Tyler,
  Put it on COPS.PHALLC

Sent from my iPhone

> On Jun 5, 2018, at 10:40 AM, Tyler Lemon <tlemon at jlab.org> wrote:
> 
> Hello,
> 
> For the small UPS for Hall C's SHMS PLC controllers, HMS PLC controllers, and HMS I/O Chassis, we will need to use a UPS management card accessory from APC to be able to monitor the UPS's status.
> 
> The card that would work best for our applications is the AP9613 Dry Contact I/O SmartSlot Card. Attached is the manual for the card.
> 
> The AP9613 gives six relay outputs that can be set to indicate UPS on battery, UPS battery low, UPS battery needs replacing, UPS overload, or an internal fault Boolean summary.
> 
> The AP9613 also gives four inputs that allow users to remotely turn UPS on/off or initiate a self-test.
> 
> The card is available as a punch-out order from CDW-G through JLab's stockroom for $223.43 (link to CDW-G site: https://www.cdwg.com/product/Schneider-Dry-Contact-I-O-SmartSlot-Card-UPS-management-module/2944677?pfm=srh#PO).
> 
> Please let us know if the AP9613 card is acceptable. If it is, I can submit the PR today.
> 
> Best regards,
> Tyler
> 
> <AP9613 Dry Contact IO SmartSlot Card user manual.pdf>