[Utility Outage] Completed HVAC Outage - 04/19/2016 10:00
    Carroll W. Jones 
    jonesc at jlab.org
       
    Wed Jun 29 18:10:49 EDT 2016
    
    
  
The following HVAC Outage has been Completed:
Outage:      Switch Center Chiller Plant from Test Lab Basement Chillers to CUP Chillers
Proposed By: Carroll W. Jones
Start Time:  04/19/2016 10:00
End Time:    04/19/2016 12:00
Description/Impacts:
CUP Chiller 60-CH-1 did not load up to 800 tons as required to support the Chiller Plant loads.  The chiller superheat was significantly higher than it should and refrigerant oil had migrated though the system.  The chiller must operate for the oil to move back where it should be during normal operation.   To enable the CUP Chiller to operate and site cooling loads to be satisfied, both the Test Lab Chillers and CUP Chiller have been configured to operate.  The CUP Chiller will be monitored and evaluated during the next few days to determine why the superheat is high and the chiller will not produce its capacity of 800 tons.
For additional information or clarification, please contact Carroll Jones at 757-876-1778. 
_______________________________________________________________________________
Central Chiller Plant must be switched from Test Lab Basement Chillers to CUP Chillers to facilitate startup of recently installed CUP Chiller 60-CH-2.  The process requires restarting CUP Chiller 60-CH-1 to cool chiller water circulating through the CUP Building during the water balancing process for the incorporation of new Chiller 60-CH-2, new primary pump 60-PCWP-2,  and new secondary pump 60-SCWP-3 without significant impact on operating loads cooled by the chiller plant (F-Wing Data Center, TLA Cleanroom, EEL clean rooms, Accelerator Service Building Chilled Water Loop, and various areas within the Test Lab and EEL Building).  Areas may see a rise in space temperature of a few degrees  during the switchover which will return to normal once the switchover is complete.
Once switched to the CUP Chiller Plant, operational restrictions will be established for the TAB subcontractor and Chiller 60-CH-2 starttup team to minimize impact to areas conditioned by the Central Chiller Plant as balancing work is performed and the new equipment (chiller, primary pump, and secondary pump) is started.
For additional information or clarification, please contact Carroll Jones at 757-876-1778.
Impacted Areas:
	Bldg 01: North LINAC
	Bldg 02: South LINAC
	Bldg 21: North Extractor Service
	Bldg 38: South Access
	Bldg 39: East Arc Service
	Bldg 40: West Arc Service
	Bldg 45: West Arc Service
	Bldg 49: East Arc Service
	Bldg 50: East Arc Service
	Bldg 53: Injector Service
	Bldg 56: West Arc Service
	Bldg 60: Chiller Utility Plant
	Bldg 63: East Arc Service
	Bldg 67: North Access
	Bldg 68: West Arc Service
	Bldg 82: South Extractor Service
	Bldg 12: CEBAF Center
	Bldg 58: Test Lab
	Bldg 90: Experimental Equipment Lab
For more details, visit the webpage listed below:
https://cc.jlab.org/cgi-bin/infrastructure/Outage/OutageView?ident=108
    
    
More information about the Fac_outages
mailing list