[Utility Outage] Scheduled Power Outage - 07/30/2024 08:00
dunlap at jlab.org
dunlap at jlab.org
Mon Jul 29 08:06:30 EDT 2024
The following Power Outage has been Confirmed:
Outage: B58 Shutdown Panel AP-LAB-18
Proposed By: Howard Dunlap
Start Time: 07/30/2024 08:00
End Time: 07/30/2024 12:00
Description/Impacts:
CMTF cave exhaust fan needs to come on during an ODH event. Fan's amp rating is 19.0 amps, fed from 20-amp breaker. Breaker could be weak/defective. FME will shut down panel AP-LAB-18, replace 3-pole 20a breaker (# 7,9, &11), replace smaller # 12 wire to # 10 thhn from panel to existing motor starter, and terminate wires. See panel schedule AP-LAB-18, ATLIS-112741, and or PTW 4145 for the affected.
Impacted Areas:
Bldg 58: Test Lab
For more details, visit the webpage listed below:
https://cc.jlab.org/cgi-bin/infrastructure/Outage/OutageView?ident=24