[Dsg-hallc_controls] Revised routine
Amanda Hoebel
amandah at jlab.org
Fri Jan 4 15:29:23 EST 2019
Sorry, I meant to say Steve, not Mike!
________________________________
From: Amanda Hoebel
Sent: Friday, January 4, 2019 3:26 PM
To: dsg-hallc_controls at jlab.org
Subject: Re: Revised routine
Hi Mike,
I am unsure of how to export routines to .L5X from version 16 of RSLogix 5000 (since this is for HMS), or if that can even be done. I know it can be done in version 20. Attached is the .csv file of the tag names and the ACD file which you could use to copy/paste the routines into the program.
Regards,
Amanda
________________________________
From: Steven Lassiter
Sent: Friday, January 4, 2019 10:39 AM
To: Amanda Hoebel
Subject: Re: Revised routine
Hello Amanda,
can you send me the routines (*.L5x) and tags (*.csv) (controller vs program, names and type) in a separate file.
I will load into the test PLC and test it out
thanks
Steven
________________________________
From: Dsg-hallc_controls <dsg-hallc_controls-bounces at jlab.org> on behalf of Amanda Hoebel <amandah at jlab.org>
Sent: Wednesday, November 28, 2018 3:27:16 PM
To: dsg-hallc_controls at jlab.org
Subject: [Dsg-hallc_controls] Revised routine
Hi Mike,
Attached are the PDFs of the revised function block diagrams and ladder logic.
Regards,
Amanda
________________________________
From: "Mike Fowler" <fowler at jlab.org>
To: "dsg-hallc controls" <dsg-hallc_controls at jlab.org>
Sent: Monday, November 12, 2018 8:43:23 AM
Subject: Re: [Dsg-hallc_controls] DSG's PLC tasks report
>>>DSG's weekly report
>>>Modified to PLC routine to ramp down the quadrupoles when interlock is enabled
(PSU_Sum_Interlock bit =1).
Not required. The existing PLC code ramps down the power supply when there is an interlock.
>>>>Added pulse-timer that waits for 100 ms and then transmits trigger pulse to enable the sending of
0 A current value.
Not required.
The new current regulation code should go into standby waiting for new input.
The code should not try to control the power supply when/if there is an interlock.
Cheers,
Mike
On 11/9/2018 4:56 PM, Pablo Campero wrote:
Hello,
I have attached the DSG's weekly report for Hall C-PLC tasks.
Best Regards,
Pablo
_______________________________________________
Dsg-hallc_controls mailing list
Dsg-hallc_controls at jlab.org<mailto:Dsg-hallc_controls at jlab.org>
https://mailman.jlab.org/mailman/listinfo/dsg-hallc_controls
_______________________________________________
Dsg-hallc_controls mailing list
Dsg-hallc_controls at jlab.org
https://mailman.jlab.org/mailman/listinfo/dsg-hallc_controls
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <https://mailman.jlab.org/pipermail/dsg-hallc_controls/attachments/20190104/86b45891/attachment.html>
More information about the Dsg-hallc_controls