Bob, thank you for promptly taking corrective actions.
Volker
On 6/11/19 3:32 PM, Bob Miller wrote:
>
> All,
>
> The following corrective actions will be taken to ensure the RICH N2
> supply is not interrupted:
>
> 1. The N2 supply valve is now locked open and has a lock out tag on
> it as shown in the pictures below
> 2. Replacement back up bottles have been ordered by Tyler
> 3. When the replacement bottles have been installed, I will move the
> supply valve to the RICH gas panel
> 4. An alarm has been set up at 20 psi N2 supply pressure that will
> notify the engineering on call person
> 5. An alarm will be set up at 10 psi for the back up bottles to know
> if they are ready to supply the RICH. This alarm will also notify
> the engineering on call person.
>
> Regards,
>
> Bob
>
>
>
> --
> Bob Miller
> Hall B Lead Engineer
> Jefferson Lab
> 757 822-9586
>