active=1, request=1, type=2, size=1 {bpm MyRestore}
IPM3H07B.XPOS: host=opsmya3, active=1, request=1, type=2, size=1, deadband='0.005' {bpm}
IPM3H07B.XRAW: host=opsmya3, active=1, request=1, type=2, size=1 {bpm}
IPM3H07B.XSOF: host=opsmya3, active=1, request=1, type=2, size=1 {bpm MyRestore}
IPM3H07B.YPOF: host=opsmya3, active=1, request=1, type=2, size=1 {bpm MyRestore}
IPM3H07B.YPOS: host=opsmya3, active=1, request=1, type=2, size=1, deadband='0.005' {bpm}
IPM3H07B.YRAW: host=opsmya3, active=1, request=1, type=2, size=1 {bpm}
IPM3H07B.YSOF: host=opsmya3, active=1, request=1, type=2, size=1 {bpm MyRestore}
IPM3H07C.XPOF: host=opsmya3, active=1, request=1, type=2, size=1 {bpm MyRestore}
IPM3H07C.XPOS: host=opsmya3, active=1, request=1, type=2, size=1, deadband='0.005' {bpm}
IPM3H07C.XRAW: host=opsmya3, active=1, request=1, type=2, size=1 {bpm}
IPM3H07C.XSOF: host=opsmya3, active=1, request=1, type=2, size=1 {bpm MyRestore}
IPM3H07C.YPOF: host=opsmya3, active=1, request=1, type=2, size=1 {bpm MyRestore}
IPM3H07C.YPOS: host=opsmya3, active=1, request=1, type=2, size=1, deadband='0.005' {bpm}
IPM3H07C.YRAW: host=opsmya3, active=1, request=1, type=2, size=1 {bpm}
IPM3H07C.YSOF: host=opsmya3, active=1, request=1, type=2, size=1 {bpm MyRestore}
IPM3H08.XPOF: host=opsmya3, active=1, request=1, type=2, size=1 {bpm MyRestore}
IPM3H08.XPOS: host=opsmya3, active=1, request=1, type=2, size=1, deadband='0.005' {bpm}
IPM3H08.XRAW not archived
IPM3H08.XSOF: host=opsmya3, active=1, request=1, type=2, size=1 {bpm MyRestore}
IPM3H08.YPOF: host=opsmya3, active=1, request=1, type=2, size=1 {bpm MyRestore}
IPM3H08.YPOS: host=opsmya3, active=1, request=1, type=2, size=1, deadband='0.005' {bpm}
IPM3H08.YRAW not archived
IPM3H08.YSOF: host=opsmya3, active=1, request=1, type=2, size=1 {bpm MyRestore}
IPM3H09.XPOF: host=opsmya3, active=1, request=1, type=2, size=1 {bpm MyRestore}
IPM3H09.XPOS: host=opsmya3, active=1, request=1, type=2, size=1, deadband='0.005' {bpm}
IPM3H09.XRAW: host=opsmya3, active=1, request=1, type=2, size=1 {bpm}
IPM3H09.XSOF: host=opsmya3, active=1, request=1, type=2, size=1 {bpm MyRestore}
IPM3H09.YPOF: host=opsmya3, active=1, request=1, type=2, size=1 {bpm MyRestore}
IPM3H09.YPOS: host=opsmya3, active=1, request=1, type=2, size=1, deadband='0.005' {bpm}
IPM3H09.YRAW: host=opsmya3, active=1, request=1, type=2, size=1 {bpm}
IPM3H09.YSOF: host=opsmya3, active=1, request=1, type=2, size=1 {bpm MyRestore}
IPM3H09B.XPOF: host=opsmya3, active=0, request=1, type=2, size=1, deadband='0.05' {bpm}
IPM3H09B.XPOS: host=opsmya3, active=0, request=1, type=2, size=1, deadband='0.05' {bpm}
IPM3H09B.XRAW not archived
IPM3H09B.XSOF: host=opsmya3, active=0, request=1, type=2, size=1 {bpm}
IPM3H09B.YPOF: host=opsmya3, active=0, request=1, type=2, size=1, deadband='0.05' {bpm}
IPM3H09B.YPOS: host=opsmya3, active=0, request=1, type=2, size=1, deadband='0.05' {bpm}
IPM3H09B.YRAW not archived
IPM3H09B.YSOF: host=opsmya3, active=0, request=1, type=2, size=1 {bpm}
IPM3P01A.XPOS: host=opsmya3, active=0, request=1, type=2, size=1, deadband='0.025' {bpm}
IPM3P01A.YPOS: host=opsmya3, active=0, request=1, type=2, size=1, deadband='0.025' {bpm}
IPM3P02A.XPOS: host=opsmya3, active=1, request=1, type=2, size=1, deadband='0.005' {bpm}
IPM3P02A.YPOS: host=opsmya3, active=1, request=1, type=2, size=1, deadband='0.005' {bpm}
IPM3P02B.XPOS: host=opsmya3, active=1, request=1, type=2, size=1, deadband='0.005' {bpm}
IPM3P02B.YPOS: host=opsmya3, active=1, request=1, type=2, size=1, deadband='0.005' {bpm}
IPM3P03A.XPOS: host=opsmya3, active=0, request=1, type=2, size=1, deadband='0.025' {bpm}
IPM3P03A.YPOS: host=opsmya3, active=0, request=1, type=2, size=1, deadband='0.01' {bpm}
Q1HallP not archived
Q2HallP not archived
Q3HallP not archived
SLD3H04RAd: host=opsmya12, active=1, request=1, type=6, size=1, deadband='1' {ioncham}
SLD3H07RAd: host=opsmya12, active=1, request=1, type=6, size=1, deadband='1' {ioncham}
SLD3H09RAd: host=opsmya12, active=1, request=1, type=6, size=1, deadband='1' {ioncham}
SLD3P03RAd: host=opsmya12, active=1, request=1, type=6, size=1, deadband='1' {ioncham}
SLDD307ARAd: host=opsmya12, active=1, request=1, type=6, size=1, deadband='1' {ioncham}
SLDD307RAd: host=opsmya12, active=1, request=1, type=6, size=1, deadband='1' {ioncham}
ecDI_ADC_MPS not archived
ecDI_ADC_SET not archived
ecDI_B_Set_NMR not archived
ecDI_B_True_NMR not archived
ecDI_Delta_T1_W not archived
ecDI_Delta_T2_W not archived
ecDI_Delta_T3_W not archived
ecDI_F_L1 not archived
ecDI_F_L2 not archived
ecDI_F_L3 not archived
ecDI_F_L4 not archived
ecDI_F_R1 not archived
ecDI_F_R2 not archived
ecDI_F_R3 not archived
ecDI_F_R4 not archived
ecDI_I_True: host=opsmya6, active=1, request=1, type=6, size=1, deadband='1%' {Cryogenics}
ecDI_I_coarse: host=opsmya12, active=1, request=1, type=6, size=1 {hallc}
ecDI_M_flow_Lx: host=opsmya6, active=1, request=1, type=6, size=1, deadband='1%' {Cryogenics}
ecDI_M_flow_Rx: host=opsmya6, active=1, request=1, type=6, size=1, deadband='1%' {Cryogenics}
ecDI_POLARITY: host=opsmya0, active=1, request=1, type=6, size=1, deadband='0.1' {HallC_HMS}
ecDI_P_He not archived
ecDI_P_N2 not archived
ecDI_S1_LVDT_true not archived
ecDI_S3_LVDT_true not archived
ecDI_S4_LVDT_true not archived
ecDI_S5_LVDT_true: host=opsmya6, active=1, request=1, type=6, size=1, deadband='0.3' {Cryogenics}
ecDI_S6_LVDT_true: host=opsmya6, active=1, request=1, type=6, size=1, deadband='0.3' {Cryogenics}
ecDI_Set_Current not archived
ecDI_T_He_L_CL_W not archived
ecDI_T_He_R_CL_W not archived
ecDI_T_LHe_1 not archived
ecDI_T_LHe_2 not archived
ecDI_T_LHe_3 not archived
ecDI_T_LHe_4 not archived
ecDI_T_LHe_In not archived
ecDI_T_LHe_L not archived
ecDI_T_LHe_Out not archived
ecDI_T_LHe_R not archived
ecDI_T_LHe_av: host=opsmya6, active=1, request=1, type=6, size=1, deadband='.05' {Cryogenics}
ecDI_T_LN2_1 not archived
ecDI_T_LN2_2 not archived
ecDI_T_LN2_3 not archived
ecDI_T_LN2_4 not archived
ecDI_T_LN2_In not archived
ecDI_T_LN2_Out not archived
ecDI_T_LN2_av not archived
ecDI_T_pipe not archived
ecDI_U1 not archived
ecDI_U2 not archived
ecDI_U3 not archived
ecDI_U4 not archived
ecDI_U5 not archived
ecDI_U6 not archived
ecDI_U7 not archived
ecDI_U8 not archived
ecDI_VL_SW not archived
ecDI_VR_SW not archived
ecDI_V_SW not archived
ecDI_Weight not archived
ecDI_cd_LHe_level not archived
ecDI_cd_LN2_level not archived
ecDI_h_LHe: host=opsmya6, active=1, request=1, type=6, size=1, deadband='.1' {Cryogenics}
ecDI_h_LN2 not archived
ecDI_p_vac not archived
ecDI_s11_LVDT_true: host=opsmya6, active=1, request=1, type=6, size=1, deadband='0.3' {Cryogenics}
ecDI_s2_LVDT_true not archived
ecDI_s7_LVDT_true not archived
ecDI_s8_LVDT_true not archived
ecHMS_Angle: host=opsmya5, active=1, request=1, type=6, size=1, deadband='0.01' {hallc}
ecHMS_Angle_Offset not archived
ecI_Q1 not archived
ecI_Q2 not archived
ecI_Q3 not archived
ecP_HMS not archived
ecQ1_ADC_MPS not archived
ecQ1_ADC_SET not archived
ecQ1_CL_N_LVDT_true not archived
ecQ1_CL_N_VE not archived
ecQ1_CL_P_LVDT_true not archived
ecQ1_CL_P_VE not archived
ecQ1_Coil_1 not archived
ecQ1_Coil_2 not archived
ecQ1_Coil_3 not archived
ecQ1_Coil_4 not archived
ecQ1_Coils_Left not archived
ecQ1_Coils_Right not archived
ecQ1_I_True: host=opsmya6, active=1, request=1, type=6, size=1, deadband='1%' {Cryogenics}
ecQ1_I_coarse: host=opsmya12, active=1, request=1, type=6, size=1 {hallc}
ecQ1_POLARITY: host=opsmya0, active=1, request=1, type=6, size=1, deadband='0.1' {HallC_HMS}
ecQ1_P_He not archived
ecQ1_P_N2 not archived
ecQ1_Penning_vac not archived
ecQ1_Pirani_vac not archived
ecQ1_Set_Current not archived
ecQ1_T1_CG not archived
ecQ1_T2_CG not archived
ecQ1_T3_CG not archived
ecQ1_T4_CG not archived
ecQ1_T_He_Delta not archived
ecQ1_T_He_Sup not archived
ecQ1_T_He_av: host=opsmya6, active=1, request=1, type=6, size=1, deadband='.05' {Cryogenics}
ecQ1_T_He_res not archived
ecQ1_T_He_ret not archived
ecQ1_T_N2_Inner not archived
ecQ1_T_N2_Resv not archived
ecQ1_T_N2_Ret not archived
ecQ1_T_N2_Sup not archived
ecQ1_T_N2_av not archived
ecQ1_T_N2_outer not archived
ecQ1_T_cls_end_coil not archived
ecQ1_T_cls_end_yoke not archived
ecQ1_T_mag_cen_coil not archived
ecQ1_T_tur_end_yoke not archived
ecQ1_V13_LVDT_true: host=opsmya6, active=1, request=1, type=6, size=1, deadband='0.3' {Cryogenics}
ecQ1_V19_LVDT_true not archived
ecQ1_V1_LVDT_true not archived
ecQ1_V3_LVDT_true not archived
ecQ1_V4_LVDT_true not archived
ecQ1_V6_LVDT_true not archived
ecQ1_V8_LVDT_true: host=opsmya6, active=1, request=1, type=6, size=1, deadband='0.3' {Cryogenics}
ecQ1_h_LHe: host=opsmya6, active=1, request=1, type=6, size=1, deadband='.1' {Cryogenics}
ecQ1_h_LN2 not archived
ecQ1_m_flow_CL_N: host=opsmya6, active=1, request=1, type=6, size=1, deadband='1%' {Cryogenics}
ecQ1_m_flow_CL_P: host=opsmya6, active=1, request=1, type=6, size=1, deadband='1%' {Cryogenics}
ecQ1_m_flow_neck not archived
ecQ1_p_vac not archived
ecQ1_vWR_LVDT_true: host=opsmya6, active=1, request=1, type=6, size=1, deadband='0.3' {Cryogenics}
ecQ2_ADC_MPS not archived
ecQ2_ADC_SET not archived
ecQ2_CL_N_LVDT_true not archived
ecQ2_CL_N_VE not archived
ecQ2_CL_P_LVDT_true not archived
ecQ2_CL_P_VE not archived
ecQ2_Coil_1 not archived
ecQ2_Coil_2 not archived
ecQ2_Coil_3 not archived
ecQ2_Coil_4 not archived
ecQ2_Coils_Left not archived
ecQ2_Coils_Right not archived
ecQ2_I_True: host=opsmya6, active=1, request=1, type=6, size=1, deadband='1%' {Cryogenics}
ecQ2_I_coarse: host=opsmya12, active=1, request=1, type=6, size=1 {hallc}
ecQ2_POLARITY: host=opsmya0, active=1, request=1, type=6, size=1, deadband='0.1' {HallC_HMS}
ecQ2_P_He not archived
ecQ2_P_N2 not archived
ecQ2_Penning_vac not archived
ecQ2_Pirani_vac not archived
ecQ2_Set_Current not archived
ecQ2_T1_CG not archived
ecQ2_T2_CG not archived
ecQ2_T3_CG not archived
ecQ2_T4_CG not archived
ecQ2_T_He_Delta not archived
ecQ2_T_He_Sup not archived
ecQ2_T_He_av: host=opsmya6, active=1, request=1, type=6, size=1, deadband='.05' {Cryogenics}
ecQ2_T_He_res not archived
ecQ2_T_He_ret not archived
ecQ2_T_N2_Inner not archived
ecQ2_T_N2_Resv not archived
ecQ2_T_N2_Ret not archived
ecQ2_T_N2_Sup not archived
ecQ2_T_N2_av not archived
ecQ2_T_N2_outer not archived
ecQ2_T_cls_end_coil not archived
ecQ2_T_cls_end_yoke not archived
ecQ2_T_mag_cen_coil not archived
ecQ2_T_tur_end_yoke not archived
ecQ2_V13_LVDT_true: host=opsmya6, active=1, request=1, type=6, size=1, deadband='0.3' {Cryogenics}
ecQ2_V19_LVDT_true not archived
ecQ2_V1_LVDT_true not archived
ecQ2_V3_LVDT_true not archived
ecQ2_V4_LVDT_true not archived
ecQ2_V6_LVDT_true not archived
ecQ2_V8_LVDT_true: host=opsmya6, active=1, request=1, type=6, size=1, deadband='0.3' {Cryogenics}
ecQ2_h_LHe: host=opsmya6, active=1, request=1, type=6, size=1, deadband='.1' {Cryogenics}
ecQ2_h_LN2 not archived
ecQ2_m_flow_CL_N: host=opsmya6, active=1, request=1, type=6, size=1, deadband='1%' {Cryogenics}
ecQ2_m_flow_CL_P: host=opsmya6, active=1, request=1, type=6, size=1, deadband='1%' {Cryogenics}
ecQ2_m_flow_neck not archived
ecQ2_p_vac not archived
ecQ2_vWR_LVDT_true: host=opsmya6, active=1, request=1, type=6, size=1, deadband='0.3' {Cryogenics}
ecQ3_ADC_MPS not archived
ecQ3_ADC_SET not archived
ecQ3_CL_N_LVDT_true not archived
ecQ3_CL_N_VE not archived
ecQ3_CL_P_LVDT_true not archived
ecQ3_CL_P_VE not archived
ecQ3_Coil_1 not archived
ecQ3_Coil_2 not archived
ecQ3_Coil_3 not archived
ecQ3_Coil_4 not archived
ecQ3_Coils_Left not archived
ecQ3_Coils_Right not archived
ecQ3_I_True: host=opsmya6, active=1, request=1, type=6, size=1, deadband='1%' {Cryogenics}
ecQ3_I_coarse: host=opsmya12, active=1, request=1, type=6, size=1 {hallc}
ecQ3_POLARITY: host=opsmya0, active=1, request=1, type=6, size=1, deadband='0.1' {HallC_HMS}
ecQ3_P_He not archived
ecQ3_P_N2 not archived
ecQ3_Penning_vac not archived
ecQ3_Pirani_vac not archived
ecQ3_Set_Current not archived
ecQ3_T1_CG not archived
ecQ3_T2_CG not archived
ecQ3_T3_CG not archived
ecQ3_T4_CG not archived
ecQ3_T_He_Delta not archived
ecQ3_T_He_Sup not archived
ecQ3_T_He_av: host=opsmya6, active=1, request=1, type=6, size=1, deadband='.05' {Cryogenics}
ecQ3_T_He_res not archived
ecQ3_T_He_ret not archived
ecQ3_T_N2_Inner not archived
ecQ3_T_N2_Resv not archived
ecQ3_T_N2_Ret not archived
ecQ3_T_N2_Sup not archived
ecQ3_T_N2_av not archived
ecQ3_T_N2_outer not archived
ecQ3_T_cls_end_coil not archived
ecQ3_T_cls_end_yoke not archived
ecQ3_T_mag_cen_coil not archived
ecQ3_T_tur_end_yoke not archived
ecQ3_V13_LVDT_true: host=opsmya6, active=1, request=1, type=6, size=1, deadband='0.3' {Cryogenics}
ecQ3_V19_LVDT_true not archived
ecQ3_V1_LVDT_true not archived
ecQ3_V3_LVDT_true not archived
ecQ3_V4_LVDT_true not archived
ecQ3_V6_LVDT_true not archived
ecQ3_V8_LVDT_true: host=opsmya6, active=1, request=1, type=6, size=1, deadband='0.3' {Cryogenics}
ecQ3_h_LHe: host=opsmya6, active=1, request=1, type=6, size=1, deadband='.1' {Cryogenics}
ecQ3_h_LN2 not archived
ecQ3_m_flow_CL_N: host=opsmya6, active=1, request=1, type=6, size=1, deadband='1%' {Cryogenics}
ecQ3_m_flow_CL_P: host=opsmya6, active=1, request=1, type=6, size=1, deadband='1%' {Cryogenics}
ecQ3_m_flow_neck not archived
ecQ3_p_vac not archived
ecQ3_vWR_LVDT_true: host=opsmya6, active=1, request=1, type=6, size=1, deadband='0.3' {Cryogenics}
ecS10_LVDT_true not archived
ecS9_LVDT_true not archived
ecSDI_ADC_readback_MPS not archived
ecSDI_B_True_NMR not archived
ecSDI_CH2_SW not archived
ecSDI_CH3_SW not archived
ecSDI_CL_L not archived
ecSDI_CL_R not archived
ecSDI_F1 not archived
ecSDI_F2 not archived
ecSDI_F3 not archived
ecSDI_F4 not archived
ecSDI_F5 not archived
ecSDI_F6 not archived
ecSDI_F7 not archived
ecSDI_F8 not archived
ecSDI_I_True: host=opsmya6, active=1, request=1, type=6, size=1, deadband='1%' {Cryogenics}
ecSDI_I_coarse: host=opsmya12, active=1, request=1, type=6, size=1 {hallc}
ecSDI_Left_CL_Valve not archived
ecSDI_PSU_Output_voltage not archived
ecSDI_P_He not archived
ecSDI_P_N2 not archived
ecSDI_Pancake_1 not archived
ecSDI_Pancake_2 not archived
ecSDI_Pancake_3 not archived
ecSDI_Pancake_4 not archived
ecSDI_Pancake_5 not archived
ecSDI_Pancake_6 not archived
ecSDI_Polarity: host=opsmya12, active=1, request=1, type=6, size=1 {hallc}
ecSDI_Right_CL_Valve not archived
ecSDI_Set_Current not archived
ecSDI_T_He_CD not archived
ecSDI_T_He_Delta not archived
ecSDI_T_He_LCLC not archived
ecSDI_T_He_RCLC not archived
ecSDI_T_He_Resv not archived
ecSDI_T_He_Sup not archived
ecSDI_T_He_WR not archived
ecSDI_T_He_av: host=opsmya6, active=1, request=1, type=6, size=1, deadband='.02' {Cryogenics}
ecSDI_T_He_ret not archived
ecSDI_T_LC_DS not archived
ecSDI_T_LC_US not archived
ecSDI_T_N2_BB not archived
ecSDI_T_N2_BT not archived
ecSDI_T_N2_OB not archived
ecSDI_T_N2_OT not archived
ecSDI_T_N2_Ret not archived
ecSDI_T_N2_Sup not archived
ecSDI_T_N2_av not archived
ecSDI_T_RC_DS not archived
ecSDI_T_RC_US not archived
ecSDI_T_Yoke_1 not archived
ecSDI_T_Yoke_2 not archived
ecSDI_T_Yoke_3 not archived
ecSDI_T_Yoke_4 not archived
ecSDI_V1_LVDT_true not archived
ecSDI_V2_LVDT_true not archived
ecSDI_V3_LVDT_true not archived
ecSDI_V4_LVDT_true not archived
ecSDI_V5_LVDT_true: host=opsmya6, active=1, request=1, type=6, size=1, deadband='0.3' {Cryogenics}
ecSDI_V6_LVDT_true: host=opsmya6, active=1, request=1, type=6, size=1, deadband='0.3' {Cryogenics}
ecSDI_Vacuum not archived
ecSDI_h_LHe: host=opsmya6, active=1, request=1, type=6, size=1, deadband='.1' {Cryogenics}
ecSDI_h_LN2 not archived
ecSDI_m_flow_CL_L: host=opsmya6, active=1, request=1, type=6, size=1, deadband='1%' {Cryogenics}
ecSDI_m_flow_CL_R: host=opsmya6, active=1, request=1, type=6, size=1, deadband='1%' {Cryogenics}
ecSDI_vWR_LVDT_true: host=opsmya6, active=1, request=1, type=6, size=1, deadband='0.3' {Cryogenics}
ecSHB_ADC_readback_MPS not archived
ecSHB_CH2_SW not archived
ecSHB_CL_L not archived
ecSHB_CL_R not archived
ecSHB_Coil_1 not archived
ecSHB_Coil_2 not archived
ecSHB_F1 not archived
ecSHB_F10 not archived
ecSHB_F11 not archived
ecSHB_F12 not archived
ecSHB_F13 not archived
ecSHB_F14 not archived
ecSHB_F3 not archived
ecSHB_F4 not archived
ecSHB_F5 not archived
ecSHB_F6 not archived
ecSHB_F7 not archived
ecSHB_F9 not archived
ecSHB_HallP not archived
ecSHB_I_True: host=opsmya6, active=1, request=1, type=6, size=1, deadband='1%' {Cryogenics}
ecSHB_I_coarse: host=opsmya12, active=1, request=1, type=6, size=1 {hallc}
ecSHB_Interlock not archived
ecSHB_PT_He_1 not archived
ecSHB_PT_He_2 not archived
ecSHB_PT_He_3 not archived
ecSHB_PT_He_4 not archived
ecSHB_P_He not archived
ecSHB_P_N2 not archived
ecSHB_Polarity: host=opsmya12, active=1, request=1, type=6, size=1 {hallc}
ecSHB_Set_Current not archived
ecSHB_T_Coil_1 not archived
ecSHB_T_Coil_2 not archived
ecSHB_T_Coil_3 not archived
ecSHB_T_Coil_4 not archived
ecSHB_T_He_CD not archived
ecSHB_T_He_Delta not archived
ecSHB_T_He_LCLC not archived
ecSHB_T_He_RCLC not archived
ecSHB_T_He_Resv not archived
ecSHB_T_He_Sup not archived
ecSHB_T_He_WR not archived
ecSHB_T_He_av: host=opsmya6, active=1, request=1, type=6, size=1, deadband='.05' {Cryogenics}
ecSHB_T_He_ret not archived
ecSHB_T_N2_10 not archived
ecSHB_T_N2_11 not archived
ecSHB_T_N2_12 not archived
ecSHB_T_N2_6 not archived
ecSHB_T_N2_7 not archived
ecSHB_T_N2_8 not archived
ecSHB_T_N2_9 not archived
ecSHB_T_N2_Ret not archived
ecSHB_T_N2_Sup not archived
ecSHB_T_N2_av not archived
ecSHB_V1_LVDT_true not archived
ecSHB_V2_LVDT_true not archived
ecSHB_V3_LVDT_true not archived
ecSHB_V4_LVDT_true not archived
ecSHB_V5_LVDT_true: host=opsmya6, active=1, request=1, type=6, size=1, deadband='0.3' {Cryogenics}
ecSHB_V6_LVDT_true: host=opsmya6, active=1, request=1, type=6, size=1, deadband='0.3' {Cryogenics}
ecSHB_Vacuum not archived
ecSHB_h_LHe: host=opsmya6, active=1, request=1, type=6, size=1, deadband='0.1' {Cryogenics}
ecSHB_h_LN2 not archived
ecSHB_m_flow_CL_L: host=opsmya6, active=1, request=1, type=6, size=1, deadband='1%' {Cryogenics}
ecSHB_m_flow_CL_R: host=opsmya6, active=1, request=1, type=6, size=1, deadband='1%' {Cryogenics}
ecSHB_vWR_LVDT_true: host=opsmya6, active=1, request=1, type=6, size=1, deadband='0.3' {Cryogenics}
ecSHMS_Angle: host=opsmya5, active=1, request=1, type=6, size=1, deadband='0.01' {hallc}
ecSHMS_Angle_Offset not archived
ecSHMS_Shutter_status not archived
ecSP_SHMS not archived
ecSQ1_ADC_readback_MPS not archived
ecSQ1_CH2_SW not archived
ecSQ1_CH3_SW not archived
ecSQ1_CL_L not archived
ecSQ1_CL_R not archived
ecSQ1_Coil_1 not archived
ecSQ1_Coil_2 not archived
ecSQ1_Coil_3 not archived
ecSQ1_Coil_4 not archived
ecSQ1_Coils_Left not archived
ecSQ1_Coils_Right not archived
ecSQ1_F1 not archived
ecSQ1_F2 not archived
ecSQ1_F3 not archived
ecSQ1_F4 not archived
ecSQ1_F5 not archived
ecSQ1_F6 not archived
ecSQ1_F7 not archived
ecSQ1_F8 not archived
ecSQ1_Flow_inc_factor not archived
ecSQ1_HallP not archived
ecSQ1_Hw_QD_interlock not archived
ecSQ1_I_True: host=opsmya6, active=1, request=1, type=6, size=1, deadband='1%' {Cryogenics}
ecSQ1_I_coarse: host=opsmya12, active=1, request=1, type=6, size=1 {hallc}
ecSQ1_Interlock not archived
ecSQ1_PSU_Control_Pwr not archived
ecSQ1_PSU_Main_Pwr not archived
ecSQ1_PSU_Output_voltage not archived
ecSQ1_P_He not archived
ecSQ1_P_N2 not archived
ecSQ1_Polarity: host=opsmya12, active=1, request=1, type=6, size=1 {hallc}
ecSQ1_Set_Current not archived
ecSQ1_T_Coil_1 not archived
ecSQ1_T_Coil_2 not archived
ecSQ1_T_Coil_3 not archived
ecSQ1_T_Coil_4 not archived
ecSQ1_T_He_CD not archived
ecSQ1_T_He_Delta not archived
ecSQ1_T_He_LCLC not archived
ecSQ1_T_He_LCLW not archived
ecSQ1_T_He_PT102_av not archived
ecSQ1_T_He_RCLC not archived
ecSQ1_T_He_RCLW not archived
ecSQ1_T_He_Resv not archived
ecSQ1_T_He_Sup not archived
ecSQ1_T_He_WR not archived
ecSQ1_T_He_av: host=opsmya6, active=1, request=1, type=6, size=1, deadband='.05' {Cryogenics}
ecSQ1_T_He_ret not archived
ecSQ1_T_N2_BB not archived
ecSQ1_T_N2_BT not archived
ecSQ1_T_N2_OB not archived
ecSQ1_T_N2_OT not archived
ecSQ1_T_N2_Ret not archived
ecSQ1_T_N2_Sup not archived
ecSQ1_T_N2_av not archived
ecSQ1_T_Yoke_1 not archived
ecSQ1_T_Yoke_2 not archived
ecSQ1_T_Yoke_3 not archived
ecSQ1_T_Yoke_4 not archived
ecSQ1_V1_LVDT_true not archived
ecSQ1_V2_LVDT_true not archived
ecSQ1_V3_LVDT_true not archived
ecSQ1_V4_LVDT_true not archived
ecSQ1_V5_LVDT_true: host=opsmya6, active=1, request=1, type=6, size=1, deadband='0.3' {Cryogenics}
ecSQ1_V6_LVDT_true: host=opsmya6, active=1, request=1, type=6, size=1, deadband='0.3' {Cryogenics}
ecSQ1_Vacuum not archived
ecSQ1_h_LHe: host=opsmya6, active=1, request=1, type=6, size=1, deadband='0.1' {Cryogenics}
ecSQ1_h_LN2 not archived
ecSQ1_m_flow_CL_L: host=opsmya6, active=1, request=1, type=6, size=1, deadband='1%' {Cryogenics}
ecSQ1_m_flow_CL_R: host=opsmya6, active=1, request=1, type=6, size=1, deadband='1%' {Cryogenics}
ecSQ1_vWR_LVDT_true: host=opsmya6, active=1, request=1, type=6, size=1, deadband='0.3' {Cryogenics}
ecSQ2_ADC_readback_MPS not archived
ecSQ2_CH2_SW not archived
ecSQ2_CH3_SW not archived
ecSQ2_CL_L not archived
ecSQ2_CL_R not archived
ecSQ2_Coil_1 not archived
ecSQ2_Coil_2 not archived
ecSQ2_Coil_3 not archived
ecSQ2_Coil_4 not archived
ecSQ2_Coils_Left not archived
ecSQ2_Coils_Right not archived
ecSQ2_F1 not archived
ecSQ2_F2 not archived
ecSQ2_F3 not archived
ecSQ2_F4 not archived
ecSQ2_F5 not archived
ecSQ2_F6 not archived
ecSQ2_F7 not archived
ecSQ2_F8 not archived
ecSQ2_HallP not archived
ecSQ2_Hw_QD_interlock not archived
ecSQ2_I_True: host=opsmya6, active=1, request=1, type=6, size=1, deadband='1%' {Cryogenics}
ecSQ2_I_coarse: host=opsmya12, active=1, request=1, type=6, size=1 {hallc}
ecSQ2_Interlock not archived
ecSQ2_Left_CL_Valve not archived
ecSQ2_PSU_Control_Pwr not archived
ecSQ2_PSU_Main_Pwr not archived
ecSQ2_PSU_Output_voltage not archived
ecSQ2_P_He not archived
ecSQ2_P_N2 not archived
ecSQ2_Polarity: host=opsmya12, active=1, request=1, type=6, size=1 {hallc}
ecSQ2_Right_CL_Valve not archived
ecSQ2_Set_Current not archived
ecSQ2_T_Coil_1 not archived
ecSQ2_T_Coil_2 not archived
ecSQ2_T_Coil_3 not archived
ecSQ2_T_Coil_4 not archived
ecSQ2_T_He_CD not archived
ecSQ2_T_He_Delta not archived
ecSQ2_T_He_LCLC not archived
ecSQ2_T_He_PT102_av not archived
ecSQ2_T_He_RCLC not archived
ecSQ2_T_He_Resv not archived
ecSQ2_T_He_Sup not archived
ecSQ2_T_He_WR not archived
ecSQ2_T_He_av: host=opsmya6, active=1, request=1, type=6, size=1, deadband='.05' {Cryogenics}
ecSQ2_T_He_ret not archived
ecSQ2_T_N2_BB not archived
ecSQ2_T_N2_BT not archived
ecSQ2_T_N2_OB not archived
ecSQ2_T_N2_OT not archived
ecSQ2_T_N2_Ret not archived
ecSQ2_T_N2_Sup not archived
ecSQ2_T_N2_av not archived
ecSQ2_T_Yoke_1 not archived
ecSQ2_T_Yoke_2 not archived
ecSQ2_T_Yoke_3 not archived
ecSQ2_T_Yoke_4 not archived
ecSQ2_V1_LVDT_true not archived
ecSQ2_V2_LVDT_true not archived
ecSQ2_V3_LVDT_true not archived
ecSQ2_V4_LVDT_true not archived
ecSQ2_V5_LVDT_true: host=opsmya6, active=1, request=1, type=6, size=1, deadband='0.3' {Cryogenics}
ecSQ2_V6_LVDT_true: host=opsmya6, active=1, request=1, type=6, size=1, deadband='0.3' {Cryogenics}
ecSQ2_Vacuum not archived
ecSQ2_h_LHe: host=opsmya6, active=1, request=1, type=6, size=1, deadband='0.1' {Cryogenics}
ecSQ2_h_LN2 not archived
ecSQ2_m_flow_CL_L: host=opsmya6, active=1, request=1, type=6, size=1, deadband='1%' {Cryogenics}
ecSQ2_m_flow_CL_R: host=opsmya6, active=1, request=1, type=6, size=1, deadband='1%' {Cryogenics}
ecSQ2_vWR_LVDT_true: host=opsmya6, active=1, request=1, type=6, size=1, deadband='0.3' {Cryogenics}
ecSQ3_ADC_readback_MPS not archived
ecSQ3_CH2_SW not archived
ecSQ3_CH3_SW not archived
ecSQ3_CL_L not archived
ecSQ3_CL_R not archived
ecSQ3_Coil_1 not archived
ecSQ3_Coil_2 not archived
ecSQ3_Coil_3 not archived
ecSQ3_Coil_4 not archived
ecSQ3_Coils_Left not archived
ecSQ3_Coils_Right not archived
ecSQ3_F1 not archived
ecSQ3_F2 not archived
ecSQ3_F3 not archived
ecSQ3_F4 not archived
ecSQ3_F5 not archived
ecSQ3_F6 not archived
ecSQ3_F7 not archived
ecSQ3_F8 not archived
ecSQ3_HallP not archived
ecSQ3_Hw_QD_interlock not archived
ecSQ3_I_True: host=opsmya6, active=1, request=1, type=6, size=1, deadband='1%' {Cryogenics}
ecSQ3_I_coarse: host=opsmya12, active=1, request=1, type=6, size=1 {hallc}
ecSQ3_Interlock not archived
ecSQ3_Left_CL_Valve not archived
ecSQ3_PSU_Control_Pwr not archived
ecSQ3_PSU_Main_Pwr not archived
ecSQ3_PSU_Output_voltage not archived
ecSQ3_P_He not archived
ecSQ3_P_N2 not archived
ecSQ3_Polarity: host=opsmya12, active=1, request=1, type=6, size=1 {hallc}
ecSQ3_Right_CL_Valve not archived
ecSQ3_Set_Current not archived
ecSQ3_T_Coil_1 not archived
ecSQ3_T_Coil_2 not archived
ecSQ3_T_Coil_3 not archived
ecSQ3_T_Coil_4 not archived
ecSQ3_T_He_CD not archived
ecSQ3_T_He_Delta not archived
ecSQ3_T_He_LCLC not archived
ecSQ3_T_He_PT102_av not archived
ecSQ3_T_He_RCLC not archived
ecSQ3_T_He_Resv not archived
ecSQ3_T_He_Sup not archived
ecSQ3_T_He_WR not archived
ecSQ3_T_He_av: host=opsmya6, active=1, request=1, type=6, size=1, deadband='.02' {Cryogenics}
ecSQ3_T_He_ret not archived
ecSQ3_T_N2_BB not archived
ecSQ3_T_N2_BT not archived
ecSQ3_T_N2_OB not archived
ecSQ3_T_N2_OT not archived
ecSQ3_T_N2_Ret not archived
ecSQ3_T_N2_Sup not archived
ecSQ3_T_N2_av not archived
ecSQ3_T_Yoke_1 not archived
ecSQ3_T_Yoke_2 not archived
ecSQ3_T_Yoke_3 not archived
ecSQ3_T_Yoke_4 not archived
ecSQ3_V1_LVDT_true not archived
ecSQ3_V2_LVDT_true not archived
ecSQ3_V3_LVDT_true not archived
ecSQ3_V4_LVDT_true not archived
ecSQ3_V5_LVDT_true: host=opsmya6, active=1, request=1, type=6, size=1, deadband='0.3' {Cryogenics}
ecSQ3_V6_LVDT_true: host=opsmya6, active=1, request=1, type=6, size=1, deadband='0.3' {Cryogenics}
ecSQ3_Vacuum not archived
ecSQ3_h_LHe: host=opsmya6, active=1, request=1, type=6, size=1, deadband='.1' {Cryogenics}
ecSQ3_h_LN2 not archived
ecSQ3_m_flow_CL_L: host=opsmya6, active=1, request=1, type=6, size=1, deadband='1%' {Cryogenics}
ecSQ3_m_flow_CL_R: host=opsmya6, active=1, request=1, type=6, size=1, deadband='1%' {Cryogenics}
ecSQ3_vWR_LVDT_true: host=opsmya6, active=1, request=1, type=6, size=1, deadband='0.3' {Cryogenics}
ecSTL_T_He_Return_Can3 not archived
ecSTL_T_He_Return_TL: host=opsmya6, active=1, request=1, type=6, size=1, deadband='1%' {Cryogenics}
ecSTL_T_He_Supply_Can3 not archived
ecSTL_T_He_Supply_Gas not archived
ecSTL_T_He_Supply_TL: host=opsmya6, active=1, request=1, type=6, size=1, deadband='1%' {Cryogenics}
ecSTL_T_N2_Supply_Can3 not archived
ecSTL_T_N2_Supply_TL not archived
ecSTL_T_N2_Vent not archived
ecSTL_V10_LVDT_true not archived
ecSTL_Vacuum not archived
ecSTL_v9_LVDT_true not archived
ecT_HX not archived
ecT_HX_LN2 not archived
echmst1: host=opsmya6, active=1, request=1, type=6, size=1, deadband='1%' {Cryogenics}
echmst2: host=opsmya6, active=1, request=1, type=6, size=1, deadband='1%' {Cryogenics}
echmst3 not archived
echmst4 not archived
echmst5 not archived
echmst6 not archived
echmst7 not archived
echmst8 not archived
haCryo_15K_total_F not archived
hcBDSPOS: host=opsmya3, active=1, request=1, type=6, size=1, deadband='1' {HallC_Cryotarget}
hcCryo_4K_Return_P not archived
hcCryo_4K_Return_T not archived
hcCryo_4K_Supply_F not archived
hcCryo_4K_Supply_P not archived
hcCryo_4K_Supply_T not archived
hcCryo_Return_P: host=opsmya3, active=1, request=1, type=6, size=1, deadband='2%' {HallC_Cryotarget}
hcCryo_Return_T: host=opsmya3, active=1, request=1, type=6, size=1, deadband='1%' {HallC_Cryotarget}
hcCryo_Supply_F not archived
hcCryo_Supply_P: host=opsmya3, active=1, request=1, type=6, size=1, deadband='2%' {HallC_Cryotarget}
hcCryo_Supply_T: host=opsmya3, active=1, request=1, type=6, size=1, deadband='1%' {HallC_Cryotarget}
hcD2_Omega_DPG_R: host=opsmya3, active=1, request=1, type=6, size=1, deadband='.1' {HallC_Cryotarget}
hcD2_P_Ballast_R: host=opsmya3, active=1, request=1, type=6, size=1, deadband='.1' {HallC_Cryotarget}
hcD2_P_Exhaust_R: host=opsmya3, active=1, request=1, type=6, size=1, deadband='.1' {HallC_Cryotarget}
hcD2_P_Fill_Bottle_R: host=opsmya3, active=1, request=1, type=6, size=1, deadband='.1' {HallC_Cryotarget}
hcD2_P_Fill_Target_R: host=opsmya3, active=1, request=1, type=6, size=1, deadband='.1' {HallC_Cryotarget}
hcH2_Omega_DPG_R: host=opsmya3, active=1, request=1, type=6, size=1, deadband='.1' {HallC_Cryotarget}
hcH2_P_Ballast_R: host=opsmya3, active=1, request=1, type=6, size=1, deadband='.1' {HallC_Cryotarget}
hcH2_P_Exhaust_R: host=opsmya3, active=1, request=1, type=6, size=1, deadband='.1' {HallC_Cryotarget}
hcH2_P_Fill_Bottle_R: host=opsmya3, active=1, request=1, type=6, size=1, deadband='.1' {HallC_Cryotarget}
hcH2_P_Fill_Target_R: host=opsmya3, active=1, request=1, type=6, size=1, deadband='.1' {HallC_Cryotarget}
hcHe3_P_Comp_In_R: host=opsmya3, active=1, request=1, type=6, size=1, deadband='.1' {HallC_Cryotarget}
hcHe3_P_Comp_Out_R: host=opsmya3, active=1, request=1, type=6, size=1, deadband='.1' {HallC_Cryotarget}
hcHe3_P_Fill_Target_R: host=opsmya3, active=1, request=1, type=6, size=1, deadband='.1' {HallC_Cryotarget}
hcHe3_P_Tank_R: host=opsmya3, active=1, request=1, type=6, size=1, deadband='.1' {HallC_Cryotarget}
hcHe_Omega_DPG_R: host=opsmya3, active=1, request=1, type=6, size=1, deadband='.1' {HallC_Cryotarget}
hcHe_P_Purge_R: host=opsmya3, active=1, request=1, type=6, size=1, deadband='.1' {HallC_Cryotarget}
hcHe_Supply_1_R not archived
hcL1_Fan_Freq_R: host=opsmya3, active=1, request=1, type=6, size=1, deadband='.1' {HallC_Cryotarget}
hcL1_Fan_current_R: host=opsmya3, active=1, request=1, type=6, size=1, deadband='.1' {HallC_Cryotarget}
hcL1_Fan_drive_hz_R: host=opsmya3, active=1, request=1, type=6, size=1, deadband='.1' {HallC_Cryotarget}
hcL1_Fan_prcnthz_R: host=opsmya3, active=1, request=1, type=6, size=1, deadband='.1' {HallC_Cryotarget}
hcL1_Fan_prcnthz_W: host=opsmya3, active=1, request=1, type=6, size=1, deadband='.1' {HallC_Cryotarget}
hcL1_Fan_voltage_R: host=opsmya3, active=1, request=1, type=6, size=1, deadband='.1' {HallC_Cryotarget}
hcL1_HPH_I_CONV: host=opsmya3, active=1, request=1, type=6, size=1, deadband='.1' {HallC_Cryotarget}
hcL1_HPH_V_CONV: host=opsmya3, active=1, request=1, type=6, size=1, deadband='.1' {HallC_Cryotarget}
hcL1_JTV_Rca: host=opsmya3, active=1, request=1, type=6, size=1, deadband='.1' {HallC_Cryotarget}
hcL1_beam_current not archived
hcL1_hp_pid.CVAL: host=opsmya3, active=1, request=1, type=2, size=1, deadband='.01' {HallC_Cryotarget}
hcL1_hp_pid.OVAL: host=opsmya3, active=1, request=1, type=2, size=1, deadband='.1' {HallC_Cryotarget}
hcL1_hp_pid: host=opsmya3, active=1, request=1, type=2, size=1, deadband='.1' {HallC_Cryotarget}
hcL1_hp_power_R: host=opsmya3, active=1, request=1, type=6, size=1, deadband='.1' {HallC_Cryotarget}
hcL1_pbeam: host=opsmya3, active=1, request=1, type=6, size=1, deadband='.1' {HallC_Cryotarget}
hcL2_Fan_Freq_R: host=opsmya3, active=1, request=1, type=6, size=1, deadband='.1' {HallC_Cryotarget}
hcL2_Fan_current_R: host=opsmya3, active=1, request=1, type=6, size=1, deadband='.1' {HallC_Cryotarget}
hcL2_Fan_drive_hz_R: host=opsmya3, active=1, request=1, type=6, size=1, deadband='.1' {HallC_Cryotarget}
hcL2_Fan_prcnthz_R: host=opsmya3, active=1, request=1, type=6, size=1, deadband='.1' {HallC_Cryotarget}
hcL2_Fan_prcnthz_W: host=opsmya3, active=1, request=1, type=6, size=1, deadband='.1' {HallC_Cryotarget}
hcL2_Fan_voltage_R: host=opsmya3, active=1, request=1, type=6, size=1, deadband='.1' {HallC_Cryotarget}
hcL2_HPH_I_CONV: host=opsmya3, active=1, request=1, type=6, size=1, deadband='.1' {HallC_Cryotarget}
hcL2_HPH_V_CONV: host=opsmya3, active=1, request=1, type=6, size=1, deadband='.1' {HallC_Cryotarget}
hcL2_JTV_Rca: host=opsmya3, active=1, request=1, type=6, size=1, deadband='.1' {HallC_Cryotarget}
hcL2_beam_current not archived
hcL2_hp_pid.CVAL: host=opsmya3, active=1, request=1, type=2, size=1, deadband='.01' {HallC_Cryotarget}
hcL2_hp_pid.OVAL: host=opsmya3, active=1, request=1, type=2, size=1, deadband='.1' {HallC_Cryotarget}
hcL2_hp_pid: host=opsmya3, active=1, request=1, type=2, size=1, deadband='.1' {HallC_Cryotarget}
hcL2_hp_power_R: host=opsmya3, active=1, request=1, type=6, size=1, deadband='.1' {HallC_Cryotarget}
hcL2_pbeam: host=opsmya3, active=1, request=1, type=6, size=1, deadband='.1' {HallC_Cryotarget}
hcL3_Fan_Freq_R: host=opsmya3, active=1, request=1, type=6, size=1, deadband='.1' {HallC_Cryotarget}
hcL3_Fan_current_R: host=opsmya3, active=1, request=1, type=6, size=1, deadband='10' {HallC_Cryotarget}
hcL3_Fan_drive_hz_R.VAL not archived
hcL3_Fan_prcnthz_R.VAL not archived
hcL3_Fan_prcnthz_W.VAL not archived
hcL3_Fan_voltage_R: host=opsmya3, active=1, request=1, type=6, size=1, deadband='0.1' {HallC_Cryotarget}
hcL3_HPH_I_CONV: host=opsmya3, active=1, request=1, type=6, size=1, deadband='.1' {HallC_Cryotarget}
hcL3_HPH_V_CONV: host=opsmya3, active=1, request=1, type=6, size=1, deadband='.1' {HallC_Cryotarget}
hcL3_JTV_Rca: host=opsmya3, active=1, request=1, type=6, size=1, deadband='.1' {HallC_Cryotarget}
hcL3_beam_current not archived
hcL3_hp_pid.CVAL: host=opsmya3, active=1, request=1, type=2, size=1, deadband='.01' {HallC_Cryotarget}
hcL3_hp_pid.OVAL: host=opsmya3, active=1, request=1, type=2, size=1, deadband='.1' {HallC_Cryotarget}
hcL3_hp_pid: host=opsmya3, active=1, request=1, type=2, size=1, deadband='.1' {HallC_Cryotarget}
hcL3_hp_power_R: host=opsmya3, active=1, request=1, type=6, size=1, deadband='.1' {HallC_Cryotarget}
hcL3_pbeam: host=opsmya3, active=1, request=1, type=6, size=1, deadband='.1' {HallC_Cryotarget}
hcLS218_1_T1: host=opsmya3, active=1, request=1, type=6, size=1, deadband='0.02' {HallC_Cryotarget}
hcLS218_1_T2: host=opsmya3, active=1, request=1, type=6, size=1, deadband='0.02' {HallC_Cryotarget}
hcLS218_1_T3: host=opsmya3, active=1, request=1, type=6, size=1, deadband='0.02' {HallC_Cryotarget}
hcLS218_1_T5: host=opsmya3, active=1, request=1, type=6, size=1, deadband='0.02' {HallC_Cryotarget}
hcLS218_1_T6: host=opsmya3, active=1, request=1, type=6, size=1, deadband='0.02' {HallC_Cryotarget}
hcLS218_1_T7: host=opsmya3, active=1, request=1, type=6, size=1, deadband='0.02' {HallC_Cryotarget}
hcLS218_2_T1: host=opsmya3, active=1, request=1, type=6, size=1, deadband='0.02' {HallC_Cryotarget}
hcLS218_2_T2: host=opsmya3, active=1, request=1, type=6, size=1, deadband='0.02' {HallC_Cryotarget}
hcLS218_2_T3: host=opsmya3, active=1, request=1, type=6, size=1, deadband='0.02' {HallC_Cryotarget}
hcLS218_2_T5: host=opsmya3, active=1, request=1, type=6, size=1, deadband='0.02' {HallC_Cryotarget}
hcLS218_2_T6: host=opsmya3, active=1, request=1, type=6, size=1, deadband='0.02' {HallC_Cryotarget}
hcLS218_2_T7: host=opsmya3, active=1, request=1, type=6, size=1, deadband='0.02' {HallC_Cryotarget}
hcLS218_3_T1: host=opsmya3, active=1, request=1, type=6, size=1, deadband='0.02' {HallC_Cryotarget}
hcLS218_3_T2: host=opsmya3, active=1, request=1, type=6, size=1, deadband='0.02' {HallC_Cryotarget}
hcLS218_3_T3: host=opsmya3, active=1, request=1, type=6, size=1, deadband='0.02' {HallC_Cryotarget}
hcLS218_3_T5: host=opsmya3, active=1, request=1, type=6, size=1, deadband='0.02' {HallC_Cryotarget}
hcLS218_3_T6: host=opsmya3, active=1, request=1, type=6, size=1, deadband='0.02' {HallC_Cryotarget}
hcLS218_3_T7: host=opsmya3, active=1, request=1, type=6, size=1, deadband='0.02' {HallC_Cryotarget}
hcLS218_4_T1: host=opsmya3, active=1, request=1, type=6, size=1, deadband='0.02' {HallC_Cryotarget}
hcLS218_4_T2: host=opsmya3, active=1, request=1, type=6, size=1, deadband='0.02' {HallC_Cryotarget}
hcLS218_4_T3: host=opsmya3, active=1, request=1, type=6, size=1, deadband='0.02' {HallC_Cryotarget}
hcLS218_4_T4: host=opsmya3, active=1, request=1, type=6, size=1, deadband='0.02' {HallC_Cryotarget}
hcLS218_4_T5: host=opsmya3, active=1, request=1, type=6, size=1, deadband='0.02' {HallC_Cryotarget}
hcLS218_4_T6: host=opsmya3, active=1, request=1, type=6, size=1, deadband='0.02' {HallC_Cryotarget}
hcLS218_4_T7: host=opsmya3, active=1, request=1, type=6, size=1, deadband='0.02' {HallC_Cryotarget}
hcScatt_Chamber_Vac_R: host=opsmya3, active=1, request=1, type=6, size=1 {HallC_Cryotarget}
hcScatt_Chamber_Vac_R_Copy not archived
hcWR_EV_R: host=opsmya3, active=1, request=1, type=6, size=1, deadband='.1' {HallC_Cryotarget}
hccrate03:CurrentRead:u0 not archived
hccrate03:CurrentRead:u1 not archived
hccrate03:CurrentRead:u3 not archived
hccrate03:CurrentRead:u5 not archived
hccrate03:VoltageRead:u0 not archived
hccrate03:VoltageRead:u1 not archived
hccrate03:VoltageRead:u3 not archived
hccrate03:VoltageRead:u5 not archived
hchcLlA_beam_current not archived
hchv14:00:023:IMon not archived
hchv14:00:023:VMon not archived
hchv14:04:002:IMon not archived
hchv14:04:002:VMon not archived
hcozone: host=opsmya11, active=1, request=1, type=6, size=1, deadband='0.1' {radmon}
hcrate2 not archived
hcrate3 not archived
hcrate4 not archived
hcrate5 not archived
hcrate6 not archived
hcrate7 not archived
hrozone: host=opsmya11, active=1, request=1, type=6, size=1, deadband='0.001' {radmon}
hsL1_TI_Cryo_Out_R not archived
hsL2_TI_Cryo_Out_R not archived
hsL3_TI_Cryo_Out_R not archived
hsLS218_4_T8 not archived
ibcm1: host=opsmya5, active=1, request=1, type=6, size=1, deadband='0.01' {hallc}
ibcm17: host=opsmya2, active=1, request=1, type=6, size=1, deadband='0.01' {HallC_bcm}
ibcm2: host=opsmya5, active=1, request=1, type=6, size=1, deadband='0.01' {hallc}
ibcm4a not archived
ibcm4b not archived
iunser: host=opsmya2, active=1, request=1, type=6, size=1, deadband='0.01' {HallC_bcm}
More information about the Dsg-hallc_controls
mailing list