[dsg-halld_magnets] Hall D Solenoid PXI
Brian Eng
beng at jlab.org
Mon Dec 16 10:44:40 EST 2024
At least for the error PV it has a .osv of MAJOR_ALARM and a .zsv of NO_ALARM, which is what you'd expect for a boolean indicating an error. So I don't think there's anything to do with that one.
As far as the state PV (attached is a screenshot of what the numeric corresponds to): it doesn't have any of the high/low/hihi/lolo fields set, but I don't think any of the PV alarm settings are set from the PXI side? However, on this one when I try to read/set any of those fields I get an error. Maybe we can just get rid of this PV from the alarm handler?
I think really the only important status fields from the PXI is that the heartbeat field is toggling and maybe the uptime field is increasing.
________________________________
From: Joshua Ballard <ballardj at jlab.org>
Sent: Monday, December 16, 2024 10:31 AM
To: Brian Eng <beng at jlab.org>; dsg-halld_magnets at jlab.org <dsg-halld_magnets at jlab.org>
Cc: Scot Spiegel <spiegel at jlab.org>; Hovanes Egiyan <hovanes at jlab.org>
Subject: Re: Hall D Solenoid PXI
Hi Brian,
Thanks for responding even though you're off!
We can see those PV's - I used an old screenshot just capture the PV names. What's more important for us is how the alarm fields are configured for those PV's. We want to make sure we are notified when PXI is unhealthy - I presume this would be based on the "Error" PV. Can you tell us how the alarm fields for that PV are configured?
We are finished testing the Solenoid for 2024, so feel free to reboot as needed.
Thanks,
Josh
________________________________
From: Brian Eng <beng at jlab.org>
Sent: Monday, December 16, 2024 10:22 AM
To: dsg-halld_magnets at jlab.org <dsg-halld_magnets at jlab.org>; Joshua Ballard <ballardj at jlab.org>
Subject: Re: Hall D Solenoid PXI
Hi Josh,
I have/am on vacation and periodically catch up with emails.
I was hoping to use Kiosk mode since it's running an IoT version of Windows, but so far haven't had much luck with that. I'll try seeing if just putting in the startup items folder will do the trick (let me know when it's okay to reboot the controller so we can see if it does try to run it).
As for those PVs, I'm not sure what is going on, both of them have values currently (and when I try to read them from another machine the .stat field is LINK and .sevr is NO_ALARM). State is just a number/enum represent what state the PXI is in, and Error is the boolean output of the LabVIEW error cluster.
________________________________
From: dsg-halld_magnets <dsg-halld_magnets-bounces at jlab.org> on behalf of Joshua Ballard via dsg-halld_magnets <dsg-halld_magnets at jlab.org>
Sent: Monday, December 16, 2024 9:55 AM
To: dsg-halld_magnets at jlab.org <dsg-halld_magnets at jlab.org>
Subject: [dsg-halld_magnets] Fw: Hall D Solenoid PXI
Hi DSG Folks,
I'm seeking support for the Hall D Solenoid PXI system - see original email below.
Is someone available to help?
Thanks,
Joshua Ballard
________________________________
From: Joshua Ballard
Sent: Tuesday, December 10, 2024 10:33 AM
To: Brian Eng <beng at jlab.org>
Subject: Hall D Solenoid PXI
Hi Brian,
We're working through the beginning steps of Solenoid commissioning and have a few questions about the PXI.
1.
Beni has instructions for remoting in and restarting the application after a power cycle. Since it is now Windows, is it possible to restart the application using a .bat file on startup (or something like that)?
2.
There are two EPICS PV's that seem to represent the state/health of PXI.
[cid:487b339f-b916-48f4-ace3-1c6f4db65052]
For these PV's - what do the values of these PV's indicate?
For these PV's - can you update the alarm fields so they show up in our alarm handler as expected (MAJOR/MINOR, etc..)?
Thanks,
Josh
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <https://mailman.jlab.org/pipermail/dsg-halld_magnets/attachments/20241216/f591faa5/attachment-0001.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image.png
Type: image/png
Size: 18295 bytes
Desc: image.png
URL: <https://mailman.jlab.org/pipermail/dsg-halld_magnets/attachments/20241216/f591faa5/attachment-0002.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: state enum.png
Type: image/png
Size: 50702 bytes
Desc: state enum.png
URL: <https://mailman.jlab.org/pipermail/dsg-halld_magnets/attachments/20241216/f591faa5/attachment-0003.png>
More information about the dsg-halld_magnets
mailing list