[Fews] OCT9_09.pdf

Steve Christo christo at jlab.org
Fri Oct 9 07:59:53 EDT 2009


Hey Will,
Here's the PDF printout of the Concept, PLC control program (attached) 
that is currently downloaded to the the PLC controller. Searching for 
"trouble" yields results in the "Announce_Alarms", "Fire_Wire", 
"Sniffer_Valves" and "Vesda" sections. When we were looking at the 
program sections yesterday, we only saw the "Announce_Alarms" section. 
The others were not displayed so it was not not clear until now how the 
PLC handled the nitrogen filling faults.  The following code in the 
"Sniffer_Valves" section is most likely generating the problem that we 
were seeing.
--------------
IF adc4[5] < 2000 THEN
IF liquid_nitrogen_is_filling = 0 THEN
trouble_lamp := 1; (* this shouldn't ever happen unless the filling 
failed and timed out, maybe not even then *)
END_IF ;
liquid_nitrogen_level_problem := 1;
plc_ready := 0 ;
(* stop cycling valves if we run out of LN2 in small dewer *)
(* this avoids making false alarms due to detector warming up *)
ELSIF liquid_nitrogen_level_problem = 1 THEN
(* Here we have transitioned from having an LN2 problem to not having a 
problem *)
(* Now reset the sniffer so the spectrometer background isn't stale *)
initialize_SNIFFER := 1 ;
wait_for_pc := 0 ;
liquid_nitrogen_level_problem := 0 ;
ELSE
liquid_nitrogen_level_problem := 0 ;
END_IF ;
--------------
The new level control is giving the fill signal to the PLC but channel 1 
of the old controller is being used to measure the liquid level in the 
large Dewar. Ch. 1 was formerly used to measure the level of the 
Detector Dewar before we installed the new level controller (the old 
controller wouldn't let us use Ch. 2 to monitor the large Dewar level 
without an input to Ch. 1). When there was a problem with the connection 
on the level probe to Ch. 1 of the old controller, it gave the PLC a 
"failed to fill" signal and caused our problem. I don't remember how I 
left the controller tied into the system but it's obviously affecting 
it. I'll try to find a way to remove the old LN2 level controller from 
the system without harm and let you know. Thanks again.
Steve