>>>DSG's weekly report
>>>Modified to PLC routine to ramp down the quadrupoles when interlock
is enabled
(PSU_Sum_Interlock bit =1).
Not required. The existing PLC code ramps down the power supply when
there is an interlock.
>>>>Added pulse-timer that waits for 100 ms and then transmits trigger
pulse to enable the sending of
0 A current value.
Not required.
The new current regulation code should go into standby waiting for new
input.
The code should not try to control the power supply when/if there is an
interlock.
Cheers,
Mike
On 11/9/2018 4:56 PM, Pablo Campero wrote:
> Hello,
>
> I have attached the DSG's weekly report for Hall C-PLC tasks.
>
> Best Regards,
> Pablo
>
>
> _______________________________________________
> Dsg-hallc_controls mailing list
> Dsg-hallc_controls at jlab.org
> https://mailman.jlab.org/mailman/listinfo/dsg-hallc_controls