[Utility Outage] Completed Power Outage - 07/30/2024 08:00
    dunlap at jlab.org 
    dunlap at jlab.org
       
    Wed Jul 31 12:40:28 EDT 2024
    
    
  
The following Power Outage has been Completed:
Outage:      B58 Shutdown Panel AP-LAB-18 
Proposed By: Howard Dunlap
Start Time:  07/30/2024 08:00
End Time:    07/30/2024 12:00
Description/Impacts:
CMTF cave exhaust fan needs to come on during an ODH event. Fan's amp rating is 19.0 amps, fed from 20-amp breaker. Breaker could be weak/defective. FME will shut down panel AP-LAB-18, replace 3-pole 20a breaker (# 7,9, &11), replace smaller # 12 wire to # 10 thhn from panel to existing motor starter, and terminate wires.  See panel schedule AP-LAB-18, ATLIS-112741, and or PTW 4145 for the affected.
Impacted Areas:
	Bldg 58: Test Lab
For more details, visit the webpage listed below:
https://cc.jlab.org/cgi-bin/infrastructure/Outage/OutageView?ident=24
    
    
More information about the Fac_outages
mailing list