[Halld-controls] [Dsg-halld_plc] PVs to be added to IOC for display in WEDM
Hovanes Egiyan
hovanes at jlab.org
Tue Jul 30 10:16:09 EDT 2019
Tyler,
Nick added an array of booleans for the status of solenoid MPS. It
translates into two
mbbiDirect EPICS records .
HDOPS gluon02:~> caget -0b 'SOL:i:MPS_Status_Read_BOOL;0'
SOL:i:MPS_Status_Read_BOOL;0 1111000001
HDOPS gluon02:~> caget -0b 'SOL:i:MPS_Status_Read_BOOL;1'
SOL:i:MPS_Status_Read_BOOL;1 10101000
HDOPS gluon02:~>
The first one (";0") keep the lower 16 bits, the second one (";1") keep
the higher bits.
EDM should be able to display these with byte monitor widget.
Hovanes
On 7/25/19 11:47 AM, Tyler Lemon wrote:
> Hello Hovanes,
>
> For the Solenoid Power supply screen, the PV
> "SOL:a:MPS_Status_Read_DINT" is the one being parsed in CSS for the
> status bits.
>
> When caget is used you get:"SOL:a:MPS_Status_Read_DINT 24 1 0 0 0 0 0
> 1 1 1 1 0 0 0 0 0 0 0 0 0 1 0 1 0 1"
>
> EDM has a byte monitor that can handle up to 16 bits. The array parsed
> in CSS is 24 elements, it would need to be split up into multiple PVs.
> On the Solenoid interlocks screen, the "MPS Interlock Sum" status is
> also pulled out of this array using a script. Since CSS is using
> scripts to get individual status bits on multiple screens, it may be
> best to make 24 new, individual Boolean PVs for each status bit.
>
> Also, on the Solenoid Voltages screen, the summed coil voltages below
> each coil graphic are obtained from a rule in CSS and cannot be
> displayed in EDM either. Four PVs will also need to be added to an IOC
> for the voltage sums.
>
> For the FDC chiller screen, the EDM byte monitor may be able to use
> the existing PVs. I'll look at this this afternoon and let you know if
> anything needs to be added to an IOC.
>
> Best regards,
> Tyler
>
> _______________________________________________
> Dsg-halld_plc mailing list
> Dsg-halld_plc at jlab.org
> https://mailman.jlab.org/mailman/listinfo/dsg-halld_plc
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <https://mailman.jlab.org/pipermail/halld-controls/attachments/20190730/b5511cbe/attachment.html>
More information about the Halld-controls
mailing list