[dsg-hallb_svt] CVT work

Yuri Gotra gotra at jlab.org
Thu Apr 1 07:53:17 EDT 2021


Thank you Brian,


I asked Sergey to install the switch. We will take care of moving the 
V450 crate tomorrow. If you have recommendations on location of other 
crates, please let me know, we have the manual forklift in the clean 
room. I expect releasing the Dynalene by RadCon soon and will proceed 
with testing the cooling system. Do you mean the thresholds in the GUI 
or EPICS settings? Could you please send instructions on accessing the 
hardware interlock GUI from EEL124. To start, we need to wire the 
signals coming from the cooling system (temperature, pressure, flow), 
and purging (humidity).

On 4/1/21 1:04 AM, Brian Eng wrote:
> Hi Yuri,
>
> I've started connecting the hardware interlock chassis. I've verified 
> that the chiller interlock works (both with the setpoint trips as well 
> as the override key) as well as the MPOD ones.
>
> I still have more work to do as I found some cables that were damaged 
> and will need to be repaired.
>
> Some quick comments.
>
>   * We need a switch installed near the racks. Right now I have a
>     single network cable going to the cRIO but that should really be
>     going to a switch
>   * The VME crate with the V450 cards is installed upside down, but
>     even then it will have trouble reaching the patch panel
>   * So either the VME should be moved to the floor under the patch
>     panel or another rack is needed
>
> If there are any particular signals you'd like wired up when I come in 
> tomorrow night let me know and I'll focus on those. Could you also 
> check the interlock thresholds? It seems like some of them didn't get 
> set correctly when moving things around.
>
> I left the coolant pressure interlock enabled so that it would force 
> everything to be off.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <https://mailman.jlab.org/pipermail/dsg-hallb_svt/attachments/20210401/4312d472/attachment.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: gotra.vcf
Type: text/x-vcard
Size: 102 bytes
Desc: not available
URL: <https://mailman.jlab.org/pipermail/dsg-hallb_svt/attachments/20210401/4312d472/attachment.vcf>