[Dsg-mvt] Mix 1 Setpoint
    Brian Eng 
    beng at jlab.org
       
    Thu Jan 11 20:25:06 EST 2018
    
    
  
Set the max flow for the argon MFCs to 1391 sccm. At some point in the future, we'll see to switch between modes to make sure it remembers the values.
As for the pressure in mix 2, I set the max to 20 psi as it is currently set to bounce between 12-16 psi so a max of 15 doesn't make sense unless the other values are changed as well.
----- Original Message -----
> From: "mdefurne" <mdefurne at jlab.org>
> To: dsg-mvt at jlab.org
> Sent: Thursday, January 11, 2018 4:26:54 PM
> Subject: Re: [Dsg-mvt] Mix 1 Setpoint
> Hi Brian,
> 
> Can you please indeed set the maximum flow rate at 1391. We will never
> reach such value.
> 
> Also, can you set the max pressure in tank 2 at 15 psi since the
> isobutane pressure is set at 25psi upstream of the MFC?
> 
> Thank you,
> 
> Maxime
> 
> 
> Le 11/01/2018 à 13:58, Brian Eng a écrit :
>> Also, the full scale (which determines minimum flow) can be adjusted if need be.
>>
>> For that I would need to know what the maximum flow rate you'd need out of the
>> Ar MFC.
>>
>> It can be set from 1391 - 2780 sccm, the min flow is 1.5% of that value, so 41.7
>> sccm as currently configured.
>>
>> I don't know if the MFC retains that value when switching gases, so we'd need to
>> test that if you decide we should change the value.
>>
>> ----- Original Message -----
>>> From: "Brian Eng" <beng at jlab.org>
>>> To: dsg-mvt at jlab.org
>>> Sent: Thursday, January 11, 2018 1:49:09 PM
>>> Subject: [Dsg-mvt] Mix 1 Setpoint
>>> Hi Maxime,
>>>
>>> The flow rate you guys are requesting is currently to low for the Ar MFC, so it
>>> isn't flowing anything.
>>>
>>> I would suggest raising the FMT (or FTT) setpoint to something higher.
>> _______________________________________________
>> Dsg-mvt mailing list
>> Dsg-mvt at jlab.org
>> https://mailman.jlab.org/mailman/listinfo/dsg-mvt
> 
> _______________________________________________
> Dsg-mvt mailing list
> Dsg-mvt at jlab.org
> https://mailman.jlab.org/mailman/listinfo/dsg-mvt
    
    
More information about the Dsg-mvt
mailing list