Hi Marco,

A few corrections/suggestions.

- Gas
Now that I understand better what you're trying to do, you should probably just get a flow meter and control the flow with a rotometer. This doesn't need a cRIO module since it readout via the network.

GM50A 013 202 S B 30 20
See page 4 of this PDF for what these mean: https://www.mksinst.com/docs/UR/GM50-DS.pdf
You might need to pick a different full scale flow (I picked 202 for 200 sccm).

- Humidity
Get a 5V DIN rail supply for the power.

- Chiller
The extra analog module we have (LRZ 912) will work with your chiller. It has 2 inputs & outputs, one of the inputs can be set to pump power which will be used to turn the flow off. I would use current instead of voltage as it is a bit more impervious to noise (NI 9265).

- HV
Nearly all of the boards have an interlock signal, but some don't (only have HV ON) and some of the interlock signals ramp the card down at the fastest rate, which is the same thing the RESET signal does. So unless there is some reason not to do it this way that's what I'd go with as it is much easier to wire up (1 signal for the crate vs multiples for each card).

> On Aug 9, 2016, at 9:34 AM, Marco Battaglieri <battaglieri at ge.infn.it> wrote:
> 
> Dear Amanda,
> here is the list of signals we would like to interlock from the FT-Cal and the FT-Hodo:
> 
> -Temperature:
>  up to 8 signals (6 from the calorimeter and 2 from the hodoscope)  from RTDs: (NI9216?)
> 
> - Gas (Cal only)
> flow from MKS GE50A Conf 013 (N2) 202 (200 sccm) (NI???)
> 
> - humidity (Cal only)
> 2 sensors HIH-4000-003: (NI-9263, NI-9215 (supply and readout)?)
> 
> - chiller: interlocked via a relay  to put the system in stand-by (NI9485?)
> 
> - HV: borads currently present in the FT crate (3xA1520P, 3xA1737P, 1xA1536HDM) with the exclusion of the A1535N that will not be present when in Hall-B. Brian checked and all boards can be individually interlocked with a relay module (NI9485?)
> 
> - LV: Wiener MPod boards (individually interlocked): 2xTTL signal (NI9401?)
> 
> - hodoscope box  switch
> 1 switch on the box lid
> 
> Hardware interlocks needed to be coordinated with Nathan, since we would like to monitor/record the interlock status in EPICS monitor (database).
> We understood this can be done communication with the cRIO controller but before to finalize the design, we would like to have the confirmation.
> 
> 
> Please let us know if you need any more information
> Cheers
> Marco and Raffaella
> 
> 
> Amanda Hoebel wrote:
>> Dear Marco,
>> 
>> Since we have been discussing the cRIO interlocks for the tagger, we were wondering if you have a list of signals needed to be monitored.
>> 
>> Also could you let us know what your plans are regarding the move for the tagger to the hall?  Thank you in advance.
>> 
>> Sincerely,
>> Amanda
>> _______________________________________________
>> Dsg-ft mailing list
>> 
>> Dsg-ft at jlab.org
>> https://mailman.jlab.org/mailman/listinfo/dsg-ft
> 
> _______________________________________________
> Dsg-ft mailing list
> Dsg-ft at jlab.org
> https://mailman.jlab.org/mailman/listinfo/dsg-ft
> _______________________________________________
> Dsg-internal mailing list
> Dsg-internal at jlab.org
> https://mailman.jlab.org/mailman/listinfo/dsg-internal





More information about the Dsg-ft mailing list