The DCGAS IOC must have been rebooted and loaded the incorrect default
values. This happens because the default EPICS boot up values are wrong.
I made temporary changes, but the wrong default values will load again
if the IOC is rebooted.
The default values should be as follows with no LOW or HI;
dc_r1out_pres
HIHI 0.100
LOLO 0.010
dc_r2out_pres
HIHI 0.100
LOLO 0.010
dc_r3out_pres
HIHI 0.100
LOLO 0.010
kashy at jlab.org wrote:
> Hi I got a page last night ~ midnight from the counting house on DR R2
> pressure tickling the .03 low alarm. I asked them if they had checked long
> term range of this pressure. The answer was no. I asked if the DC was
> operating normally, the answer was yes.
> I check the LOLO value of the alarm it is .01 so I had them put the LOW
> value to .015
>
> George or Denny, Please check out the system if we need to make this
> change permanent or fix something else.
>
> After 3am I got another page on the LHe dewar. The IOC had crashed and the
> shift guys could not get it going. I talked them through it. This was the
> second crash in less than 24 hrs. Why? And we need to get the proper
> values in the reboot script. Earlier when this happened I saved the proper
> settings, but when we do a restore they do not come back properly.
>
>
> Thanks
> Dave
>
>
> _______________________________________________
> Hallb-engineering mailing list
> Hallb-engineering at jlab.org
> https://mailman.jlab.org/mailman/listinfo/hallb-engineering
>
--
George Jacobs
TJNAF
12000 Jefferson Ave.
Newport News, VA 23606
(office) 757-269-7115
(FAX) 757-269-5577
(cell) 757-876-0480
(texting)757-327-5435
(email) jacobsg at jlab.org
http://www.jlab.org/~jacobsg
More information about the Hallb-engineering
mailing list