Hi Tim and Nick,
I've gathered a list of signals on the FCAL PLC that will need to be moved to the new Point IO system that DSG is developing.
Below is a table with the signals found. There are 12 PLC tags for the DIRC and ComCal. However, some of these tags are linked to the same input channel (like the bar box top and bottom differential pressures). These channels are highlighted in the table below.
Should the point IO system be configured in the same way? Or should we leave open channels for the potential addition of separate sensors for each tag?
PLC Tag Description PLC Slot PLC Channel
DIRC_BB_N_T_F North bar box N2 flow top 5 3
DIRC_BB_S_B_F South bar box N2 flow bottom 9 0
DIRC_BB_S_T_F South bar box N2 flow top 9 1
DIRC_BB_N_B_F North bar box N2 flow bottom 9 2
DIRC_BB_S_T_DP South bar box differential pressure top 9 3
DIRC_BB_S_B_DP South bar box differential pressure bottom
DIRC_BB_N_T_DP North bar box differential pressure top 9 4
DIRC_BB_N_B_DP North bar box differential pressure bottom
DIRC_BB_M_DP Barbox N2 manifold pressure 9 5
ComCal_N2_Flow ComCal N2 purge 9 6
DIRC_OB_N_F North optical box purge flow 9 7
DIRC_OB_S_F South optical box purge flow
I also received a quote on the modules needed from EECO.
The 1734-AENT Point IO Ethernet Adapter is $508.92.
The 1734-IE2V two-channel analog voltage input module is $289.88 per module.
I will put together a final cost estimate once the number of channels to be monitored are finalized.
Best regards,
Tyler