[Dsg-hallc_controls] Revised routine

Amanda Hoebel amandah at jlab.org
Wed Nov 28 16:27:16 EST 2018


Hi Mike, 

Attached are the PDFs of the revised function block diagrams and ladder logic. 

Regards, 
Amanda 



From: "Mike Fowler" <fowler at jlab.org> 
To: "dsg-hallc controls" <dsg-hallc_controls at jlab.org> 
Sent: Monday, November 12, 2018 8:43:23 AM 
Subject: Re: [Dsg-hallc_controls] DSG's PLC tasks report 

>>>DSG's weekly report 
>>>Modified to PLC routine to ramp down the quadrupoles when interlock is enabled 
(PSU_Sum_Interlock bit =1). 
Not required. The existing PLC code ramps down the power supply when there is an interlock. 

>>>>Added pulse-timer that waits for 100 ms and then transmits trigger pulse to enable the sending of 
0 A current value. 
Not required. 

The new current regulation code should go into standby waiting for new input. 
The code should not try to control the power supply when/if there is an interlock. 

Cheers, 
Mike 




On 11/9/2018 4:56 PM, Pablo Campero wrote: 



Hello, 

I have attached the DSG's weekly report for Hall C-PLC tasks. 

Best Regards, 
Pablo 


_______________________________________________
Dsg-hallc_controls mailing list Dsg-hallc_controls at jlab.org https://mailman.jlab.org/mailman/listinfo/dsg-hallc_controls 






_______________________________________________ 
Dsg-hallc_controls mailing list 
Dsg-hallc_controls at jlab.org 
https://mailman.jlab.org/mailman/listinfo/dsg-hallc_controls 
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <https://mailman.jlab.org/pipermail/dsg-hallc_controls/attachments/20181128/1061b682/attachment-0001.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: HMS_Controls_current_loop_LL.pdf
Type: application/pdf
Size: 23526 bytes
Desc: not available
URL: <https://mailman.jlab.org/pipermail/dsg-hallc_controls/attachments/20181128/1061b682/attachment-0002.pdf>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: HMS_Controls_current_loop_FBD.pdf
Type: application/pdf
Size: 43295 bytes
Desc: not available
URL: <https://mailman.jlab.org/pipermail/dsg-hallc_controls/attachments/20181128/1061b682/attachment-0003.pdf>


More information about the Dsg-hallc_controls mailing list