Jefferson Lab Lessons Learned : Print Lesson
Have New Process Ideas Reviewed Before Use - Swift Staley Team
Statement of Lessons Learned
Worker-initiated improvements, while encouraged, must still be reviewed for safety.
Discussion of Activities
Internal surveillance uncovered an improper "improvement" for performing electrical zero-energy checks that had been passed by word-of-mouth between electricians.
NFPA 70E, section 120.1 requires an electrician to check a voltage testing device against a known energized source before and after use to confirm there is no voltage on the circuit and that the circuit had been de-energized.
Typically, an electrician uses a nearby receptacle as the known source. However, if the circuit is outdoors, removed from other structures, there might not be a receptacle nearby.
According to the informal "improvement," an electrician could use a 12-volt automotive battery in a work vehicle to confirm the voltage testing device is working. The assessor noted that to do this would require the meter to be switched to the direct-current-volts (V DC) setting when measuring the battery voltage and to the alternating-current-volts (V AC) setting when testing the de-energized circuit, thus failing to check the same internal meter circuits against the known source that were used to confirm the circuit is de-energized.
Analysis
Workers did not question the safety of an informally developed change to a procedure related to personnel safety.
Recommended Actions
Ensure that all personnel understand that any safety process modifications have been reviewed and approved through the safety expert or process orwner.
Managers and supervisors are to review and emphasize the importance of bringing new ideas through the work control process before passing them on to workers.
Equip electrician�s vehicles with an approved 12V DC to 110V AC Power Inverter so appropriate verification of the voltage testing device can be made.
JLab Preventive Measures
This lesson learned is provided as a good work practice.
Comments
9/12/2016 9:12:15 AM by Bailey, Mary Jo
Submitted to those with SAF603A: ELECTRICAL SAFETY AWARENESS
Summary Lesson ID: 967
Status: OK
Doc ID: 2016-JLAB-967
Priority: Info
Safety Related: YES
Originator: Bailey, Mary Jo
Issued: 9/12/2016 8:41:14 AM
Approved By: Bailey, Mary Jo
Approved On: 9/12/2016 9:12:15 AM
Source: DOECRD
Location: OTHER
Cost Savings:
Contact: James Tortorelli 270-441-5030
Queued Emails: 0
Sent Emails: 0
Viewings: 2 times Attachments
Hazard Issues
* Electricity
* Stored Energy: Mechanical, Hydraulic, Pneumatic
Skills
* SAF603A: ELECTRICAL SAFETY AWARENESS
Distribution/Notification
* *Division Safety Officers (DSOs)
* *Safety Wardens
* *DOE Notification
* *ESH&Q Liaisons
Do you have a lesson learned you would like to contribute? Contact the Lesson Learned Coordinator .
More information about the Hallb-engineering
mailing list