Pablo, 
Just a thought, does the same problem exist on the Torus? 
| From: "Pablo Campero" <campero at jlab.org>
| To: "dsg-hallb magnets" <dsg-hallb_magnets at jlab.org>
| Cc: "Sarin Philip" <philip at jlab.org>, "Mark Todd" <mtodd at jlab.org>
| Sent: Wednesday, April 26, 2017 9:04:40 AM
| Subject: Re: [Dsg-hallb_magnets] Hall B Solenoid PSU issues
| Hello Ruben,
| Yesterday afternoon the problem with the PSU was solved.
| The PSU remote crate display was showing an interlock, which was occurring
| because of their interlocks inputs were not activated. These inputs are
| provided from the relay outputs of the PLC.
| The following steps were followed to solve the problem:
| 1.Verify interlock hardwiring for the PSU crate board; used drawings
| B000000900-0639 and B000000900-0654.
| 2. Notice that PLC relay outputs that are wired to the interlock inputs of the
| PSU remote crate has to be always ‘ON’ to avoid the interlocks.
| 3. Added PLC code in ‘ Magnet Interlocks’ routine to have always active the
| relay outputs (Slot 1- Remote PLC chassis) and match with the wiring mention
| above.
| 4. Two PLC tags were added to the PLC routine: PLC_FAST_DUMP_BACKUP and
| PLC_SLOW_DUMP at channels 12 and 13 respectively.
| All changes in the Solenoid PLC were made Online, and latest version is running
| in the PLC controller.
| Best Regards
| Pablo Campero
| The following is a new meeting request:
| Subject: 	Hall B Solenoid PSU issues
| Organizer: 	"Ruben Fair" <rfair at jlab.org>
| Location: 	Hall B Level 2 - by solenoid PSU
| Time: 	Tuesday, April 25, 2017, 1:15:00 PM - 2:15:00 PM GMT -05:00 US/Canada
| Eastern
| Invitees: 	campero at jlab.org; mtodd at jlab.org; spiegel at jlab.org; philip at jlab.org;
| ghoshal at jlab.org
| *~*~*~*~*~*~*~*~*~*
| Pablo,
| We will need you there to possibly make changes to the PLC settings.
| Regards
| Ruben
| _______________________________________________
| Dsg-hallb_magnets mailing list
| Dsg-hallb_magnets at jlab.org
| https://mailman.jlab.org/mailman/listinfo/dsg-hallb_magnets
-- 
George 
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <https://mailman.jlab.org/pipermail/dsg-hallb_magnets/attachments/20170426/e3a1fd47/attachment.html>
    
    
More information about the Dsg-hallb_magnets
mailing list