Hi Hovanes and Nick,

Using the changes you all made to the PLC and IOC, I was able to get the status bits in EDM.

The Solenoid power supply screen and FDC chiller screen have been added to the epicsweb menu. With that, we have converted all 18 of the screens requested by Tim to WEDM.

If Hall D wants any other CSS screens converted to WEDM, let us know and we can make them.

Best regards,
Tyler
________________________________
From: Hovanes Egiyan <hovanes at jlab.org>
Sent: Tuesday, July 30, 2019 10:16 AM
To: dsg-halld_plc at jlab.org <dsg-halld_plc at jlab.org>; Tyler Lemon <tlemon at jlab.org>; Hall D Controls <halld-controls at jlab.org>
Subject: Re: [Dsg-halld_plc] PVs to be added to IOC for display in WEDM


Tyler,


Nick added an array of booleans for the status of solenoid MPS. It translates into two

mbbiDirect EPICS records .


HDOPS gluon02:~> caget -0b 'SOL:i:MPS_Status_Read_BOOL;0'
SOL:i:MPS_Status_Read_BOOL;0   1111000001
HDOPS gluon02:~> caget -0b 'SOL:i:MPS_Status_Read_BOOL;1'
SOL:i:MPS_Status_Read_BOOL;1   10101000
HDOPS gluon02:~>



The first one (";0") keep the lower 16 bits, the second one (";1") keep the higher bits.

EDM should be able to display these with byte monitor widget.


Hovanes



On 7/25/19 11:47 AM, Tyler Lemon wrote:
Hello Hovanes,

For the Solenoid Power supply screen, the PV "SOL:a:MPS_Status_Read_DINT" is the one being parsed in CSS for the status bits.

When caget is used you get: "SOL:a:MPS_Status_Read_DINT 24 1 0 0 0 0 0 1 1 1 1 0 0 0 0 0 0 0 0 0 1 0 1 0 1"

EDM has a byte monitor that can handle up to 16 bits. The array parsed in CSS is 24 elements, it would need to be split up into multiple PVs. On the Solenoid interlocks screen, the "MPS Interlock Sum" status is also pulled out of this array using a script. Since CSS is using scripts to get individual status bits on multiple screens, it may be best to make 24 new, individual Boolean PVs for each status bit.

Also, on the Solenoid Voltages screen, the summed coil voltages below each coil graphic are obtained from a rule in CSS and cannot be displayed in EDM either. Four PVs will also need to be added to an IOC for the voltage sums.

For the FDC chiller screen, the EDM byte monitor may be able to use the existing PVs. I'll look at this this afternoon and let you know if anything needs to be added to an IOC.

Best regards,
Tyler



_______________________________________________
Dsg-halld_plc mailing list
Dsg-halld_plc at jlab.org<mailto:Dsg-halld_plc at jlab.org>
https://mailman.jlab.org/mailman/listinfo/dsg-halld_plc

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <https://mailman.jlab.org/pipermail/halld-controls/attachments/20190730/a2f8e4ba/attachment.html>


More information about the Halld-controls mailing list