Hi Don,

>From the pump data sheet it looks like it could supply up to 130 mbar of pressure, but from that drawing it seems the way it is operated is you just bleed off the excess flow/pressure via the adjustment valve?

So the actual pressure should be significantly lower due to always trying to get the most free air flow out of the blower.

Do you have any measurements for what you think the system pressure is actually running at inside the enclosure or should we just select a sensor that is close to the max?

My worry is that we get one that reads in the 100 of mbar, but then the system only is at a handful of mbar so we lose a lot of precision and can't really tell what is going on with the system.

________________________________
From: Dsg-halla_ecal <dsg-halla_ecal-bounces at jlab.org> on behalf of Donald Jones via Dsg-halla_ecal <dsg-halla_ecal at jlab.org>
Sent: Thursday, November 14, 2024 10:48 AM
To: dsg-halla_ecal at jlab.org <dsg-halla_ecal at jlab.org>; Marc Mcmullen <mcmullen at jlab.org>
Subject: Re: [Dsg-halla_ecal] pressure sensors for cooling volume

I planned to insert a pressure gauge somewhere into the vertical pipe between the pump and manifold but your gauge could co in there anywhere.

[cid:ded82ade-0fe5-4a2d-9533-6caf62532a9d]


Donald Jones
Hall A/C Staff Scientist
Jefferson Lab
Newport News, VA
________________________________
From: Dsg-halla_ecal <dsg-halla_ecal-bounces at jlab.org> on behalf of Marc Mcmullen via Dsg-halla_ecal <dsg-halla_ecal at jlab.org>
Sent: Thursday, November 14, 2024 10:36 AM
To: dsg-halla_ecal at jlab.org <dsg-halla_ecal at jlab.org>
Subject: [Dsg-halla_ecal] pressure sensors for cooling volume

Hi Don,

Do you have a drawing or diagram of the cooling volume and system so we can give it a once over. It will help us determine the best sensor for the task.

Marc
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <https://mailman.jlab.org/pipermail/dsg-halla_ecal/attachments/20241114/93d78afe/attachment-0001.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image.png
Type: image/png
Size: 1229125 bytes
Desc: image.png
URL: <https://mailman.jlab.org/pipermail/dsg-halla_ecal/attachments/20241114/93d78afe/attachment-0001.png>


More information about the Dsg-halla_ecal mailing list