[Dsg-hallc_controls] Controls7 issue
Pablo Campero
campero at jlab.org
Wed Jul 25 11:27:09 EDT 2018
Hi Steve,
>From your attached screen shots it seems like you will need to configure your Ethernet driver on RSLink Classic.
The IP adrress for the SHMS ethernet module is 129.57.165.13. Then you can try again on RSLOGIX5000 by re-assigning the correct path to the SHMS PLC controller and go online with no problems.
Regards,
Pablo
From: "Steve Lassiter" <lassiter at jlab.org>
To: "dsg-hallc controls" <dsg-hallc_controls at jlab.org>
Sent: Wednesday, July 25, 2018 11:13:58 AM
Subject: Re: [Dsg-hallc_controls] Controls7 issue
Hi,
Update..
screen shots of what happens when I try to go online.
I now have a checked out license for RSlogix5000
Steven
From: "Steve Lassiter" <lassiter at jlab.org>
To: "dsg-hallc controls" <dsg-hallc_controls at jlab.org>
Sent: Wednesday, July 25, 2018 10:24:52 AM
Subject: Controls7 issue
Hi,
I am having to use controls7 pc for work as the laptop ccont01 is being repaired (just a black screen).
The HMI is working fine on controls7 but the rslogix program cannot find the path to the PLC's inside the fence.
Also, it cannot obtain a license fro skylla7 for rslogix.
I am working from home today, so I need to stay on controls7.
Steven
_______________________________________________
Dsg-hallc_controls mailing list
Dsg-hallc_controls at jlab.org
https://mailman.jlab.org/mailman/listinfo/dsg-hallc_controls
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <https://mailman.jlab.org/pipermail/dsg-hallc_controls/attachments/20180725/4516782e/attachment.html>
More information about the Dsg-hallc_controls
mailing list