[Dsg-hallc_controls] Ethernet vs Controlnet test
Tyler Lemon
tlemon at jlab.org
Tue Jun 12 16:46:10 EDT 2018
Hi Mike,
After a quick search, we found Allen-Bradley's manual on how to set up a Device Level Ring and what type of communication module is needed. It seems that a 1756-EN2TR module with embedded switch technology is needed.
In the manual, we also found that the EN2TR module is only compatible with RSLogix5000 version 17 or later (page 30).
We double checked the compatibility with version 16 by trying to add a new EN2TR module to the SHMS PLC program and the EN2TR module is not listed as an option.
It seems that the best option to replace ControlNet modules is still the 1756-EN2T Ethernet/IP module since there are a few spare EN2T modules available and the EN2T modules are compatible with RSLogix5000 version 16.
Best regards,
Tyler
From: "Mike Fowler" <fowler at jlab.org>
To: "dsg-hallc controls" <dsg-hallc_controls at jlab.org>
Sent: Tuesday, June 12, 2018 3:17:52 PM
Subject: Re: [Dsg-hallc_controls] Ethernet vs Controlnet test
Hi,
Please look into the Rockwell Automation Ethernet Device Level Ring.
Thank you,
Mike
On 6/12/2018 1:14 PM, Tyler Lemon wrote:
Hi Mike,
No, the Ethernet modules that will be added should not open a security hole to the chassis.
The new modules will be as secure as the existing Ethernet modules and will be put on the same Hall C subnetwork behind accelerator's firewall.
Best regards,
Tyler
From: "Mike Fowler" <fowler at jlab.org>
To: "dsg-hallc controls" <dsg-hallc_controls at jlab.org>
Sent: Tuesday, June 12, 2018 11:42:18 AM
Subject: Re: [Dsg-hallc_controls] Ethernet vs Controlnet test
>>>1. New IP address assignment for two Ethernet modules in Hall C subnet.
Does this open up security hole to the chassis?
Perhaps different Ethernet modules should be used.
Mike
----- Original Message -----
From: "Pablo Campero" <campero at jlab.org>
To: "dsg-hallc controls" <dsg-hallc_controls at jlab.org>
Sent: Tuesday, June 12, 2018 10:57:30 AM
Subject: Re: [Dsg-hallc_controls] Ethernet vs Controlnet test
Hello,
Yesterday, test was performed and results were the expected.
Standalone PLC test station configured back to its previous configuration to allow Mike continue with his test.
Based in the discussion with Steve, two Controlnet modules will be swapped by two Ethernet modules in the "Q1" and "HX" PLC chassis; so in preparation for this test it will be required the following:
1. New IP address assignment for two Ethernet modules in Hall C subnet.
2. Identify Ethernet switch and ports available in Hall C to connect two Ethernet modules - Steve will contact Brad Sawatzky to identify switch.
3. Run Ethernet cables from the switch to the modules respectively.
4. Create a new SHMS PLC program, new program will include only the Ethernet module modifications and will keep all I/O module configurations/values as previously used by Controlnet - In progress by DSG.
For item #1: Steve/Mike can you decide and let us know which of the available Ethernet modules will be used? So then we can get the MAC address from these modules and assign the IP address.
Best Regards,
Pablo
From: "Steve Lassiter" <lassiter at jlab.org>
To: "Pablo Campero" <campero at jlab.org>
Cc: "dsg-hallc controls" <dsg-hallc_controls at jlab.org>
Sent: Monday, June 11, 2018 11:51:45 AM
Subject: Re: [Dsg-hallc_controls] Ethernet vs Controlnet test
Hi,
Sounds Good.
I would like to look over the setup and test. Lets shoot for 1:30pm today in ted 1544.
Did the PLC down time include time to re-schedule the PLC on networxs?
Steven
From: "Pablo Campero" <campero at jlab.org>
To: "dsg-hallc controls" <dsg-hallc_controls at jlab.org>
Sent: Monday, June 11, 2018 11:26:11 AM
Subject: Re: [Dsg-hallc_controls] Ethernet vs Controlnet test
Hello Steve and Mike,
>From DSG's point of view the pre-test requested has been completed.
For the test three chassis were configured as follow:
Chassis #1: (Master chassis which has the controller Stand Alone PLC)
Chassis #2 : Slave 1; configured with Controlnet module for interface communication and I/O modules
Chassis #3: Slave 2; configured initially with a Controlnet module (to then be swapped by a Ethernet module) and I/O modules.
Two PLC ACD. files (PLC programs) have been created and used for this test. The first PLC program has the all Controlnet configurations between Master and Slaves chassis and is simulating the actual configuration in the SHMS PLC systems; the second PLC program contains the combined network configurations with Slave 1 chassis using a Controlnet module, Slave 2 with Ethernet module, this chassis #3 is simulating the changes that needs to be implemented.
The results of the test showed that Ethernet module work without any problem when it was used to replace the Controlnet module.
The system is able to run with a combined network configuration (Ethernet and Controlnet modules) with no problems. The down period (PLC off line) measured in the test for the PLC was less than 1 min, this is the time needed to download the new version of the PLC program which includes the implementation of the Ethernet module the SHMS PLC I/O chassis. So based in this test, we can follow the previous procedure mentioned (6 steps) and after downloading of the new version of the PLC program to the SHMS PLC shouldn't be any error.
If you want to check the test running, please let us know and we can go over it today and be done with this check to allow Mike continue with his test in the Standalone PLC test station.
Best Regards,
Pablo
From: "Pablo Campero" <campero at jlab.org>
To: "dsg-hallc controls" <dsg-hallc_controls at jlab.org>
Sent: Friday, June 8, 2018 5:05:13 PM
Subject: [Dsg-hallc_controls] Ethernet vs Controlnet test
Hello,
To test the performance of the Ethernet vs Controlnet for the SHMS PLC systems, Amanda, Tyler and I have done the following:
1. Set up standalone PLC to mimic how the SHMS PLC system is set up with the controller and I/O modules in different chassis.
2. Added DSG-PLC chassis to the standalone PLC system using initially Controlnet network for a total of three chassis (1 controller chassis, and 2 I/O chassis)
3. Began development of PLC program to very test system works
Next week DSG plans to swap the Controlnet module with Ethernet module to verify that Standalone PLC can run with one I/O chassis using an Ethernet module and a second I/O chassis using a Controlnet module.
Best Regards,
Pablo
_______________________________________________
Dsg-hallc_controls mailing list
Dsg-hallc_controls at jlab.org
https://mailman.jlab.org/mailman/listinfo/dsg-hallc_controls
_______________________________________________
Dsg-hallc_controls mailing list
Dsg-hallc_controls at jlab.org
https://mailman.jlab.org/mailman/listinfo/dsg-hallc_controls
_______________________________________________
Dsg-hallc_controls mailing list
Dsg-hallc_controls at jlab.org
https://mailman.jlab.org/mailman/listinfo/dsg-hallc_controls
_______________________________________________
Dsg-hallc_controls mailing list
Dsg-hallc_controls at jlab.org
https://mailman.jlab.org/mailman/listinfo/dsg-hallc_controls
_______________________________________________
Dsg-hallc_controls mailing list
Dsg-hallc_controls at jlab.org
https://mailman.jlab.org/mailman/listinfo/dsg-hallc_controls
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <https://mailman.jlab.org/pipermail/dsg-hallc_controls/attachments/20180612/4f97edbb/attachment-0001.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: Allen-Bradley Ethernet-IP Embedded Switch Technology - Lineara and Device-level Ring Topologies.pdf
Type: application/pdf
Size: 15919450 bytes
Desc: not available
URL: <https://mailman.jlab.org/pipermail/dsg-hallc_controls/attachments/20180612/4f97edbb/attachment-0001.pdf>
More information about the Dsg-hallc_controls
mailing list