If it can wait until tomorrow, then we can ramp magnets down and safely reboot it during the pass change tomorrow morning.

-Eugene


From: Hallb-engineering <hallb-engineering-bounces at jlab.org> On Behalf Of Brian Eng via Hallb-engineering
Sent: Monday, May 13, 2024 10:58
To: David Kashy <kashy at jlab.org>; Probir Ghoshal <ghoshal at jlab.org>; Sandesh Gopinath <gopinath at jlab.org>
Cc: Hallb-eng <hallb-engineering at jlab.org>; dsg-hallb magnets <dsg-hallb_magnets at jlab.org>
Subject: Re: [Hallb-engineering] DP8620VCLDP

So I poked at the tags some more and it turns out that this one is updated on the DBox PLC, which I can still connect to. So I manually reset the error bit and this value is now updating on the PID screens.

caget B_TORUS:LHe:PV8522SR_Val:CVAL.INP
B_TORUS:LHe:PV8522SR_Val:CVAL.INP @PLC_CRYO PV8522SR_Val.CVAL

The torus PLC still isn't seeing updating values from the solenoid, but maybe we can put off the reboot until tomorrow?

________________________________
From: David Kashy <kashy at jlab.org<mailto:kashy at jlab.org>>
Sent: Monday, May 13, 2024 10:49 AM
To: Brian Eng <beng at jlab.org<mailto:beng at jlab.org>>; Probir Ghoshal <ghoshal at jlab.org<mailto:ghoshal at jlab.org>>; Sandesh Gopinath <gopinath at jlab.org<mailto:gopinath at jlab.org>>
Cc: Hallb-eng <hallb-engineering at jlab.org<mailto:hallb-engineering at jlab.org>>; dsg-hallb magnets <dsg-hallb_magnets at jlab.org<mailto:dsg-hallb_magnets at jlab.org>>
Subject: DP8620VCLDP

Just as a reminder,
This signal is a calculated value base on two pressure sensors.
the math goes as follows:

DP8620VCLDP =PT8620-PT8571

There is a similar setup of
DP8670MAGDP = PT8670-PT8571

Dave