[Fews] OCT9_09.pdf
Steve Christo
christo at jlab.org
Fri Oct 9 07:59:53 EDT 2009
Hey Will,
Here's the PDF printout of the Concept, PLC control program (attached)
that is currently downloaded to the the PLC controller. Searching for
"trouble" yields results in the "Announce_Alarms", "Fire_Wire",
"Sniffer_Valves" and "Vesda" sections. When we were looking at the
program sections yesterday, we only saw the "Announce_Alarms" section.
The others were not displayed so it was not not clear until now how the
PLC handled the nitrogen filling faults. The following code in the
"Sniffer_Valves" section is most likely generating the problem that we
were seeing.
--------------
IF adc4[5] < 2000 THEN
IF liquid_nitrogen_is_filling = 0 THEN
trouble_lamp := 1; (* this shouldn't ever happen unless the filling
failed and timed out, maybe not even then *)
END_IF ;
liquid_nitrogen_level_problem := 1;
plc_ready := 0 ;
(* stop cycling valves if we run out of LN2 in small dewer *)
(* this avoids making false alarms due to detector warming up *)
ELSIF liquid_nitrogen_level_problem = 1 THEN
(* Here we have transitioned from having an LN2 problem to not having a
problem *)
(* Now reset the sniffer so the spectrometer background isn't stale *)
initialize_SNIFFER := 1 ;
wait_for_pc := 0 ;
liquid_nitrogen_level_problem := 0 ;
ELSE
liquid_nitrogen_level_problem := 0 ;
END_IF ;
--------------
The new level control is giving the fill signal to the PLC but channel 1
of the old controller is being used to measure the liquid level in the
large Dewar. Ch. 1 was formerly used to measure the level of the
Detector Dewar before we installed the new level controller (the old
controller wouldn't let us use Ch. 2 to monitor the large Dewar level
without an input to Ch. 1). When there was a problem with the connection
on the level probe to Ch. 1 of the old controller, it gave the PLC a
"failed to fill" signal and caused our problem. I don't remember how I
left the controller tied into the system but it's obviously affecting
it. I'll try to find a way to remove the old LN2 level controller from
the system without harm and let you know. Thanks again.
Steve
-------------- next part --------------
A non-text attachment was scrubbed...
Name: OCT9_09.pdf
Type: application/pdf
Size: 81571 bytes
Desc: not available
Url : https://mailman.jlab.org/pipermail/fews/attachments/20091009/0b2e7c8b/attachment-0001.pdf
More information about the Fews
mailing list