Short of connecting to that PLC, no.
Should I also be writing to the controller tag Steve created on the HMS PLC as well?
Since we don't have access to the HMI screens I don't know what the field the PT2025 is reporting (EPICS only has the dipole current), but currently the PT2026 has 1.4442039 T with the last 2 digits bouncing around, but it's staying pretty close to 40 (low of 36, high of 46 for the short time I was watching the tag).
----- Original Message -----
> From: "Mike Fowler" <fowler at jlab.org>
> To: "dsg-hallc controls" <dsg-hallc_controls at jlab.org>
> Sent: Wednesday, September 26, 2018 2:55:38 PM
> Subject: Re: [Dsg-hallc_controls] Dipole Field Regulation PLC code completed
> On 9/26/2018 11:07 AM, Brian Eng wrote:
>> the NMR is currently locked and sending field values
>
> Any way we can see the values?
>
> Mike